Calculating Excitation Voltage and Current from a Synchronous Generator?

09/26/2007 5:07 AM

Can any one explain me how can i calculate excitation voltage and current of 660MW generator having Xd=225.5% ,Xd"=21.4(sat), with terminal voltage of 22KV and power factor is .85.No other information is available????????????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Feb 2007
Posts: 60
#1

Re: synchronous generator

09/26/2007 7:09 AM

This is not possible.

You must have the saturation curve(V x Iexc) of the equipment as well as all the parameters concerning the primary side of the transformer, such as primary resistance and all the primary impedances.

Regards

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: synchronous generator

09/26/2007 7:56 AM

Excitation voltage is a design parameter and to be given by manufacturer.The parameters ref are for different purpose like to calculate Fault current etc.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#3

Re: Calculating Excitation Voltage and Current from a Synchronous Generator?

09/27/2007 12:28 AM

Contact the Manufacturer.

If you dont know the manufacturer return to line one of this comment

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

coconutpete (1); elbf2801 (1); nesubra (1)

Previous in Forum: high spped motors for vacuum pumps   Next in Forum: Rated Torque of a Servo Motor?

Advertisement