Chiller Controls

09/09/2018 2:43 AM

Hi, I'm new to HVAC Controls. I have attached the PID & chiller control box terminal drawing.

https://www.dropbox.com/s/y6intbfiy24lci9/Chiller%20Controls.pdf?dl=0

In the chiller terminal drawing wiring sheet, I could see the Interlock for chilled water pump but as per the PID, but the primary chilled water pump is not available.

1) What is the purpose of this Interlock?

2) There is a differential pressure sensor between the suction and the discharge side of each pump. What is the purpose of this differential pressure sensor.

3) How would the sequence of operation be achieved?

Register to Reply
Pathfinder Tags: Chiller Controls
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Chiller Controls

09/09/2018 3:03 AM

Generally speaking you have two types of controls, those for safety, to protect the system components, and those for controlling the system, that turn components on and off or regulate to match load...Most chilled water systems like this one regulate themselves to meet the load required....as the heat load demand increases the compressor loads up, this requires more water circulation, both chilled and condenser water....these are usually regulated by either pressure or temperature...

https://www.controleng.com/single-article/control-sequences-for-chilled-water-systems/2eb1feb85d57006c05373f54d9a37eeb.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#2

Re: Chiller Controls

09/10/2018 11:48 PM

The pump running contact can be used to inhibit the integral term of the controller.

If the pressure is low because the pump is not running, then the valve or speed setpoint controller output will try to go to max. If you then start the pump, then you'll get a big slug of water through the open valve, or full speed pump. The controller won't 'wind up' if it doesn't try to respond to an invalid process condition, such as pump stopped.

The differential pressure sensor is another method to determine if the pump is running. If the pump is stopped, and your sensor is not fooled by a check valve between the pump and the sensor, the pressure at suction & discharge will be very close. So you can inhibit the controller by using the pump differential pressure switch, if that is something you have.

You don't really need to establish a sequence, so much as to make sure your valve ramps and speeds allowed don't cause large amounts of water to move quickly, breaking pipe supports and cracking equipment casings.

Register to Reply Score 1 for Good Answer
Member

Join Date: Sep 2018
Posts: 6
#3

Re: Chiller Controls

09/27/2018 7:06 AM

Water Chiller Controls. Controls for regulating water coolers. Among other features the controls have functions for regulating temperature and capacity as well as for safeguarding against sub-optimal temperatures. Controls for regulating water coolers.

Register to Reply Off Topic (Score 7)
Register to Reply 3 comments