May i know in which standards ( like IS,CBIP ,CEA,Indian Electricity rules etc), the minimum panel to panel clearances are mentioned ?Like the clearance between HT switchgear to LT switchgear, clearance from wall etc.
As far as I can think, the IE Rules themselves have become obsolete now. They have been replaced with the CEA Safety Regulations, 2010. Having said, no such inter-panel clearances are mentioned anywhere in any of these rules/regulations, either.
Also, every state's local electrical inspector MUST follow the CEA Regulations and the NEC, 2011 only. Local Electrical Inspectors CANNOT have their own rules.
It up to each individual designer preference of the minimum panel to panel clearances like the clearance between HT switchgear to LT switchgear, clearance from wall etc. Make sure there is enough clearance for maintenance works that need to be carry out in that switchgears room. Otherwise, maintenance works will be very difficult of space or the clearance is not enough.
__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Regulation 37(iii) of Central Electricity Authority (Measures relating to Safety & Electric Supply) Regulations, 2010 is reproduced below
"37(iii) Every switchboard shall comply with the following,-
(a) a clear space of not less than one meter in width shall be provided in front of the switchboard;
(b) if there are any attachments or bare connections at the back of the switchboard, the space, if any, behind the switchboard shall be either less than twenty centimeters or more than seventy five centimeters in width, measured from the farthest protruding part of any attachment or conductor;
(c) if the space behind the switchboard exceeds seventy five centimeters in width, there shall be a passage way from either end of the switchboard, clear to a height of 1.8 meters."
The working clearance shall also be based on protection against internal arc fault