We were measuring inductance of generator's stator winding for each phase separately (after removing the star connection) using a simple RLC meter, to check for any inter-turn fault (yes I know - we didn't have anything else to check with).
The inductance of Red and Yellow phase was identical (4mH) but blue phase showed more than twice (12mH). We thought something is wrong with the blue phase winding. Suddenly we thought of manually rotating the rotor, and turned it 90 degrees, but found same reading. Then we rotated 45 degrees; rechecked the inductance and this time, the inductance of yellow and blue phase measured same (4mH) but red phase showed 12mH - it was as if the 'abnormal' reading had rotated with the rotation of the rotor and there was no fault with the blue phase winding as we initially had thought.
So now I want to ask: Does the presence and/or position of rotor, affects the inductance of stator windings?
It clearly did here. And what caused it when the machine was stationery and offline for over a month? Residual magnetism in the rotor? Would the results be any different if it were a non-salient pole rotor?
Our generator is 3-phase, Y-connected, brushless, 4-pole rotor (salient), turbine driven machine, and had been offline for over a month.