Tandem Breakers

11/12/2018 4:14 PM

I am considering purchasing a 48 year old house. The house has a 125 amp breaker panel and the panel has several, probably over half of the breakers, tandem breakers in it.

I've done some research on the subject and it seems that overheating may be a problem and, that there is possibly a limit to the number of tandems in a panel.

Does the National Electrical Code limit the number of tandems in a panel in relation to the total amps or the total number of breakers? Also, there is no master breaker in the panel. I really don't like that. The only way to cut power to the entire panel is to pull the meter!

Thanks,

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Tandem breakers

11/12/2018 4:29 PM
Register to Reply Good Answer (Score 3)
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#2
In reply to #1

Re: Tandem breakers

11/12/2018 4:45 PM

Thanks Lyn. Good info!

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#5
In reply to #1

Re: Tandem breakers

11/12/2018 11:19 PM

GA from me old man! The first link I found especially informative. Thanks Pal!

__________________
Most people are mostly good most of the time.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Tandem breakers

11/12/2018 5:42 PM

There USED TO BE a limit to the total number of circuits (42), that is no longer the case (since 2008), so long as the load does not exceed the rating of the panel you can install as many breakers as you like.

But regardless of that lack of theoretical limitation, you still cannot install more circuits than the panel was designed to accept. So in most panels that can accept tandems there is still a feature called "CTL" which stands for "Circuit Total Limitation" meaning the breakers and panel are designed with rejection clip features of some sort, preventing you from putting the tandem breakers in slots not designed for them. Originally this was done to prevent you from exceeding the 42 circuit limit but now it is still done this way because it prevents someone from installing more circuits than the panel was designed for. So typically on LARFGE panels (i.e. 42 circuit and aove), no more than half of the spaces in a residential panel will be set up for CTL breakers, sometimes less. In 12 space panels, most of them now are not going to have limits, but you still need to use "CTL" listed breakers.

If your panel is older than 1965 it may have been installed prior those limits, in which case the breakers will be designed without the rejection features and you can buy what are referred to as "Non-CTL" versions of the tandem breakers. Note that it is illegal (by code) to install Non-CTL breakers into a CTL panel to get around the limitation and even if the panel doesn't have the rejection features, you must still obey the listing of the panel with regard to the total number of circuits, which should tell you on the info sheet, usually on the inside of the cover). So for example if the info says "12-24", that means it has 12 pole spaces, 24 circuits maximum, meaning if you use tandems in all of the spaces so you can put 24 circuits in it. But if it says "12-18", that means there are 12 slots, but only 6 off them can accept tandem breakers, so 18 circuits maximum (12 tandems + 6 more single poles).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Tandem breakers

11/12/2018 7:34 PM

I would bring the electrical up to code... in a house that old no telling what's been done...Here 150 amp panel is minimum, and a main breaker is required next to the meter...This external main is for safety, in case of fire the firemen can cut the power to the house...I always check breaker operating temperatures with my IR heat gun...this identifies any bad connections or overloaded circuits...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#6

Re: Tandem breakers

11/13/2018 6:25 AM

As for tandem breakers, while I don't care for them personally, my house panel is chock full of them. (My home, built in '89/'90, 150A service. Siemens panel and breakers.) Outside of a shared neutral kitchen circuit, a 20A SP breaker for the clothes washer, and a 20A SP for the garage workshop, every branch circuit is on 20A tandem breakers. I have lived in the house since new and have never had any issues with heat in the panel.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Tandem breakers

11/13/2018 7:21 AM

The Surveyor will indicate whether or not there is a cause for concern in the Report that might accompany the decision to buy.

If in doubt, consult a qualified local Electrician to carry out a detailed inspection.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Tandem Breakers

11/13/2018 9:15 AM

I forgot to address the lack of a Main Breaker. That would be illegal. The main disconnect must be there somewhere, it doesn’t need to actually be IN the panel, it can be ahead of it. Are you sure there isn’t a main breaker outside underneath the meter behind a lift-up panel? That’s a common way of doing it in some areas.

The only other possibility is that when originally installed, there were only 6 breakers in the entire panel, in which case it falls under what’s called the “six hand rule”, meaning a firefighter can kill all power in the building with no more than 6 movements of his hand, hence 6 breakers maximum. If someone added circuits later by using twins, that became a violation and a Main would need to be added.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#9
In reply to #8

Re: Tandem Breakers

11/13/2018 9:24 AM

Are you referring to the picture in my post or the OP? If my post, no worries. My main disconnect is a 150A CB, outside next to the meter box. Technically making my main panel, a sub panel. Notice the segregated neutral and ground buss bars.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #9

Re: Tandem Breakers

11/14/2018 6:27 PM

I was addressing that to the OP.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#10

Re: Tandem Breakers

11/13/2018 3:16 PM

Thanks to everyone for the helpful comments. I'll be much better armed for the inspection. I'll be meeting the inspector, with my real estate agent, tomorrow.

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Tandem Breakers

11/14/2018 3:52 AM

Everything can be "brought up to code", i.e. improved so as to align with current installation best practice as determined by Standard. It is whether or not the improvement is worthwhile that is the issue, with items of primary safety concern being at the top of the improvements list. In the UK, regulations are not retrospective, and plenty of installations exist that do not comply with current code. However, it would be inappropriate to carry out new installations that are not up to current codes.

Best to review the inspection report afterwards, and carry out a "value judgement".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12

Re: Tandem Breakers

11/14/2018 8:57 AM

My suggestion is to upgrade the electrical system by having a qualified electrician install a 6 main-lug-only combination meter base/panel on the outside,below the current meter location.

Feed the inside panel from one of the the outside breakers,and move all 240volt loads to the outside panel breakers, such as electric range,water heater,electric dryer, and Central Air/heat Pumps/heat strips.

This will unload the major loads from the old inside panel, leaving only receptacles and lighting loads on the old panel,and eliminate the need for tandem breakers.

Remember to separate the Neutral(Grounded) and Equipment(Grounding) grounds in the inside panel since it is now a sub-fed panel.

Factor this expense in when negotiating a price.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#14
In reply to #12

Re: Tandem Breakers

11/15/2018 6:57 PM

Thanks for the advice. I met the inspector at the house. He said the existing, old panel (125 amp) allows the top breakers to be used as the main breaker, if wired properly, which it was not.

I'm simply asking for the replacement to an up to date panel (200 amp) which can properly carry the load.

Thanks again,

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Deefburger (1); Don in LA (3); HiTekRedNek (1); IanR (2); JRaef (3); lyn (1); PWSlack (2); SolarEagle (1)

Previous in Forum: Power Fuse Documentation   Next in Forum: Questions About Electrical Engineering

Advertisement