NGR Connection Through ATS

08/08/2018 12:25 PM

In our project, we have both utility Transformer and generator power source. We are using 3-Pole ATS (automatic Transfer Switch). The grounding system is HRG (High Resistance Grounding). I would like to transfer the NGR to the neutral of utility transformer and Generator with the transferring the power source. Could please suggest how can I do it.

I am using a reversing contactor for the switching and operating it through an auxiliary contact of the ATS. I am not sure, I am doing the right thing.

Thanks,

- Lasam

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: NGR Connection Through ATS

08/08/2018 1:56 PM

The first thing you need to do is contact an electrical engineer who knows the codes and standards where your project is located.

If this was in Canada, I would tell you that.... with a 3 pole transfer switch, the neutral from the transformer and the neutral from the generator must be connected to a hard bolted neutral bar in the transfer switch and that any neutral to case ground at the generator needs to be removed.

As to where the HGR resistor gets connected depends upon where your utility service point is located.

If the secondary of your transformer is your service box, then the HGR resistor must be connected between the neutral of the transformer and the system grounding grid with nothing between them. As well, a connection between the neutral from the transformer must be bonded to your equipment bonding system.

If the transformer is not your service point from the utility system, the HGR needs to be connected to the utility service point neutral and the bonding system needs to be established. These two separately derived systems need to be interconnected from a grounding perspective.

Call a pro...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: NGR Connection Through ATS

08/08/2018 2:55 PM

A professional will cost money. CR4 doesn't charge anybody for services rendered.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: NGR Connection Through ATS

08/08/2018 4:40 PM

Interesting, your local utility allows customers to tamper with the utility mandated earthing methods, and utilizes High Resistance Grounding on its distribution transformers? Both are highly unlikely in systems where codes are followed.

It is much easier, safer, and cheaper to simply install a dedicated NGR in the generator neutral. Problem solved, and your AHJ (like North of 60), will be much happier.

Get a copy of the latest revision of IEEE Std C62.92.4-2014 for more info.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#4

Re: NGR Connection Through ATS

08/09/2018 9:38 AM

There is no problem technically having two earth connections on all the time (assuming you parallel the local generation with utility), as it is HRG at both locations.

Why complicate with transfer scheme for HRG!

__________________
Raghunath
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: NGR Connection Through ATS

08/09/2018 10:55 AM

"...assuming you parallel..." The OP is using an ATS, such switches are either/or and are not allowed to connect to both sources at the same time. Paralleling two sources requires a synchronizing panel, two independent electrically operated breakers, and an entirely different protective relaying scheme.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

North of 60 (1); raghun (1); RAMConsult (2); redfred (1)

Previous in Forum: Electrical Installation in Hazardous Area   Next in Forum: Electrical Question

Advertisement