Substation Grounding System

06/30/2018 1:28 AM

Dear Sirs,

Determination of soil resistivity is important for designing substation grounding systems.

For example: if a substation under consideration reads 270 ohms meter to 4.5 kilo-ohms of resistivity when the soil resistivity was measured - what value of resistivity should be considered for designing substation grounding systems?

I understand that - we are only measuring apparent value of soil resistivity and this is used to find the reduction factor for derating the nominal value of surface layer resistivity.

The best (lowest) value obtained (for 1 metre electrode spacing using wenner method) is 270 ohm metres. Can this value be considered for substation grounding system design?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Substation Grounding System

06/30/2018 10:30 AM
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Substation Grounding System

06/30/2018 9:57 PM

...and after you have the facts, get the standards that are applicable to the installation and its locale, then have your design approved by an electrical engineer who has experience dealing with the AHJ.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Substation Grounding System

06/30/2018 11:59 PM

Here try this... and next time do your own research!
LINK

__________________
The square root of nothing is what you make it!
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Substation Grounding System

07/01/2018 10:00 PM

The resistance value you measure may well be accurate on the day you measured it. But the resistance value limit is whatever the standard the substation grounding is to be built to says it needs to be, and if you cannot achieve it with the existing soil resistivity then you dig earth pits and use additives and extra earth rods and otherwise lower the resistivity of the site until you can achieve it.

This needs to be included in the design and costs when building the substation.

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Substation Grounding System

07/02/2018 8:48 AM

...and soil resistivity varies with a number of factors, not least of which is the amount of moisture in the soil. Among the techniques for reducing it is the pouring of a tanker-load of seawater into the soil immediately where it is to be measured, though this may have unwanted impact on the vegetation in the area. If none is available, bovine urine would seem to make a reasonable substitute.

In the limit, the soil resistivity has to be low enough to operate any applicable circuit protective device in the event of a fault, and equipment needs to be selected accordingly. There are national standards for such things, which one would be well advised to follow.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

brich (1); jack of all trades (1); lyn (1); PWSlack (1); RAMConsult (1)

Previous in Forum: Effect of Rotor on Stator Winding Inductance in an Offline Generator   Next in Forum: 3VA PT/VT Measurement and Safety/Accuracy

Advertisement