I have just finished a wee endurance test that has produced some interesting results that I would like to share.

The test subject was an electronic PID heating controller that we manufacture which uses a 25A single-pole SSR of the puck-type, to control the heating of a 1750W heater. We wanted to see if we could replicate the results observed in field trials, where some internal components (heatshrink, PVC wire insulation) were degrading due to heat.

The SSR's datasheet indicates that the maximum temperature it should be operated at is 80°C.

We put our controller inside a makeshift 'oven' and ran it at an oven temp of 50°C for a week, and then when that did not kill it, we ran it for another week at 70°C, all with a 2200W load.

Here is a plot of the results:

Note that the red trace is the SSR temp, measured on the backplate of gthe controller that the SSR is bolted to. It has now spent two weeks at temperatures that I was predicting would kill it within hours. And still it runs fine.

__________________
paulusgnome
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Solid State Relay Endurance

02/21/2019 10:40 PM

If the gates are driven properly and the devices protected against such things as voltage spikes SSRs can take some abuse (such as operating them outside recommended ambient temperature parameters).

I see a potential issue with your fault method methodology however. Have you tried checking and replicating loose SSR press-on crimp power terminals or similar?

Like power relays, loose power connections in the field can cause overheating and premature failure even if the device is normally operating well below the maximum power requirements. Operating normally at an increased ambient temperature will NOT test for this.

I have seen this first hand where an overheating issue was caused because a batch of press-on crimp connectors were out of tolerance and some in the batch were very loose. It would be a very good idea to look into this if your product also incorporates press-on crimp connectors.

__________________
jack of all trades
Register to Reply Good Answer (Score 3)
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#4
In reply to #1

Re: Solid State Relay Endurance

02/21/2019 11:48 PM

Thanks for the heads up on that Jack.

I will definitely see if I can simulate a crimp failure. I am thinking that a short tail of N80 crimped between terminal and wire tail will be a good start.

We have seen crimp failures in the field, but they are very rare.

These controllers often run 24/7 for weeks at a spell, usually they see a 30°C ambient, perhaps a little more, but some field units seemed to be getting a bit warmer than we could ever get them in our testing. Not failing, but enough to warrant a deeper dig. Hence the cook-up.

I am astonished, but pleased that the SSR has taken this much punishment without failing. My prediction, made after the first week at 50°C and having just cranked it up to 70°C, was that it would expire within 24 hours. Very confidence-inspiring.

__________________
paulusgnome
Register to Reply
2
Member

Join Date: Feb 2019
Posts: 5
Good Answers: 1
#12
In reply to #4

Re: Solid State Relay Endurance

02/23/2019 10:49 AM

One thing users of SSRs tend to overlook is the thermal contact surface for the base of the relay. Make sure the baseplate surface is completely flat - no proud rivets or swarf on the mounting areas. Check the mounting position for flatness, rigidity and proximity to other heat producing components and use plenty of heat-sink compound spread thinly over the whole baseplate area. Make sure mounting screws are fully tightened and locked, especially if there is any vibration

It's definitely worth spending a bit of time getting the mounting right if you want get maximum benefit from your SSR and your oven.

As others have already mentioned make sure the terminal contacts are tight and as big as possible and they will act as additional heat sinks

Register to Reply Good Answer (Score 2)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#18
In reply to #12

Re: Solid State Relay Endurance

02/24/2019 8:40 AM

I would add that short term tests do not replicate aging and thermal cycling effects.

The heat-sink compound do ages. Some brands more than others. It can harden when subjected to high temperature or be pumped out when fresh if frequent thermal cycles are experienced.

Do you use the same thermal compound that production use? Do they all know how to apply it? Maybe the "new" assembler has not been trained properly.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #1

Re: Solid State Relay Endurance

02/22/2019 9:43 AM

Yes, a very good point on the crimping of the wires to connectors and pins. Loose connections make for unanticipated hot spots.

I would also examine the strain relief and mechanical dressing of these overheating hookup(?) wires. Remember, with hookup wires the metal conductor is the only internal mechanical support. Consistent vibration of hookup wires during shipping and operation can induce metal fatigue breaks in the conductor. This is more obvious with the complete failure of solid or single strand conductors but in multi-strand wires this failure mode will only appear as extra self heating of the wire.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Solid State Relay Endurance

02/21/2019 10:48 PM

It could be a bad batch of relays...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Solid State Relay Endurance

02/21/2019 11:23 PM

I would expect at high heat an SCR would fail in turning OFF and likely closer to maximum currents. I doubt your 1750W heater uses 70 VAC so if you were using 120 VAC you were only just over half the maximum RMS current.

At this hour, my solid state textbooks will remain on the shelf.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: Solid State Relay Endurance

02/22/2019 3:15 AM

You state that some internal components,such as heat shrink and PVC wiring insulation,you did not mention any failures internal to the SSR.

If it only the insulation that concerns you,then upgrade to a higher temp insulation,such as fiberglass,etc.

However, if it is really an internal active component,and the application is frequently switched or modulated you need to duplicate the same conditions to give valid results.

Are the field failures a result of the input or output failure?

Triac's and SCR's require power to be applied before the gate is activated.

A weak or out of spec internal capacitor could cause failure of the Triac by allowing the trigger to gate prematurely.

As previously mentioned,I would test the SSR under a switching load.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#7

Re: Solid State Relay Endurance

02/22/2019 11:15 AM

Yeah, uncertainty is a +/- thing. I doubt if you conduct the test with not just one but 10, probably some will fail or may be not.

You must have taken a greater design factor that's why.

The main purpose is to make it close to fail as you designed it. Otherwise, it might cause too much for the purpose which is bad for bean counters and your company's business as a whole.

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#8

Re: Solid State Relay Endurance

02/22/2019 3:23 PM

Perhaps after taking some of the good advice suggested in the comments here (switching loads, bad crimps, meaningful sample size, etc), if you become very confident about the durability of your controller in high heat, consider making a video (for marketing or just bragging, either way sent a copy to us) in which you use the backplate of the controller to fry an egg...each day for a week.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#9

Re: Solid State Relay Endurance

02/23/2019 12:58 AM

Your test results are no surprise.

Automotive components with similar heat ratings are typically "design verified" by testing at up to 80 Deg C ambient and also down to -40. Storage temp ranges even higher/lower.

Failure usually happens as the result of multiple simultaneous deviations. For instance, your "test" might actually be cooling the device by sinking heat away. Testing ovens sometimes have air flow that can assist the DUT by blowing heat off the item.

The manufacturer's max temp has to consider all applications. Encapsulant coating of the board and then installed inside a closed cabinet could have device surface temps far greater than you imagine.

A separate test might be to insulate the DUT and monitor its temp as you increase the loading. This will give you some indication of the capability of the relater insulation and nearby items you have observed failing.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#10

Re: Solid State Relay Endurance

02/23/2019 6:22 AM

Typically as experienced in the field, SSR failures that are heat related starts to be more common is when the Thermal compound between the heatsink and the device started to deteriorate and dries up...

Most of the time the poor conduction of heat is the root cause..

__________________
vsar
Register to Reply Score 1 for Good Answer
Member

Join Date: Feb 2019
Posts: 5
Good Answers: 1
#11

Re: Solid State Relay Endurance

02/23/2019 9:34 AM

We carried out a series of tests last year to achieve EMC compliance for our SSRs and the test rig got so hot that it melted the label off the SSR and heated the test room so much that the doors got jammed with the expansion. SSRs are pretty tough components, much better than electromechanical relays which tend to burn out contacts and sometimes explode - not a good thing when they are installed in a petrol pump.

The only drawback with standard SSRs is they produce a lot of conducted noise - well above the guidelines in the EMC Directive and you have to add line filters which tend to be expensive and problematic. This is why we now make EMC compliant SSRs which produce hardly any noise in use.

Register to Reply
Associate

Join Date: Jan 2011
Posts: 52
#13

Re: Solid State Relay Endurance

02/23/2019 10:31 PM

I could not read/understand the graphs. But...

Kinda looks like temperature *may* not be the item associated with early failures.

You may want to look at other factors... Humidity? Airborne pollutants? Particulates?

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#14

Re: Solid State Relay Endurance

02/23/2019 11:19 PM

I've been using/contributing to CR4 for almost 13 years, and I continue to be amazed and highly disappointed that CR4 does not provide some means of attaching higher-resolution images.

I can't read any of the text on your graphs, even after enlarging and using a loupe. Can you please provide a text version of the legend for your graph, so we can have some idea of the meaning thereof?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#15
In reply to #14

Re: Solid State Relay Endurance

02/24/2019 2:02 AM

Legend is:

Red Trace (top) = SSR temp, measured between the mounting screws with a thermocouple stuck to the back panel(1.5mm s/steel).

The next two traces Orange and Yellow are in the controller under the controller PCB and in the wiring loom.

The green trace is the oven temp.

The lowest trace Blue is test room ambient.

So the SSR spent a week with the measured temp at a bit over 115°C, followed by a second with it mostly over 120°C. There is a 2-day spell just after the start of week 2 where the PID control was used on a 1-second switching cycle to give this function some exercise.

The load was a 230V load so line current was 9.7A.

Yes, the SSR is overframed but they are cheap enough that using them seems like good insurance against unreliability. Especially if they can take this level of abuse - far more than would be possible in the field where most of our experience with this controller has been acquired.

__________________
paulusgnome
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#16

Re: Solid State Relay Endurance

02/24/2019 4:47 AM

You state in your OP:"(heatshrink, PVC wire insulation) were degrading due to heat."

If this is the only problem and not an internal component failure then as others have stated,the likely cause is a high resistance connection(crimp or other connection inside of the heat shrink.An undersized conductor can also result in excessive heat,especially at junctions.

I recommend properly sized THHN conductors with a 90C rating.

A #14AWG copper minimum is recommended.Aluminum conductors are seldom used anymore in small gauges because they are problematic and require special splicing connectors when connecting to copper.

I may be preaching to the choir,but below is a link that explains the variables that can cause conductors to overheat.

I have used SSR's for over 30 years with no problems,even with high inductance loads,such as motors,etc.

https://iaeimagazine.org/magazine/2000/03/16/wire-temperature-ratings-and-terminations/

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17

Re: Solid State Relay Endurance

02/24/2019 5:04 AM

Ask the user to provide a sample of the wire with the crimp or junction attached and make certain that the proper crimp tool was used.I have seen many instances where the crimp was done with lineman pliers instead of a crimp tool and gave problems with overheating.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Member

Join Date: Feb 2019
Posts: 5
Good Answers: 1
#19

Re: Solid State Relay Endurance

02/24/2019 10:14 AM

This is an example of an electromechanical relay fitted in supermarket petrol pumps - 30A relay controlling a 3/4hp motor! I have replaced hundreds of these and they all show serious damage to the contacts! Downtime costs, (loss of sales) £10k/day.

SSRs do break down, (usually one of the back-to-back thyristors goes short circuit), but I have only ever seen one that 'blew up' so the reliability is far superior.

By comparison this is a solid state relay undergoing EMC testing - yes 'components' ARE required to comply with EMC Directive 2014/30/EU, (at least in this neck of the woods) and definitely in sensitive environments.

The small single phase SSR puck in the lower centre of the picture will switch all 10 of those 2.5kw hot plates without any problem, (apart from wrecking the test room with the heat).

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#20
In reply to #19

Re: Solid State Relay Endurance

02/24/2019 11:14 AM

Always do a carriage return before inserting an image, so the image starts at the left. Once the image appears, click on it to select it, then drag a right corner of the image to the right side of the window to enlarge it to usable size.

Also, on that first image, use your image editing software to lighten the shadows. That's easy to do in Photos on a Mac, I presume there is similar software on PCs.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Member

Join Date: Feb 2019
Posts: 5
Good Answers: 1
#21
In reply to #20

Re: Solid State Relay Endurance

02/24/2019 11:57 AM

Thanks for that - not the easiest way to submit pictures on this site and I tried every which way to do it, but thought they might be of general interest.

Tom

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#22
In reply to #19

Re: Solid State Relay Endurance

02/25/2019 5:19 AM

Hello, you may have provided another clue to the concern.

In use, the controllers seem to be intended for pump (motors) and such. Testing with a resistive load, especially when switching can provide significantly different results.

Switching incandescent headlamps (DC 21V) provides inrush currents typically 7x the SS condition. Heater elements seldom have the same characteristics as the load experienced in the field.

EMC from switching of heaters could be significantly different from switching motors.

__________________
Just an Engineer from the land down under.
Register to Reply
Member

Join Date: Feb 2019
Posts: 5
Good Answers: 1
#23
In reply to #22

Re: Solid State Relay Endurance

02/25/2019 6:16 AM

One of our Customers commissioned an independent test house to carry out comparison EMC tests using several solid state relays loaded with resistive and inductive, (6 electric motors) loads. The only relay which successfully passed the conducted emissions test was the one we manufacture, but it was interesting to note that the inductive load tests produced less noise than the resistive so that's the test we now use for certification. All waveforms are available if anyone is interested?

Inrush current is less of a problem with thyristor SSRs which can take 1,200A surges, but you have to be careful when selecting line fuses and circuit breakers. Surges such as this can occur in localised generator situations such as on ships.

With inductive loads we have found that the worst case is when switching off at peak waveform. The back emf causes arcing across contacts in electromagnetic relays and contactors, but SSRs seem to take the surges with no apparent damage.

Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#24
In reply to #19

Re: Solid State Relay Endurance

02/25/2019 8:17 AM

Do you guys not use inter-phase contacts dealing from low to high voltage/power lines, instead use SSR? I don't know if that's a good practice.

I am gladly will be hearing any objection.

Register to Reply Score 1 for Off Topic
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#25
In reply to #24

Re: Solid State Relay Endurance

02/25/2019 1:31 PM

This comment appears to be totally unrelated to anything being discussed here, what exactly are you talking about?

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#26

Re: Solid State Relay Endurance

03/03/2019 8:42 PM

I didn't see anyone ask about the brand name of the SSR.

FOTEK has so many China vendors that make counterfeit copies, as well other brand names.

I had a failure of a 25amp SSR powering a radiant heater of 10amp. The TRIAC was not bonded to the back shell of the SSR. This is inside a potted assembly.

My search back then I found a guy who had an eBay auction to advertise this fact of counterfeit SSRs he experienced.

Forgive me if this issue was brought up as a possible root cause.

__________________
ignator -
Register to Reply
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dkwarner (2); Flook (5); gutmonarch (2); HiTekRedNek (3); ignator (1); jack of all trades (2); Just an Engineer (2); KT4YE (1); marcot (1); Paulusgnome (2); redfred (2); SolarEagle (1); truth is not a compromise (1); vsar (1)

Previous in Forum: UPS and Power Line Noise   Next in Forum: Charging Capacity and Amperage of Charging Unit

Advertisement