Reference to subject, this is regarding incidents of over voltage alarm 59VHz annunciation intermittently (around 12-13 times) on our both gas-turbine driven turbo generators (nameplate attached) since July 02, 2018 12:30 AM. We have two identical turbo generators that run in parallel to supply load of our Complex. Reactive power of one turbo generator TG-702 goes into negative value at / just before the time of alarm and other generator supplies excessive reactive power (see attached presentation for values and trends). Oscillography plots of generator protection relays G60 of both TG-701 / 702 are also attached for reference (for one fault event). Existing protection relays setting file is also attached for reference. Existing excitation system is Compound Type SCT / PPT based Static Excitation System. Following are my queries in this regard.
Our initial assessment is that the fault is being caused by intermittent loss of excitation of TG-702 (though not detected by Protection Relay) and operation of generator in under-excitation mode as induction generator. TG-701 increases its excitation (VARs and Voltage) to supply this reactive power demand in such a case. Comment. What could be the possible causes and checks to detect this anomaly? Existing schematic drawings of TG-701 / 702 are also attached. Why this situation is not detected by Loss of Excitation Protection? In one of the faults, the alarm of 59VHz persisted for ~4-5 sec.
- The overvoltage alarm 59VHz also annunciated during first start-up (before synchronizing) of our TG-701 generator after rewind in March 2018 and tripped generator. No fault was observed during troubleshooting of this fault, however we suspected loss of generator voltage feedback signal (from PT2 in attached drawings). Confirm if same suspected problem (loss of generator voltage feedback) can cause the abnormal behavior as observed. What are the possible causes and remedies in such a case?
- What further steps can be taken to isolate / diagnose the problem further as we suspect abnormal behavior with one generator. Can opening of tie-breaker (between two generators) an option? What are the possible outcomes in such a case?
A really prompt response over the issue will be appreciated.