Excitation Problem with Parallel Operation of Turbo Generator

07/02/2018 4:13 AM

Reference to subject, this is regarding incidents of over voltage alarm 59VHz annunciation intermittently (around 12-13 times) on our both gas-turbine driven turbo generators (nameplate attached) since July 02, 2018 12:30 AM. We have two identical turbo generators that run in parallel to supply load of our Complex. Reactive power of one turbo generator TG-702 goes into negative value at / just before the time of alarm and other generator supplies excessive reactive power (see attached presentation for values and trends). Oscillography plots of generator protection relays G60 of both TG-701 / 702 are also attached for reference (for one fault event). Existing protection relays setting file is also attached for reference. Existing excitation system is Compound Type SCT / PPT based Static Excitation System. Following are my queries in this regard.

Our initial assessment is that the fault is being caused by intermittent loss of excitation of TG-702 (though not detected by Protection Relay) and operation of generator in under-excitation mode as induction generator. TG-701 increases its excitation (VARs and Voltage) to supply this reactive power demand in such a case. Comment. What could be the possible causes and checks to detect this anomaly? Existing schematic drawings of TG-701 / 702 are also attached. Why this situation is not detected by Loss of Excitation Protection? In one of the faults, the alarm of 59VHz persisted for ~4-5 sec.

  1. The overvoltage alarm 59VHz also annunciated during first start-up (before synchronizing) of our TG-701 generator after rewind in March 2018 and tripped generator. No fault was observed during troubleshooting of this fault, however we suspected loss of generator voltage feedback signal (from PT2 in attached drawings). Confirm if same suspected problem (loss of generator voltage feedback) can cause the abnormal behavior as observed. What are the possible causes and remedies in such a case?
  2. What further steps can be taken to isolate / diagnose the problem further as we suspect abnormal behavior with one generator. Can opening of tie-breaker (between two generators) an option? What are the possible outcomes in such a case?

A really prompt response over the issue will be appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Mar 2018
Posts: 31
#1

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 4:19 AM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 5:12 AM

Please relate the content of the telephone discussions that have taken place with the original equipment manufacturer on this topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#3
In reply to #2

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 5:28 AM

Dear PWSlack,

We have taken up matter with OEM M/s GE and their comments are awaited.

BR,

Kashif

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #3

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 8:51 AM

Having re-read your message, I realise your current problem is overvolt alarm, although you have had overvolt trip before. So voltage increase is small %. Could be droop circuit problem or switching which modifies volt ref. according to plant state e.g. circuit sheet 5 - 52G?? contact or trouble with wiper contact on many pots on sheet 4. It does not look like a protection relay fault because you see over & under excitation occurring.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #6

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 6:56 PM

Kashif,

You wrote that your initial interpretation of problem was under-excitation fault on a machine.

This would lower system voltage not raise it.

My thought is that TG701, the machine which previously gave an overvoltage fault, gives increased voltage/excitation causing voltage increase and alarm. Because both machine relays see same voltage it is chance which has most sensitive/fast response. Note that an increase in gain or increased firing by the AVR electronics would be corrected by the feedback, suggesting problem is with the reference value or more likely, the feedback components.

You need to investigate the correct machine, the one which over-excited (increased lagging VArs). My last message gave suggestions to investigate the droop and generator voltage setting switching/adjustment variable resistors.

67model

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #3

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 8:52 AM

That statement is of doubtful veracity, for were (a) telephone conversation(s) to have taken place, those comments would have been available immediately, and not remain outstanding since <...July 02...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#10
In reply to #7

Re: Excitation Problem with parallel operation of Turbo Generator

07/03/2018 5:05 AM

Who are you to doubt the veracity of OP's response. If you have nothing constructive to add, I would suggest that you desist.

Register to Reply Off Topic (Score 7)
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#11
In reply to #10

Re: Excitation Problem with parallel operation of Turbo Generator

07/03/2018 1:02 PM

That's rich!

Someone decided that anonymous was the best choice for a post begins with, "Who are you...".

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 8:12 AM

If excitation failed on one generator, other would have to supply excitation current for faulty one (as an induction motor) + lagging load current - that looks like a voltage reduction.

Have you observed the field current meters on the machines during these events?

Loss of voltage control (low voltage from VT) on one machine would cause it to overvolt (over excite), but this could cause other machine to reduce excitation to compensate.

Do you have any VAr sharing coupling between machines or an external active/reactive load sharing/frequency control box?

Loss of excitation relay may not operate if one machine goes overvolt - neither machine has lost excitation.

The date on the circuits is 2015 - have you contacted GE?

Unfortunately, I cannot read any graphs from the G60 .cfg files, but I do not think it will give you a cause. The fact that you had a previous overvolt fault suggests fault in voltage control - loss of feedback, jump-up of reference, excitation amp fault causing high excitation current. These things are amenable to investigation on running unit, off-load. Fault in "lagging current droop" possible, but it is a simple circuit and I do not think it would raise volts to overvolt trip level.

Check all excitation panel wires & connections for bad connection by ohmmeter/pulling&pushing while running off-load. Any connections added/altered by recent excitation related modification are particularly suspect.

Did this unit work OK for long period before any recent modifications?

Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#5
In reply to #4

Re: Excitation Problem with parallel operation of Turbo Generator

07/02/2018 8:29 AM

Dear 67Model

Thank you for your valuable comments . . The required details are as :

1) Have you observed the field current meters on the machines during these events? Nopes there is no logging on field ammeters and the event last only for 3-4 seconds therefore we were not able to observe field ammeter.

2) Do you have any VAr sharing coupling between machines or an external active/reactive load sharing/frequency control box? The sharing is reactive current compensation.

3) Did this unit work OK for long period before any recent modifications? We did no modification in excitation circuit since long time. There is no 59VHZ alarm from last 16 hours :)

Register to Reply
Associate

Join Date: Mar 2018
Posts: 31
#12
In reply to #4

Re: Excitation Problem with parallel operation of Turbo Generator

07/05/2018 12:26 AM

https://drive.google.com/drive/folders/1nD9rpfOtHuJyjO2kbaxGYp_N7WaXXEAq?usp=sharing

Please find attached revised link including G60 relays fault data osc (OSC_254_39_20150527_085720 for TG-701) OSC_254_440_20160324_113935 for TG-702 Generator

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Excitation Problem with Parallel Operation of Turbo Generator

07/02/2018 10:24 AM

"...Reactive power of one turbo generator TG-702 goes into negative value at / just before the time of alarm and other generator supplies excessive reactive power..."

The situation that you describe is typical when there are two machines tied together, share common protective relaying, and the rate of reactive output of one machine does not match the other. As 67 Model points out, in paralleled machines, if one machine cannot meet the demand put on it by the load, then the other tries to make up for the difference. The question is, what is causing the drop in excitation on one machine? Unfortunately your drawings do not not include any details on the AVR/Excitation system, its inputs/outputs, and/or settings, so all that can be offered are generic suggestions.

Some places to look:

Polarity of all PTs and CTs,

Settings of both AVRs must be identical; gain, damping, sensitivity, droop, etc.

Both generators must be in the same mode; parallel, isolated, only one Master,

If one generator consistently reaches a point where its reactive power starts falling, then there could be thermally or load related issues such as: shorted turns in the rotor winding, overheating connections, failing diodes/fuses, poor contact makeup, etc., etc.

GE knows their equipment very well, so make sure that everything that on your side of the boundaries are in perfect working order, otherwise you will be responsible for any repairs outside of the scope of the rebuild.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Anonymous Poster (1); kashifidrees (4); PWSlack (2); RAMConsult (1); truth is not a compromise (1)

Previous in Forum: Delta Connected Motor to VFD   Next in Forum: Protection

Advertisement