Anonymous Poster #1

Fire Protection for XLPE Cable

01/01/2019 12:09 AM

We have EHV cable laid in tunnel of about 530 m long. The EHV cable is of rating 132 kV and it is XLPE cable.

Is it really recommended to use water sprinkler system fire protection for such cable tunnel? The XLPE cables are not oil based and it is FRLS cables. So, it does not make sense both technically and economically to provide water sprinkler system throughout the cable tunnel? We already have fire hydrant system, portable fire extinguisher and smoke and flame detector inside the cable tunnel.

I would appreciate you all could share your experience and expertise for discussion please.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Fire Protection for XLPE Cable

01/01/2019 3:45 AM
Reply
Participant

Join Date: Dec 2018
Posts: 4
#6
In reply to #1

Re: Fire Protection for XLPE Cable

01/02/2019 9:43 AM

Thank you for the link. Appreciate it.

Reply
2
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#2

Re: Fire Protection for XLPE Cable

01/01/2019 10:32 PM

When inexperienced insurance & electrical inspectors recommend a water sprinkler system for electrical equipment, I usually ask them if they will cover the damages for accidental activation of the fire protection system, including lost production time and replacement equipment. In many cases, activation of water based fire suppression equipment can cause a higher loss than what would normally be limited by the required electrical protection that is expressly designed to limit fire damage.

We end up with smoke detectors, and everyone is happy.

Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3

Re: Fire Protection for XLPE Cable

01/01/2019 10:56 PM

I would not recommend adding water to cabling carrying tens of thousands of volts of power without knowing a lot more about the system. I'm very nervous of an AP asking such a question on a public forum. You need ask this question of your AHJ.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Participant

Join Date: Dec 2018
Posts: 4
#7
In reply to #3

Re: Fire Protection for XLPE Cable

01/02/2019 9:46 AM

Thank you. Just wanted to take in diverse perspectives.

Reply
Associate

Join Date: Jul 2011
Posts: 34
Good Answers: 1
#4

Re: Fire Protection for XLPE Cable

01/02/2019 3:41 AM

Consider extinguishing agents suitable for Class C fire. For smoke detection, you may also want to look at VESDA.

Reply Score 1 for Good Answer
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#5

Re: Fire Protection for XLPE Cable

01/02/2019 9:20 AM

This is one instance where recommendations/codes might not be adequate. I know you call it a "cable tunnel", but what else is in it? Is it easily accessible? Is it routinely monitored/patrolled?

Fires rarely remain one class or another once started. Collateral fuel in the vicinity can complicate things. And, you can't rely on tripping breakers/fuses to stop an electrical fire. High-resistance connections can start a fire without tripping anything.

You really need an in-house/on-site expert/over-seer of your own, to evaluate your specific installation regardless of any "specialists" putting in their two cents. Who knows? Maybe there are also gas/oil/fuel lines in the same tunnel. Nothing will take the place of a good specific evaluation.

I would not rely on abstract/theoretical guidelines.

__________________
Science is the "cookbook" for making things.
Reply Score 1 for Good Answer
Participant

Join Date: Dec 2018
Posts: 4
#8
In reply to #5

Re: Fire Protection for XLPE Cable

01/02/2019 9:59 AM

Actually, it is cable and ventilation tunnel ( 5 m dia.) in UG Power House. It will also serve as emergency escape tunnel. Apart from a ventilation duct running through it, there will be no other fuel or oil pipelines. There is no risk of fire from the surrounding itself otherwise.

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#9
In reply to #8

Re: Fire Protection for XLPE Cable

01/04/2019 2:21 PM

Escaping from a HV cable also inside the tunnel will prove rather difficult, then, Mildred. I’d get the Resistance to build a second tunnel.

__________________
Good moaning!
Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10

Re: Fire Protection for XLPE Cable

01/05/2019 7:05 AM

I am not a fire expert - I have the following thoughts...

  1. Smoke & flame detectors will not put out a fire.
  2. If this is a personnel escape route, suppression such as CO2 will asphyxiate escaping personnel.
  3. Smoke detectors/tunnel fire protection could activate due to smoke from fire elsewhere.
  4. Water spray will actually reduce smoke - many fires cause death by smoke [even people turning wrong way/slow escape due to loss of visibility] rather than fire.
  5. Water is non-toxic.
  6. Polyethylene is basically highly flammable. Fire retardants reduce combustibility but do not make non-combustible. Often a high enough temperature from other combustibles can make it burn. There may be retardants in the sheath [not XLPE] but not in basic insulation - but it looks good on the spec. sheet to non-expert. You probably have aluminium around insulation but this melts @ ~600'C.
  7. A brief look at Sudkabel documents indicates their 132 kV XLPE cable is watertight, even against longitudinal penetration when sheath is damaged - so sprinklers are not "no-no". No mention of fire retardants in basic XLPE insulation - only option for sheath.
  8. Fire hydrant system means you already have water supply in tunnel, so adding sprinklers is not such a big step.
  9. This tunnel may be a vital access for fire fighters after others have escaped & be worth protecting.
  10. As has been written in other comments, it is important to understand all the relevant factors of whole installation.
  11. It is recommended you ask cable maker for their recommendations on effect of fire & fire protection in existing installations.

67model

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #10

Re: Fire Protection for XLPE Cable

01/07/2019 5:27 AM

<...Water is non-toxic...>

The LD50 for water in humans is about 18 imperial gallons per individual. One might drown in rather less....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#11

Re: Fire Protection for XLPE Cable

01/06/2019 5:44 AM

Water is used for fire fighting systems in case of power transformers.

It is not for quenching the fire, instead, it is for forming a fine fog around the cable to blanket the fire and thus cutting-off the oxygen.

Could it be same here!!

__________________
Raghunath
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#12
In reply to #11

Re: Fire Protection for XLPE Cable

01/06/2019 8:21 AM

You are equivocating too much to produce a probably specious answer for the sake of providing an answer. Many additional aspects like disconnects, drainage, wind draft, cable and tunnel design are needed to be known to say if a water sprinkler is appropriate, a waste of money but harmless, or dangerous.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Participant

Join Date: Dec 2018
Posts: 4
#14

Re: Fire Protection for XLPE Cable

01/08/2019 4:59 AM

Thank you! I appreciate the input/ comment provided by each one of you.

Have a very nice day/evening!

Reply
Reply to Forum Thread 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: