Relay Minimum Phase Trip Current

02/13/2019 9:09 AM

How to choose relay/Auto Recloser minimum phase trip current?

Register to Reply
Pathfinder Tags: power protection Relay
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Relay Minimum Phase Trip Current

02/13/2019 10:47 AM

NFPA 72 or BS 71 or IS SP 30, and any local codes must be followed.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Relay Minimum Phase Trip Current

02/13/2019 2:50 PM

Using British Standard 7671, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Relay Minimum Phase Trip Current

02/13/2019 11:29 PM

Depends on the load connected downstream. It is not less than 125% of the connected load. It can be higher but typically not more than 1/10th of the available minimum short circuit fault current at the location.

If it is auto recloser in the field with long overhead line downstream, there is a possibility that the available fault level at the farthest point could be quite low and the phase current setting should be below that value for protection to be effective.

__________________
Raghunath
Register to Reply Good Answer (Score 2)
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#4

Re: Relay Minimum Phase Trip Current

02/14/2019 1:15 AM

Hi Fazlay

The relay for OC overcurrent and EF earthfault needs to be chosen such that the current input to the relay matches the secondary current of the protection current transformers CTs.

The minimum phase trip current should have been established at the design phase of the system depending on how the load is fed, underground cable, aerial cable or a combination. The tripping time also needs to be set for various fault levels to account for close in faults and remote faults as does the minimum pick up level which accounts for short term motor starting loads which initially appear as short circuits on the phases if used as DOL direct on line.

The use of auto reclosing is dependant on the final load and the number of intermediate trip points between the supply and the end of line. Auto reclosing in my experience has been used on transmission lines where it is used to limit and isolate the number and causes of power outages. Auto reclossers usually have a number of instantaneous trips and time delay trips which hopefully give time for intermediate protection to operate and isolate the faulty section of line.

Regards Stef

__________________
Hare today, goon tomorrow!
Register to Reply