NGR Information Required

09/19/2007 2:31 AM

We have 6 DG sets of 11KV/1.2MW each connected parallel to each other. Now as we are in the phase of ordering NGR, service provider is giving two options i.e. separate NGRs for individual set or a common NGR for all DG sets. Can any body tell me which one is better and why? Any other suggestions will be highly precious for us.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#1

Re: NGR Information Required

09/20/2007 3:48 AM

We always go for a common neutral earthing resistor and individual neutral earthing breakers or contactors with cross interlocking. The only downside of this is when the resistor/path goes open circuit. For 6 sets you could use duty/standby system for the resistors, assume you will have earth monitoring kit.

__________________
A day without a smile is a day lost
Register to Reply
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#2
In reply to #1

Re: NGR Information Required

09/23/2007 1:06 AM

Can u send me the elementary Single Line Diagram ( even a hand made sketch) showing major equipment parameters . The reason is that I prefer to get a whole picture of your project, and not look at it through a key-hole.

Register to Reply
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#3

Re: NGR Information Required

09/23/2007 11:50 PM

I understand the economic reasoning for choosing the single-NGR approach, but in my experience the preferred arrangement is the multi-NGR approach, that is, each generator with its own NGR! The principal reasons follow:

1) For safety considerations the common NGR scheme requires that each generator-neutral be disconnectable from the common neutral-bus!

2) For maintenance requirements the common NGR scheme approach should consist of at least two NGRs, so that maintenance can be performed, while the plant is in operation!

3) For operational simplicity the common NGR scheme unduly complicates procedures because whenever a machine is taken out of service, its neutral must be disconnected, either manually or automatically!

I also appreciate that additional engineering is required to provide individual generator-earthing, but in the end, the goal must be to insure personnel safety and simplify operations!

I can provide you with additional details when I have a good picture of the overall design!

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4

Re: NGR Information Required

09/26/2007 7:19 AM

I suggest that you use separate NGR for each DG.NGR of the incoming DG set during parallel operation will remain open and closed during running. . But you have to ensure how much circulating current DG set can endure.

__________________
BNDas
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

biswanath.das (1); dhilju82 (2); peterd (1)

Previous in Forum: help me with da contorller   Next in Forum: Earthing For 300 KVA DG

Advertisement