Anonymous Poster

Earthing For 300 KVA DG

09/19/2007 3:11 AM

I have to make earthing pits for 300 Kva DG. I am planning two copper earth pits for neutral and two for body earth...will that work? Please tell me what should be the minimum distance between these earth pits because I dont have much area available.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Apr 2007
Posts: 178
Good Answers: 3
#1

Re: Earthing For 300 KVA DG

09/19/2007 11:05 PM

Almost all calculations require the value of your soil resistivity ? Ohm/centimeters

You need to measure it and post it. Along with the type of soil and moisture content information. Please define your terms body and earth pits. They are not (normally) used in US engineering terminology.

Then perhaps we may be able to help you...

Why are not all grounds bonded together at this point. (this is a point of generation, not a customer load point.

Snakers

Reply
Anonymous Poster
#2

Re: Earthing For 300 KVA DG

09/19/2007 11:32 PM

Number of earth pits depends on the soil resistivity and the moisture content in the soil.

As per Indian regulations the distance between earth pits should be 3050mm and the earth pit away from the building structure should be 1525mm.

Geetha

Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#3

Re: Earthing For 300 KVA DG

09/20/2007 12:49 AM

You have not indicated the countery of yours.You need to refer your local earthing code.each countery will have its codes.

crm

__________________
Run silent run deep
Reply
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#4

Re: Earthing For 300 KVA DG

09/20/2007 7:38 PM

I'm not sure you need to earth the neutral. Someone smarter than me should comment. Typically I don't earth the neutral of DGs, even 30 kW to 5 MW. For 'earth' earthing in dry soil, consider a Ufer Ground. To measure the earth resistance you need a special clamp on earth Resistance tester. For earth rods they need to be more than 2 meters apart, connected to each other then on-wards to the frame of the DG, and frame of the generator can, by exothermic weld connections for perfect conductivity.

__________________
If it eats, it's going to be trouble!
Reply
Power-User

Join Date: Apr 2007
Posts: 178
Good Answers: 3
#5
In reply to #4

Re: Earthing For 300 KVA DG

09/20/2007 9:16 PM

if you dont earth the neutral, there is no ground return path to operate any GFI (ground fault interruper) or ground sensing relay in the system. This may become a safety related issue, depending on the codes for your area and country.

Snakers

Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#6

Re: Earthing For 300 KVA DG

09/21/2007 1:13 AM

You can go for pipe type earth station as per IS 3043 OR IEEE 80 fro constaint of space. You can bore the earth and carry out the installation.

Copper / or other metal is to be consided to be resistat to corrosion in the type of soil, the important factor is the restance should be minimum so that the fault current is clear in safe time.

The earth condition is important.

nacon

Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#8
In reply to #6

Re: Earthing For 300 KVA DG

09/26/2007 11:08 PM

i agree both IEEE 80 and IS 3043 are the referance documents for DG earthing.At the same time soil chemistery report of your site is very impartent.

crm

__________________
Run silent run deep
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#7

Re: Earthing For 300 KVA DG

09/26/2007 7:21 AM

the distance between two earth pit is 1.5 times of the length of electrode.

__________________
BNDas
Reply
Power-User

Join Date: Jul 2007
Posts: 182
Good Answers: 1
#9

Re: Earthing For 300 KVA DG

09/28/2007 3:19 AM

Without a californium based hydrometer sensor, there can be no accurate measurement, at depth. That's maybe why some responders are willing to keep ignoring the details about detecting the moisture and compaction, at depth?

"Where's the dishwasher???? She's at her sister's... learning about harmonic ground imballance, the hard way".