Metering Dirty Air Flow in an Air Pollution System

10/02/2007 11:14 AM

I need suggestions as to be best way to accurately meter "dirty" air flow at temps 150 - 300 F. System has a 48 inch diameter main duct. 10ga steel. sytem pressure 10-15 inches WC Chuck

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Metering Dirty Air Flow in an Air Pollution System

10/02/2007 11:45 AM
  1. Pitot-tube-and-manometer; do a traverse across the duct?
  2. Ultrasonic flowmeter looking at the velocity echoes coming from the moving dirt particles?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Oct 2007
Location: Olympia Fields, IL
Posts: 2
#2
In reply to #1

Re: Metering Dirty Air Flow in an Air Pollution System

10/02/2007 5:09 PM

Thanks for the prompt response.

Pitot tubes tend to get dirty and thus give false readings. Where can I find a source for the ultrasonic flowmeter?

Register to Reply
Power-User

Join Date: Jun 2005
Posts: 394
Good Answers: 1
#3
In reply to #2

Re: Metering Dirty Air Flow in an Air Pollution System

10/03/2007 9:08 AM

A thought. What if you bleed control air to the pitot tube -- using an adjustable restrictor -- actually you might need two, for Tp and Sp. Enough so that the orifices on the tubes were kept clear. Calibrate the resultant signal against a standard pitot tube for the range of velocities you are interested in.

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#4
In reply to #3

Re: Metering Dirty Air Flow in an Air Pollution System

10/03/2007 9:31 AM

A second thought, install solenoid valves and periodically sequence them to isolate the P transmitters and blow out the pitot statics with compressed air. The shut off the "blow off" air and reopen to the P transmitters. Depending on dirt in system, one or two 15 second blasts should keep the system clean.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: Metering Dirty Air Flow in an Air Pollution System

10/04/2007 5:46 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply