power transformers

09/25/2007 12:33 AM

can we place temperature sensors inside the transformer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: power transformers

09/25/2007 1:42 AM

Physically, yes.

Seriously, I've never tried it. The problem with putting sensors on transformers is that the changing magnetic field may affect the sensor and/or its signal. A transmitter or temperature display may have a common-mode input or a filter that may reduce the interference enough to get a decent reading but you'll have to find that out from your instrument supplier.

However, I don't see any problem with trying it. 'Should be simple to do just to test it. Other than the standard safety measures of working with electrical equipment, it should be safe to do.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: power transformers

09/25/2007 10:46 AM

If this is an existing transformer, it will depend on the type of insulation. A cast epoxy resin would not have any openings for inserting any type of sensor. An air-cooled varnish insulated unit, or an oil-cooled unit would allow you to place an RTD or thermocouple directly on the winding insulation.

If you are having temperature concerns, it might be easier to use a non-contact thermometer. These devices use infrared measurement to determine temperature. You could mount one on the enclosure and point it at the windings to get pretty good temperature values. You could also use it to monitor temperature at various locations on the windings to check for hot spots.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#3

Re: power transformers

09/25/2007 11:50 AM

Yes, but you must decide carefully what you want to measure. There will generally be a sizeable temperature gradient even for steady state temperature. If you want copper temperature, you'll need to get good contact; I've used spot-welding and thermal epoxies. For large conductors, you may want to drill a hole and insert a thermocouple (as, for example, during fault currrent testing) to get interior short-time temperature.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: power transformers

09/25/2007 3:47 PM

Depends on the application, what are you trying to do?

__________________
jack of all trades
Reply
Commentator

Join Date: Sep 2007
Location: Watertown, SD USA
Posts: 68
Good Answers: 1
#5

Re: power transformers

09/25/2007 4:43 PM

We use thermocouples all the time - they work well, but require about 5-30 sec averaging. You can also use the change in resistance of the wires to calculate the Trise of the copper itself.

Most transformers, when properly tested are done so in an insulated box, with zero airflow, running at full load until a stabil temp has been reached for at least 5 minutes.

Hope this helps.

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: power transformers

09/26/2007 8:10 AM

Normally the manufacturer provides the means for monitoring the temp .If u want to place a sensor inside there must something specific.In oil cooled transformers u can place but you won't have any advantage as it it is difficult to locate the hot spot.For normal operations manufacturers provision is sufficient

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#7

Re: power transformers

10/06/2007 2:13 AM

Which part of Transformer you want to measure temprature ?

nascon

Reply
Reply to Forum Thread 7 comments