Effect Of Cable Rolling

09/18/2007 7:37 AM

hi all.

I have a 300mm2 , xlpe aluminium cable, 3 1/2 core .i had to temporarily terminate it to the supply mains. the cable of about 50 meters is lying on the ground but in a roll ed postion and then terminated to supply mains. will that 50 meter ROLL will effect the the supply or the surroundings. i mean any magnetic field will be created , because this is wat i was told by some men.

__________________
electrified
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: effect on supply due to cable rolling

09/18/2007 7:44 AM

Depending on the size of the attached load, there might be a problem with heat dissipation from concentric turns. Extension leads, for instance, are intended to be used fully unwound from the reel, and if left partly-wound on the reel are usually subject to de-rating.

__________________
Good moaning!
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Effect Of Cable Rolling

09/18/2007 4:26 PM

I have also seen it cause a severe voltage drop, worse than just the extra length of wire. Think of it as an air-core reactor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Nov 2006
Location: antwerp/belgium/europe
Posts: 160
Good Answers: 5
#3

Re: Effect Of Cable Rolling

09/19/2007 5:45 AM

The magnetic field is probably not the biggest problem (unless there is ultra sensitive things in the neighborhood) The problem (and danger !) lies in the heat production of the "coil" you make by "winding" the cable. Laying it out i zig-zag would be the best sollution, if you don't have the place to do this, make the windings (circles) as big as possible and CHECK the temperature of the cable when it is in use. I witnessed one time how a roll of cable just melted into one big "clump" of plastic and copper. And it was NOT because there was to much current flowing through that cable. It happened because of the generated heat.

For this reason the "fuse" you see on some extention-cable-rolls is not a current fuse, but a THERMAL fuse !

__________________
44mEurope
Register to Reply
Anonymous Poster
#4

Re: Effect Of Cable Rolling

09/19/2007 9:04 AM

Does this sound safe, leaving an energized cable lying in coils on the ground?

Register to Reply
Commentator

Join Date: Sep 2007
Location: Here, there and everywhere...
Posts: 61
#5

Re: Effect Of Cable Rolling

09/19/2007 10:13 AM

Never use cable rolled in a coil, it will heat up and may cause a fire.

__________________
An EXPERT is a 'has been', that is a drip under pressure - My Boss
Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#6

Re: Effect Of Cable Rolling

09/19/2007 12:30 PM

Magnetic field will almost not appear because the "coil" is bifilar. The major problem is the warming.

__________________
Aged man is not old man...
Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#7

Re: Effect Of Cable Rolling

09/19/2007 5:16 PM

Unroll it before you apply any power unless you derate it by about 90% even if you are lucky and it doesnt melt or catch fire it will be so badly damaged you will have to throw it away

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Power-User

Join Date: Jul 2007
Posts: 182
Good Answers: 1
#8

Re: Effect Of Cable Rolling

09/19/2007 10:25 PM

"Figure-eight" the extra wire. The magnetic will balance and the heat will be manageable.

We routinely perfom this with high voltage, running through 4/0 for every rock concert you've ever been to. Temporary power cables are often too short for desired runs and need be extended. "Figure-eight-ing" the coil prevents connectors from fusing together or burning the casing off the wires.

Register to Reply