Hi Team.

I have connected two blowers in series controlled individually by VFDs. First blowers output is connected through a long duct to the second blower. Second blower output is connected to spray drier through a hot air generator. Iam facing challenges in maintaining air flow volume at the same time maintining the air velacity after second blower. request team valuable inputs and some reading materials in this regard.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33395
Good Answers: 1817
#1

Re: Air Balancing in Blowers in Series

11/07/2018 2:49 PM

Sounds like your hot air generator is causing some back pressure to the airflow...this might be minimized by placing the hot air generator before the second blower or ideally before both blowers...air turbulence can be a velocity killer, therefore the duct layout is very important and might require internal vanes for turbulence reduction...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#2

Re: Air Balancing in Blowers in Series

11/07/2018 3:37 PM

There will be a pressure drop as air flows through the duct and other parts of the system. The greater the airflow, the greater the pressure drop.

https://apps.engineeringtoolbox.com/air-flow-head-loss-a_16.html

The fans have a response curve (fan curves), pressure difference vs airflow. The lower the airflow, the more the pressure difference. The rest of the system (ducts, etc) have a curve of pressure drop versus flow rate - system curve. The resultant flow rate will be the point where the fan pressure-flow curve crosses the load line. (Total pressure loss equals total pressure supplied by the fans.)

https://www.saylor.org/site/wp-content/uploads/2011/09/Chapter-3.5-Fans-Blowers.pdf

If you have insufficient airflow, you need to either reduce the pressure drop or increase the capacity of the fans so that the operating point is at higher airflow.

https://www.captiveaire.com/MANUALS/AIRSYSTEMDESIGN/DESIGNAIRSYSTEMS.HTM#Fan_Total_Pressure

http://www.sunon.com/uFiles/file/03_products/07-Technology/006.pdf

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2009
Posts: 42
#3

Re: Air Balancing in Blowers in Series

11/08/2018 1:12 AM

Thanks

Register to Reply
2
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#4

Re: Air Balancing in Blowers in Series

11/08/2018 6:18 AM

Use the downstream blower VFD to control the required air flow. Add a pressure sensor in line at the downstream blower intake and control the upstream blower VFD with a PID loop to maintain a constant pressure at the downstream intake. This bi-passes any changes in pressure loss in the long feed pipe owing to different flow rates. Defining the downstream intake pressure as slightly positive, say +2psi gauge, makes setting the PID controller easier as it gives you both positive and negative adjustment options. The upstream blower flow must track the downstream blower flow in order to maintain the set pressure.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#5

Re: Air Balancing in Blowers in Series

11/09/2018 12:44 PM

I am facing challenges in maintaining air flow volume at the same time maintining the air velacity after second blower.

This may be obvious, but do you have any air filters that need cleaning or replacing?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2011
Posts: 8010
Good Answers: 286
#6

Re: Air Balancing in Blowers in Series

11/09/2018 6:19 PM

".... Iam facing challenges in maintaining air flow volume at the same time maintining the air velacity after second blower. ...."

Are these separate issues? Is the cross section variable? Might there be problems with continuity of the ducting?

Unless you have leaks or a nonobvious setup, except for small changes to density volumetric flow rate will be constant down the single duct series blower set up. Air velocity average for similar cross sections at different points in the duct will be simlar at steady state except for leaks and any changes in density.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#7

Re: Air Balancing in Blowers in Series

11/12/2018 12:06 PM

Are they positive displacement blowers?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jhhassociates (1); L.Ramamurthy (1); PWSlack (1); Rixter (2); SolarEagle (1); truth is not a compromise (1)

Previous in Forum: Glues Good with Polyethelyne and Gasoline   Next in Forum: Copper vs. Stainless Steel

Advertisement