Electrical Question

08/10/2018 11:31 PM

Hi, I have a question that I think is an electrical engineering question. Hopefully someone here can help me. I have an enclosed trailer with a 12v deep cycle battery hooked up to a 3000w inverter. What I would like to do is hook up a solar panel and charger to the battery and have the battery and inverter run an electric compressor. The compressor will be running a lot. I have a few people using roofing nailers for most of the day. I know that a compressor is a large draw on power especially when it first kicks in so I was thinking about hooking up a capacitor to handle the draw in power like a subwoofer for a car stereo. I figured at least in the long run it should help extend the battery life. Just not sure if it's worth it or not, a lot of people say capacitors are useless. Is this a good idea or would this set up even run a compressor all day? Any advice is appreciated

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: Electrical question

08/11/2018 3:27 AM

You really do need to find a local expert to help you with this, but here are a few of the sort of questions they will need to research on your proposal.

Firstly: What is the total storage capacity of the battery set? This is so that while the compressor is going through a run cycle, there will be enough available "power" to complete the fill cycle.

Next: What is the "inrush" current/power for your compressor to start? They might be able to determine this from the manufacturer's name plate.

Next: I'm already presuming that your inverter is large enough to actually run the compressor.

Next: Is the need to have enough solar collection to re-charge the battery set in each cycle over the day. In rough terms over the day you need to be able to collect more power (Efficiency of converters/inverters/chargers etc ) than the total amount to be used. Eg a 1kW system will only collect 8kWh over 8 hours (perfect alignment and such), If the compressor is drawing 4kw and running 30 minutes per hour it will not work. Your not topping up the tank as quick as you are draining it.

Your compressor probably already has capacitor start, so that might be an exotic experiment that gives you nothing. Your local expert might be able to determine how much power the motor would use if running "unloaded" so that you do not need to start the motor each cycle.

Good luck.

Oh, by the way, welcome to CR4.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#2

Re: Electrical question

08/11/2018 8:30 AM

Solar panels.. not panel

__________________
High Tolerance is Beautiful
Register to Reply Score 1 for Good Answer
7
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3

Re: Electrical question

08/11/2018 8:57 AM

A few points to ponder:-

Let's assume you have a 100 Amp hour battery and also assume that's at the standard 20Hr rate. So it can deliver 20 Amps for 5 hours, 5 Amps for 20 hours etc. until considered flat at 10.5 volts.

Also assume the compressor is half horsepower and that it is 120V, so it will draw around 12 Amps on full load and about 65 amps on starting - that's at mains voltage, multiply that by a factor of ten for the 12 volt current draw.

The inverter, depending on quality, will draw between one and 3 amps for the internal electronics and another 120 Amps to run the motor once it has actually overcome inertia - theoretically that gives you somewhere less than one hour running until the battery is dead flat, but you also have to take into account the Peukert's constant of the battery which will reduce that time by about another 10 to 20%.

Then there is the problem of the starting current of 65 Amps which equates to 650 amps from the battery. This will cause severe voltage depression at the battery terminals which will likely cause the inverter to turn off due to low input voltage after the first couple of starts.

With all of the above taken into account, you would see less than 30 minutes run time from a fully charged 100Ah battery even less with multiple starts - add 30 minutes for every extra 100Ah capacity that you have.

To adequately replace that power draw using solar alone would require approximately 2.5 kilowatts of photovoltaics operating under ideal insolation - not something that you can rely on most days, and you generally only get around 5 to 6 peak sun hours per good day after which solar input decreases rapidly.

"A lot of people say that capacitors are useless" for this and they are correct, the size of the bank required would be prohibitive.

I would suggest that you seriously consider cordless nail guns such as the Paslode gas ignition types - they are lighter, you don't have to trail air hoses around the worksite, and you could buy a fleet of them for less than you would spend bringng the compressor idea to fruition.

Register to Reply Good Answer (Score 7)
Member

Join Date: Aug 2018
Posts: 6
#4
In reply to #3

Re: Electrical question

08/11/2018 9:29 AM

It may not be a good idea because of how long the compressor will be running but maybe more info would help or it may still be useless.

Battery:

https://www.princessauto.com/en/detail/8d-commercial-battery/A-p8620171e

Capacitor:

https://www.ebay.ca/i/392021659354?chn=ps&dispItem=1&ul_ref=https%253A%252F%252Frover.ebay.com%252Frover%252F1%252F706-89093-2056-0%252F2%253Fmpre%253Dhttps%25253A%25252F%25252Fwww.ebay.ca%25252Fi%25252F392021659354%25253Fchn%25253Dps%252526dispItem%25253D1%2526itemid%253D392021659354%2526targetid%253D296570367735%2526device%253Dm%2526adtype%253Dpla%2526googleloc%253D9000864%2526poi%253D%2526campaignid%253D798988068%2526adgroupid%253D47089348212%2526rlsatarget%253Dpla-296570367735%2526abcId%253D1063836%2526merchantid%253D116255371%2526gclid%253DCjwKCAjwkrrbBRB9EiwAhlN8_C5Etoap2rj7u0ZlkBFvORigjy3EF0rLPV1G2Mf1uVn_iouI_TYrvhoCeOUQAvD_BwE%2526srcrot%253D706-89093-2056-0%2526rvr_id%253D1628383640832%2526rvr_ts%253D292137ab1650a99c1501bb92fff684af

Inverter:

http://www.canadiantire.ca/en/pdp/motomaster-eliminator-power-inverter-with-bonus-cables-3000w-1999930p.html

And I was thinking of also using a battery charger with the solar panel but it kind of defeats the purpose unless I can charge it over night and have it run all day slowly being recharged by the solar panel(s)

Charger:

http://www.canadiantire.ca/en/pdp/dewalt-30a-battery-charger-with-80a-engine-start-0111922p.html#srp

Register to Reply
Member

Join Date: Aug 2018
Posts: 6
#5
In reply to #3

Re: Electrical question

08/11/2018 9:36 AM

Also I forgot, this is the compressor I would like to run, but I could probably go smaller if it would make the battery last longer

https://www.homedepot.ca/en/home/p.15-continuous-hp-568l-200-psi-compact-workshop-air-compressor.1000529113.html

Register to Reply
4
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: Electrical question

08/11/2018 10:09 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 4)
Member

Join Date: Aug 2018
Posts: 6
#7
In reply to #6

Re: Electrical question

08/11/2018 10:24 AM

That solar power kit seems like overkill to me. And i have gas powered air compressors so I don't really need a generator.

The problem is my guys will leave the gas compressor running all day rather than turn it off every time they take a break or have to do something that doesn't require the nail gun. I only need the compressor to run when they are nailing which isn't steady for 8 hours a day. If I had to guess I would say the compressor would actually run for a total of 3 hours of a 10 hour work day. But kicks in to refill the tank like 100 times. My goal here is to stop wasting money on gas in a compressor that's used only half of the time it's running. Also to save money by running a compressor off grid and reducing carbon output at the same time.

Register to Reply
5
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #7

Re: Electrical question

08/11/2018 10:36 AM

So what you need is a start/stop on-demand compressor....?

https://www.homedepot.com/b/Tools-Air-Compressors-Tools-Accessories-Air-Compressors-Stationary-Air-Compressors/Automatic-Start-Stop/Gas/N-5yc1vZc9piZ1z0r35aZ1z0r88j

You're not going to find anything cheaper than on-grid power....off-grid = more money, otherwise everybody would be off-grid....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 5)
Member

Join Date: Aug 2018
Posts: 6
#10
In reply to #9

Re: Electrical question

08/11/2018 10:49 AM

I never knew those existed. Thank you.

Though they are pretty expensive. And still cost money for gas over time. Also I wonder if it uses more gas to turn back on and fill up than if it were already running.. Maybe that's why these are not as popular as ones that stay on?

I think the best option for me is to use the electric compressor on site where there is power and use the gas compressor when there is no power available. Should help save a little money in the long run

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11
In reply to #10

Re: Electrical question

08/11/2018 11:14 AM

Yeah plugging into somebody else’s electric is always going to be cheaper...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Aug 2018
Posts: 6
#12
In reply to #11

Re: Electrical question

08/11/2018 11:18 AM

I think originally what I really wanted to know - besides the solar power requirements which doesn't seem worth it - is if using a capacitor between the battery and compressor would help save the battery from being damaged because of the large draw in power.

What if my set up was more like this.. (since I always pop breakers on the average home)

Shore line --> Battery charger --> Battery --> Capacitor --> Inverter --> Compressor / Mini-fridge / lights / power tool battery chargers / alarm / etc.

then have my generator for back-up if there is no shore line.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #12

Re: Electrical question

08/11/2018 12:32 PM

Your compressor should already have a start capacitor, most all compressors have start capacitors as part of the system....that's those Mickey Mouse ears on the motor...Circuit breakers have a time delay built in to accommodate starting motors, if you are tripping breakers you are drawing overamps for an extended period of time, or you have a weak breaker that needs to be changed out...

Sounds like you're plugging in to 15amp circuits, when you need 20amp...Have you checked the amp draw on your compressor? Should be a FLA (full load amps) rating on the electrical tag on the unit....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: May 2017
Posts: 27
Good Answers: 3
#16
In reply to #7

Re: Electrical question

08/12/2018 11:42 AM

If the compressor is toggling often when not in use, it may be that the system has some leaks. I also wonder if the refill pressure is set too close to the full tank pressure and it's topping off often in short bursts.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #6

Re: Electrical question

08/11/2018 10:25 AM

....oh, and by the way, you'll still need the generator as a backup if you go with the solar system....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#14

Re: Electrical Question

08/11/2018 2:22 PM

IMO forget the capacitor... the battery itself is better than any capacitor as a low impedance source.
A capacitor is just something else to go wrong.
Keep it simple.
Keep the low voltage and high voltage sides nicely separated and isolated. Match the solar panels (with fuse and isolator) to the battery. Run the inverter from the battery suitably fused and isolated.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#15

Re: Electrical Question

08/12/2018 9:04 AM

I'd have to go with the cordless idea in reply#3. Compressed air as a power source is very inefficient; use it only when absolutely necessary. Cordless power is more direct with much less losses.

My solar-power setup included a home-made 12v charger from a lawn-mower engine driving a car alternator. You could use more than one alternator on one engine. That way, you could get substantial on-demand available power, with the batteries buffering the over-demand periods while continuously charging the batteries for the next over-demand period. Once the power-draw is over, and the charge-demand is near the solar capacity, you could turn off the alternators' engine at let the solar panels top-off the batteries.

__________________
Science is the "cookbook" for making things.
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#18
In reply to #15

Re: Electrical Question

08/12/2018 6:50 PM

The cordless guns that I was referring to in number three only use battery power to ignite a gas charge from a cartridge in the gun to create the driving force and for a small cooling fan.

The Paslode brand that I am familiar with will drive around 1000 nails from one cartridge and about 3 times as many on one battery charge.

For framing they are far superior to air driven devices and no hoses to drag around or trip over or have to pack up afterwards.

For fast work such as flooring or cladding they may be a little slow for some operators as they recommend firing only about 2 shots per second.

Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#19
In reply to #18

Re: Electrical Question

08/12/2018 7:30 PM

"...gas charge from a cartridge in the gun to create the driving force" I realize that, but it's still a better idea. I only added the solar/alternator system as an alternative, just in case. I guess I could have worded it better, but I don't like typing. Sorry.

__________________
Science is the "cookbook" for making things.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#17

Re: Electrical Question

08/12/2018 6:27 PM

You are overestimating the power available from the sun, especially if you're just trying to save some gasoline. The capacitor is a bad idea, and adds to the cost for no return on investment (ROI). Most fixed frequency static inverters are not very good at handling the highly inductive starting currents of a motor that are near its overload limit, and will self-destruct after too many 6.5 times rated current overloads. You could try a VFD (Variable Frequency Drive) which basically slowly ramps up the power to the motor, but they're expensive.

You already have all you need for either electric or gasoline operation, why throw all that extra money at something that may never return your investment in it?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#20

Re: Electrical Question

08/13/2018 10:41 AM

The output of the inverter is a pseudo sine wave made up of small pulses of DC coming out of high speed transistors that when put together in strings of varying pulse and gap durations, approximates an AC output. Putting a capacitor on the output is like putting a bomb on it as far as those transistors are concerned. Capacitors charge and discharge almost instantly and the charging current is pulled into them at the maximum available current rate. But pulling current through the transistors that fast exceeds there capacity to handle that and the little layers of silicon inside of them that facilitate their functionality will eventually break down, rendering them useless. At the same time, the capacitors, which like nice smooth AC sine waves, will absorb the harmonics created in that inverter pseudo sine wave, which will over heat them until their internal components break down. So basically it’s a race to the bottom to see who fails first, the transistors in the inverter or the capacitors.

You can get away with the capacitors built into the single phase motor because they are only on for a second when the motor is first starting, and they are in series with an inductor (the motor windings) which mitigates these issues. Adding your own capacitors outside will do nothing but harm.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Aug 2014
Posts: 33
Good Answers: 2
#21

Re: Electrical Question

08/13/2018 12:23 PM

I have read the previous replies. Your implementation is marginal depending on the compressor load. I believe that it will work however. There is a better supercap for your application https://www.digikey.com/product-detail/en/maxwell-technologies-inc/BMOD0058-E016-B02/1182-1027-ND/3079291, this device is designed to handle starter loads in auto applications.

Be sure to regulate the charging voltage maximum from the solar panels.

Good luck!

Register to Reply
Associate

Join Date: Aug 2014
Posts: 33
Good Answers: 2
#22

Re: Electrical Question

08/14/2018 4:05 PM

2Hp, 1500W 14A@110V 180A@12V. A typical storage battery is rated about 100AH. Your battery would take a damaging discharge after < 1/2 hour. You should size the solar panels for the 1500W average motor draw and use the battery/capacitor combo for startup of the compressor only. 1500W is a lot of solar panels.

Lithium storage batteries are available, they have higher maximum currents for the same storage size. They are also very pricey.

Register to Reply
Associate

Join Date: Aug 2014
Posts: 33
Good Answers: 2
#23

Re: Electrical Question

08/14/2018 4:09 PM

Lithium batteries have a longer life under severe duty such as your application.

Acid batteries are damaged every time they go below about 80% charge its about the worst technology for a storage battery ever devised, they are cheap to make.

Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bo1000 (1); Dennis R. Levesque (2); Jasonmcgahey (5); JE in Chicago (1); johnhotmer (3); JRaef (1); Just an Engineer (1); RAMConsult (1); SolarEagle (5); spades (2); user-deleted-1105 (1)