Voltage rating of power cables?

09/24/2007 7:04 PM

The voltage rating of power cables are given in phase/line volts, for example 3.5/6 KV

the question is: What is difference between voltage rating Uo/Un and Umax?

Umax = max pemissible continuous operating voltage, as defined by the manufacturers and is always greater than Uo even Un as well.

For the above example Umax = 7.2 KV

Register to Reply
Pathfinder Tags: cables
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: Voltage rating of power cables?

09/26/2007 7:32 AM

Umax is the maximum permissible continuous over voltage.

__________________
BNDas
Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#2
In reply to #1

Re: Voltage rating of power cables?

09/26/2007 5:35 PM

Thanks Biswanath, but, does it make sense?

The voltage rating for an electrical aparatus is (by difinition) the ceiling of this parameter for it to operate safely.

I guess a cable maximum permissible continuous operating voltage is enough for a user to be respected as it is bigger than Uo/Un . i.e. if the 1st. is given, the 2nd. is useless. Do you agree?

Regards... Samak

Register to Reply
Anonymous Poster
#3

Re: Voltage rating of power cables?

09/26/2007 7:27 PM

The insulation is calculated on the peak voltage not the rms, which is what you get when you touch it, so beware!

Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#4
In reply to #3

Re: Voltage rating of power cables?

09/26/2007 7:56 PM

Sorry!!!

The given value in Siemens Catalog as I said in the example doesn't match your answer.

Umax=7.2 KV

Uo=3.5 KV

Un=6 KV

However, Un = √3 Uo ,

but unfortunately, Umax ≠ √2 Un.

Regards... Samak

Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#5
In reply to #4

Re: Voltage rating of power cables?

09/27/2007 3:05 AM

You are quite close to the answer:

U0 is the voltage between the lines and the earth and neutral conductor.

Un is the voltage between the lines.

Umax must be the absolte maximum application of the cable, when no voltage differences between the conductors are present.

__________________
"Here we are now, entertain us"
Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#6
In reply to #4

Re: Voltage rating of power cables?

09/27/2007 4:55 AM

Find IEC 60183 and IEC 60885-3, Uo-U-Umax all defined inside, about partial discharge test dan voltage test.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #4

Re: Voltage rating of power cables?

09/27/2007 9:51 AM

Hi Samak, responding to your message on "Question for experts", but I'm not sure I can add much to this. Quoting both Uo = 3.5 and Un = 6 kV = Uo x √3 is redundancy, as you say, but I suppose it's better to have too much info than not enough! We sometimes in UK refer to 230/400 volt.

Agree with your response to #3, I was thinking that before I read yours. I can only assume that Umax 7.2 kV is rms value, so cable can stand √2 x that as a peak on a AC supply (ie not necessarily on a continuous basis).

I don't understand Gwen's #5 (last line). Perhaps it's just wording. I assume Umax (rms) voltage difference must not be exceeded, whatever the actual values on the phases are. But Umax relates to the complete cable, so max actual voltage is Un. Can you clarify please Gwen?

Cheers.....Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#8
In reply to #7

Re: Voltage rating of power cables?

09/27/2007 10:06 AM

As I tried to explain: Uo and Un are pointing to the potential difference between the lines in the cable, typical for tri faze setup.

Umax relates to the absolute level a cable can be used. Nothing to see with the peak-peak values and the line differences.

__________________
"Here we are now, entertain us"
Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

Abu Khansa (1); Anonymous Poster (1); biswanath.das (1); Codemaster (1); Gwen.Stouthuysen (2); Samak (2)

Previous in Forum: Isolation Transformer   Next in Forum: power transformers

Advertisement