UPS and Power Line Noise

02/21/2019 12:39 AM

I was wondering if there is a simple fix to a UPS problem we have. We have a small pumping skid with a PLC and a radio system for SCADA. The system is powered from an APC model BR1000G UPS. The pumps are two 100 hp VFD driven pumps. THe VFDs are Eaton SVX 9000. These work great until the pumping units has to work under higher loads and at motor speeds above 80%. Under high loads the noise from the VFD causes the UPS to see a voltage drop and it switches to battery operation. The UPS will switch back and forth until the battery is completely drained and the unit shuts down. If we run just one pump at 100% load there is no problem but with both running; the drives must run below 75-80%. This allows the system to keep running but cannot keep up with flow rates needed.

I know there are line filters for the 480v inputs to the line side of the VFD, some of the earlier versions of this setup had those and we have no problems. The newer versions have no filters though. What I was wondering was if there was a low voltage (120/240V) filter we could install that would eliminate this problem or a similar sized UPS we could install that would be less susceptable to the noise level.

__________________
deanpavil
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#1

Re: UPS and power line noise

02/21/2019 3:22 AM

You can try and filter the supply to the UPS (voltage stabilisers etc e.g. https://www.claudelyons.co.uk/products/voltage-stabilisers) but at the end of the day most folks would be better to fix the problem at source and filter the VFDs. Always difficult - either throw solutions at it until one sticks or investigate properly and find the actual source of the problem.

Bear in mind that if your local UPS can't cope then you are also sending those same harmonics/dips etc back up the supply chain and may be affecting other gear.

__________________
rogerggbr
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: UPS and power line noise

02/21/2019 4:09 AM

It sounds as though the bottleneck is the cables. Have a qualified local Electrical Engineer assess the cable sizing according to local electrical codes, and recommend improvements.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: UPS and power line noise

02/21/2019 5:29 AM

You have harmonics generated by non linear loads.

These harmonics can generate excessive currents in the neutral conductor.

The NEC recommends doubling the size of the neutral in such cases to prevent damage to wiring and equipment.

There are many ways to mitigate the harmonics as well.

These issues are covered very thoroughly in this link:

https://www.researchgate.net/publication/3169578_Improving_power_factor_in_the_presence_of_harmonics_using_low-voltage_tuned_filters

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Power-User

Join Date: Apr 2011
Posts: 104
Good Answers: 5
#5
In reply to #3

Re: UPS and power line noise

02/21/2019 10:16 AM

Thanks to all,

The cables are good and sized correctly. The load lines to the motor are only 15'. Voltage drops are negligible or non-existant. Of course getting the noise at the source would be best but some someone above my pay grade decided to remove them and now we have to sort out the issues

__________________
deanpavil
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: UPS and power line noise

02/21/2019 1:14 PM
  • So why does the UPS alarm on low voltage at higher loads, if <...The cables are good and sized correctly...>?
  • Has anyone oversized the cables yet, particularly the neutral conductor, by way of experiment?
  • Has thermal imaging been carried out on the cables, particularly the neutral conductor, at higher loads?

Way to go.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7
In reply to #5

Re: UPS and power line noise

02/21/2019 3:17 PM

As suggested,view the power with an oscilloscope,or rent a line monitor and it will give a recording of the upsets on the line(voltage).

A clamp-on amp meter will not detect harmonic currents in the neutral,that is why the NEC recommends DOUBLING THE SIZE OF THE NEUTRAL to prevent overloading of the neutral and reducing harmonic frequencies.

There are special meters that will detect harmonic currents,but not your standard clamp on type.

There is the possibility of a loose connection at some point in the system that is exacerbated by high load.

An infrared thermal scan would beneficial to find the problem.

Where is the source of the 120Volts for the UPS?

Is it powered from the same source as the 3 phase for the inverter,through a transformer?

Lots of unknowns here.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#10
In reply to #5

Re: UPS and power line noise

02/22/2019 3:27 AM

Hi Dean,

Are the cables from the VFD to the motor screened and is the screen terminated at one end.

Normally screened cables are required to prevent the RFI from being transmitted but remember the screening should only be terminated at one end else an earth loop could be introduced to act as yet another source harmonics.

As others have said check the supply to the pump skid with a power scope to check for interference.

A suitable filter on the supply for to the UPS would be beneficial in any case or you could use a constant voltage transformer to supply the UPS.

Also placing the UPS and PLC in a single enclosed cabinet should help eliminate RFI and EMI.

Regards Stef

__________________
Hare today, goon tomorrow!
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#18
In reply to #5

Re: UPS and power line noise

02/28/2019 5:56 AM

Are the motor leads in METAL conduit? If so, are the conduit(s)properly bonded at each end to the metal frame,using bonding lock nuts where applicable? Do the motor conduits share the same conduit at some point?Does each motor have a separate conduit?Are the phases to the motors separated at any point? If the motors share a common feeder conduit,are both motors run at the same speed all of the time?

All conductors of a 3 phase supply conductors must run together in the same conduit to prevent induced currents in the conduit and in the other conductors.

Here is a link to factory recommendations to eliminate noise in/from VFD drives.

I suggest that your problem is probably not unique,and the answer may be found in this link.

Good luck.

http://www.heanderson.com/VFD%20Whitepaper.pdf

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#19
In reply to #5

Re: UPS and power line noise

03/01/2019 8:29 AM

If you had a working system that was butcherd by a higher pay grade, the only way is to get an even higher pay grade involved and go back to what worked. Engineerig should run engineering and not higher pay grades.

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Register to Reply
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#4

Re: UPS and Power Line Noise

02/21/2019 7:43 AM

Can you put an oscilloscope on the equipment? A little insight into what is actually happening could be very useful. If the steady state voltages are good then filters might be very helpful. If the E=IR drop drags line voltage below the turn on threshold of the UPS then all the filters in the world won't help.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply Score 1 for Good Answer
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: UPS and Power Line Noise

02/21/2019 6:10 PM

"... Under high loads the noise from the VFD causes the UPS to see a voltage drop and it switches to battery operation."

How do you know it is noise? When you said "voltage drops are negligible" was that tested under >80% load, which is where you say the problem occurs?

Did you read the manual for the UPS? One thing is says is that excessive running on the battery can be caused by "The AC input voltage is out of range, the frequency is out of range, or the waveform is distorted."

With VFDs, the more power you pull from the source, the more harmonic distortion they create (not "noise"). So the scenario you describe is what I would expect. To make matters worse, the higher the input impedance, the more distortion you see. So if your source transformer is too small or is a generator, the distortion (and potentially the Voltage Drop) created by the VFD loading will be worse. The only solution is to add harmonic filtering to the VFDs. Line reactors might help a little, but they might not be enough. You may need to go to tuned trap filters (also called Passive Harmonic Filters).

In addition (and what I would try first because it is free), the UPS allows you to adjust the "sensitivity" and mentions this as one possible way to avoid nuisance battery operations:

"Unit sensitivity Adjust the sensitivity of the Back-UPS to control when it will switch to battery power; the higher the sensitivity, the more often the Back-UPS will switch to battery power. "

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Power-User

Join Date: Apr 2011
Posts: 104
Good Answers: 5
#13
In reply to #8

Re: UPS and Power Line Noise

02/23/2019 3:22 PM

Yes we did test the voltage at 100% load and there was no voltage drop seen with a true RMS meter. I was using the term "noise" generically- classifying harmonic distortion in that category.

3% line reactors were used in the original configuration but someone decided to omit them in recent manufacturing, creating this situation.

And thank you for pointing out the sensitivity adjustment. That is something we missed.

__________________
deanpavil
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#14
In reply to #13

Re: UPS and Power Line Noise

02/23/2019 5:06 PM

One of the advantages of the 3% line reactors on the VFDs is that momentary power/voltage dips that are not long enough to drop out a typical FVNR motor starting contactor (63% one cycle) will also possibly not drop out your drive.

I found this out the hard way, where I left off the reactors because of space in an Allen-Bradley Centerline MCC retrofit. So the next time National Grid bumped the plant, the only two motors that stopped and shut down the process were the 2 new conversions I had just completed. This happened at least 2 more times before I made the space for the reactors. After they were installed, either we rode through the bumps, everyone, or the entire plant went down.

Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#9

Re: UPS and Power Line Noise

02/21/2019 11:12 PM

You might be able to smooth out some of the harmonics by installing a 1:1 transformer in front of the UPS. It appears that front end harmonics from the inverters are fooling the sensing circuits for the UPS.

I'd size the transformer tight to the rated capacity of the UPS system, to take advantage of impedance of right sized transformer.

I think other manufacturers have different firing schemes for this type of equipment, 150HP Rockwell / Vacon drives never bothered similar equipment, but we never had to worry about communications when power went out. Easier to sort things out if everything goes off when power goes off.

You also might try a 3% VFD line reactor of suitable ampere rating in front of your UPS, just clean things up where it matters. Not too big, though. Even applied on the high side of your high voltage to low voltage transformer, it might help by keeping the current low, and cover all of your load side low voltage equipment.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#16
In reply to #9

Re: UPS and Power Line Noise

02/25/2019 3:20 AM

I agree.I have seen 1:1 transformers clean up a lot of harmonics;such as from a inductive cap sealer, VFD,elevator controls etc.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#11

Re: UPS and Power Line Noise

02/22/2019 10:47 AM

What's your power ratio Supply Capacity of the UPS vs. Load? If its close to 1 then probably you got scam by harmonics.

Line filters will do the job.

How close are the pumps and the controls?

Register to Reply
Power-User

Join Date: Apr 2011
Posts: 104
Good Answers: 5
#17
In reply to #11

Re: UPS and Power Line Noise

02/27/2019 11:09 PM

Pumps and controls are about 15' away.

UPS load ratio is about 0.23

We are going to try new settings on the UPS on this weeks startup

__________________
deanpavil
Register to Reply
Commentator
United States - Member - VT

Join Date: Jun 2014
Posts: 59
Good Answers: 4
#12

Re: UPS and Power Line Noise

02/22/2019 5:59 PM

"Stepped approximation to a sinewave"

I think any process running 2 @ 100hp pumps likely involves more value than that little UPS is worth. Last time I looked at APC's products, there wasn't much in that price range that had sine wave output, filtering, and voltage regulation.

Buy a better unit, one that provides your controls clean power. I have purchased CyberPower PFC models for a similar application in the past, because of cost & size considerations. I wondered why Schneider/APC doesn't sell a equivalent product.

__________________
Teach your cat to write
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15

Re: UPS and Power Line Noise

02/24/2019 6:10 PM

Since you have not given the UPS mains input frequency, voltage or VA/current rating; it would be difficult for someone to suggest a filter between UPS line input and UPS!!

The usual line filter does not have much effect At 100 kHz, particularly not for line-line - which is what the UPS looks at.

As suggested in another post, a look at the UPS mains input with an oscilloscope would help a lot to find the nature of the interference.

Do you have a grounded supply to UPS?? Floating adds problems

Register to Reply
Power-User

Join Date: Dec 2018
Posts: 121
Good Answers: 9
#20

Re: UPS and Power Line Noise

03/01/2019 10:51 AM

I had a communication issue that was resolved by the addition of a filter to the electric function. In my case it was an LED FAA Marker light that messed up a 911 relay antennae on a water tower. I found the filter at the following link.

https://www.alliedelec.com/schaffner-fn2010-10-06/70027166/?mkwid=s9chY8ysI&pcrid=30980760979&pkw=&pmt=&gclid=EAIaIQobChMI2PaVxqPw3wIV1LfACh2EYAlCEAQYASABEgKAI_D_BwE

Register to Reply
3
Power-User

Join Date: Apr 2011
Posts: 104
Good Answers: 5
#21

Re: UPS and Power Line Noise

03/05/2019 10:52 PM

Well the solution was the simple and easiest. We selected the low sensitivity range and were able to run the pumps at full speed. Thank you for the insight and ideas

__________________
deanpavil
Register to Reply Good Answer (Score 3)
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); BruceFlorida (1); ccoop609 (1); deanpavil (4); gutmonarch (1); HiTekRedNek (4); jonaparker (1); JRaef (1); Oomborrie (1); PWSlack (2); rogerggbr (1); rwilliams (2); Stef (1)

Previous in Forum: Problem with Bluetooth Read Range for Arduino Project   Next in Forum: Solid State Relay Endurance

Advertisement