I was wondering if there is a simple fix to a UPS problem we have. We have a small pumping skid with a PLC and a radio system for SCADA. The system is powered from an APC model BR1000G UPS. The pumps are two 100 hp VFD driven pumps. THe VFDs are Eaton SVX 9000. These work great until the pumping units has to work under higher loads and at motor speeds above 80%. Under high loads the noise from the VFD causes the UPS to see a voltage drop and it switches to battery operation. The UPS will switch back and forth until the battery is completely drained and the unit shuts down. If we run just one pump at 100% load there is no problem but with both running; the drives must run below 75-80%. This allows the system to keep running but cannot keep up with flow rates needed.
I know there are line filters for the 480v inputs to the line side of the VFD, some of the earlier versions of this setup had those and we have no problems. The newer versions have no filters though. What I was wondering was if there was a low voltage (120/240V) filter we could install that would eliminate this problem or a similar sized UPS we could install that would be less susceptable to the noise level.