Anonymous Poster #1

Delta Connected Motor to VFD

07/01/2018 4:52 PM

We have six terminal outgoing terminals from a VFD to a motor. It means the motor is delta connected. why not the Motor have a Delta winding Internally or delta connected through links or through cables. why we need to run a cables from the VFD to the motor for making a delta connection?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9915
Good Answers: 1141
#1

Re: Delta Connected Motor to VFD

07/01/2018 7:36 PM

Why six wires? Maybe so you can easily read or monitor the current in each motor winding.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Delta Connected Motor to VFD

07/01/2018 7:43 PM

If it is not stolen, it should have come with an operator's manual. That is likely to have a wiring diagram.

If not, ask the manufacturer for one.

If all else fails, hire a tech that knows VFDs and motors.

Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Delta Connected Motor to VFD

07/01/2018 8:32 PM

I think you have some faulty information....what is the VFD brand and model #? Is this a 2 speed motor? Is this the original motor? What other info do you have on the motor? What type of equipment is this on?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: Delta Connected Motor to VFD

07/02/2018 2:54 AM

Are you sure its a VFD and not a StarDelta starter?

__________________
The square root of nothing is what you make it!
Reply Good Answer (Score 2)
Anonymous Poster #1
#5

Re: Delta Connected Motor to VFD

07/02/2018 11:48 AM

I have attached the terminal details of VFD in the link,

https://www.dropbox.com/s/syemub2szqbdv2e/Power%20and%20control%20cables%20arrangement.pdf?dl=0

The load is a compressor Motor. I don't have the motor drawings. The VFD make is Fuji Electric's Frenic Eco Series

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Delta Connected Motor to VFD

07/02/2018 12:58 PM

It appears as though that inverter was modified to run two motors from the one inverter. If you look carefully, each of the terminal pairs is labeled the same: U1, V1, W1.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster #1
#7
In reply to #6

Re: Delta Connected Motor to VFD

07/02/2018 2:49 PM

JRaef,

If you closely look at the right side terminals, (Y, X, Z) is written in that attachment, which implies that it is a delta connection. Sample image below,

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: Delta Connected Motor to VFD

07/02/2018 8:05 PM

I think you are reading too much into this. But what do I know? I’m not there...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Delta Connected Motor to VFD

07/03/2018 2:26 AM

The 6-terminals at motor may not be for Delta connection.

Could it be that the motor has two windings internally!

The 'One-channel 12/12 -pulse series connected LCI drive' supplying the two windings!!

Could you get hold of the motor winding connection diagram (Motor name plate may have it)!!

__________________
Raghunath
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#10

Re: Delta Connected Motor to VFD

07/14/2018 2:22 AM

Are sure the 6 terminal are for the motor winding?..

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); brich (1); JRaef (2); lyn (1); raghun (1); Rixter (1); Simon Wan (1); SolarEagle (1)