Wind Load Calculation Formula for a Communications Cabinet?

10/08/2007 12:40 PM

Greetings,

I need to place a communications cabinet on the roof of our office and need a wind load calculation. Did a brief search but didn't find a quickly useable formula.

In feet the cabinet measures 6H x 5W x 3D. There 4 floor retaining bolts that can be considered to be at the corners. Assuming an 80 MPH broadside wind I need to know how much force will be applied to the windward bolts. Should be simple if I could find a formula for MPH to Pounds.

Thanks,

John

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Minnesota
Posts: 529
Good Answers: 15
#1

Re: Wind load calculation

10/08/2007 2:27 PM

From a pressure vessel handbook.

70 MPH = 13 psf (Pounds per Square Feet)

80 = 17

90 = 21

100 = 26

110 = 31

120 = 37

130 = 44

The above info was dated 1982

I hope this helps.

__________________
downhill slide to 112 (damn memor.)
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 17
#9
In reply to #1

Re: Wind load calculation

10/09/2007 8:16 AM

Thanks,

This jives fairly well with Willyap06's post #6 below which yields 16.4 PSF for 80 MPH.

jh

Register to Reply
Member

Join Date: Apr 2009
Posts: 5
#25
In reply to #1

Re: Wind load calculation

04/15/2009 9:21 AM

Greetings,

I hope you will be able to help me. I am a sales rep for a Solar company. We pre-assemble 3 panels and frame them, wire them, attach a microinverter, ready to go. We have sold a couple of jobs in the Miami Dade area, a 146 mph wind zone. I have submitted our module to a testing company however they would like to know what is the PSF would be for this and what the accepted amount of deflection is? Could you answer this or steer me in the right direction? Thanks,

Mike Kantor mikekantor@readysolar.com

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#2

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/08/2007 4:49 PM

6H x 5W x 3D.

Units? Cubit? span? Metre? Foot?

Inch foot by a thick wide ?

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/08/2007 8:30 PM

First sentence of 2nd pp begins "In feet the cabinet measures..."

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4
In reply to #3

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/08/2007 9:41 PM

Ah got it cheers..

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#12
In reply to #2

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 3:43 PM

FSF system Furlong, Stone, Fortnight. Didn't they teach history of measurement units when you were in school?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#13
In reply to #12

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 3:57 PM

Ah... that's helped me out with my cross word!

I've been looking for this word for a couple of weeks!

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#15
In reply to #13

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 4:01 PM

And I thought us Americans were unwashed and ignorant! ( with a dollop of sarcasm and tongue in check!)

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Feb 2007
Posts: 273
Good Answers: 3
#23
In reply to #15

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/10/2007 1:27 PM

The truth is that Americans wash was quite frequently, more so than most Europeans.

As far as ignorance you would have to list the subjects that Americans are ignorant about in order for me to prove or disprove your statement.

That said, we do not do so bad engineering wise for a bunch of dumb, dirty hicks.

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#17
In reply to #12

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 4:18 PM

I actually gave a problem on a quiz to a prospective employee once which read: "Car "A" is headed for St. Louis from New York at a constant speed of 65 mph, and car "B" is headed to New York from St. Louis at a constant speed of 105 kilometers per hour. What is their mutual rate of approach? Express your answer in furlongs per fortnight? (Hint: furlong = 660 ft; fortnight = 14 days)."

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#18
In reply to #17

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 4:31 PM

And you could have asked to explain why the car from NY performed more work than the car from STL!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Member

Join Date: Oct 2007
Posts: 7
#5

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 1:48 AM

Have u checked in CP 3, Chapter V, Part 2 for wind load calculation?

Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 17
#7
In reply to #5

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 8:07 AM

Thanks for posting.

Pardon my ignorance but I am not familiar with CP 3. I am EE by degree but have been pretty much a software weenie since '80 so maybe one of you 'civil' gentlemen could point me in the right direction.

Thanx,

jh

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#14
In reply to #7

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 3:57 PM

What is your location?

Who is the local "AHJ" (Authority Having Jurisdiction)?

What "Building Code" do they follow?

The structural section of the building code will usually state the required wind loading in terms of pounds per square foot or miles per hour. Depending on the type of building or occupancy, they may even assign an "Improtance Factor" multiplier to applly to the requirement.

Ried the "maniacal inginear"

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Power-User
Engineering Fields - Civil Engineering - Member

Join Date: Apr 2007
Location: Island of Stone Money
Posts: 310
Good Answers: 5
#6

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 3:02 AM

Formula:

q=0.002558V2

where: q = pressure in psf, on plane normal in the direction of the wind.

V= velocity of wind in mph.

Apply corresponding horizontal cross section factor for different shapes.

__________________
"The more I learn, the more I know the less I've learnt"
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 17
#8
In reply to #6

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 8:10 AM

Thanks.

All I need now is the cross section factor for a flat surface. I have seen 1.0 and 2.0 for flat surfaces. Does your formula account for negative pressure on the backside?

Thanx,

jh

Register to Reply
Power-User
Engineering Fields - Civil Engineering - Member

Join Date: Apr 2007
Location: Island of Stone Money
Posts: 310
Good Answers: 5
#19
In reply to #8

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 8:43 PM

The formula is the same for the windward and leeward side of the structure.

To determine the effective pressure, multiply q by the corresponding horizontal factor C.

For a more complex structure like building, there is also consideration of coefficients, say k, for vertical section configuration (e.g., 0.80 windward/0.40 leeward) multiplied by the horizontal cross section factor C. The effective pressure will then be C x k x q.

The negative factor is for suction effect of the wind.

__________________
"The more I learn, the more I know the less I've learnt"
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#11
In reply to #6

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 12:27 PM

I thaught wind resistance for a vehicle...( not exactly the same I know) was proportional to the cube of the speed...

Wouldn't this imply wind load should be proportional to cube of wind speed?

I'm not trying to be argumentative... just genuinely curious.. (hmmm we know what curiosity did..)

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Power-User
Engineering Fields - Civil Engineering - Member

Join Date: Apr 2007
Location: Island of Stone Money
Posts: 310
Good Answers: 5
#20
In reply to #11

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 9:27 PM

I'm curious too!

Somebody in the CR4 community may help shed light on this!

HELP... please help.

__________________
"The more I learn, the more I know the less I've learnt"
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#10

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 8:43 AM
__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#16
In reply to #10

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/09/2007 4:11 PM

Folks, sorry about the link given in my last post. After I actually looked at the site in detail, I noticed that the formula given for the stressed area is incorrect. I also noticed, even if the formula had been correct, there's no information given for elastic modulus of steel (or any other metal, for that matter).

Yield strength for steel ranges between 35 kips and 100 kips (bolts => 50,000 psi), and elastic modulus ranges from about 28 X 106 to 30 X 106 psi (bolts => 100,000 psi).

Since I could have sent you on a wild goose chase, the root diameters and stress areas for various sized bolts are: 1/2" => .422", .140 in2; 5/8" => .531", .222 in2; 3/4" => .656", .338 in2; 7/8" => .766", .461 in2; 1" => .875, .601 in2.

Wind load, in psf, on a flat surface given by willyap06 is 0.00256v2. If the velocity is 80 mph, then the total load is 16.4 psf. The total area facing wind is 30 sq. ft. maximum, yielding a maximum load of about 500 lb. A 500 lb load 3 feet up (half the total distance) amounts to 1,500 lb tensile load on two bolts on windward side and 1,500 lb compression load on two bolts on leeward side.

Stresses on various bolts: 1/2" => 5,360 psi; 5/8" => 3,380 psi; 3/4" => 2,220 psi; 7/8" => 1,630 psi; 1" => 1,250 psi

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#22
In reply to #16

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/10/2007 9:29 AM

Please! Somebody help me get my head outta my a**!

Thanks . . . I needed that.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 270
Good Answers: 19
#21

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/10/2007 4:19 AM

A communications cabinet is not very big really but your location might be a little bit problematic i.e. if it falls off the roof it might kill someone.

Given that your measurements are in feet, I am guessing that you are located in America. The advice to use CP3 (Code of Practice 3) is refering to the old British codes which have since been superseded by BS 6399 (British Standards) which are currently being superseded by Eurocode 1. However, some countries do still use a version of CP3 e.g. Singapore. They use the local wind speeds as measured over the past 50 years or so with a statistical measure of 3 second gust speed which then corresponds to the manner in which the maximum wind speed is calculated based on location of building (valley, side of hill etc), height of building, form of building (is it long rather than tall).

But let's say for the sake of argument that your maximum wind speed on top of your building is 80mph (corresponds to about 35m/s which is a hurricane on the Beaufort scale which is conservative unless you know otherwise). Your building is 10m or less in height and does actually have that wind speed on the top of it.

http://en.wikipedia.org/wiki/Beaufort_scale

The basic wind pressure is 0.613 x 35 x 35 = 750Pa = .75kN/m2

The coefficients for windward and leeward are respectively +0.8 amd -0.5 for rectangular objects = +1.3 overall.

1.3 x .75 = .957kN/m2 say 1.0kN/m2. That's your overall wind pressure.

From that you generally need to apply a load factor for stress related calcualtions. For wind in the british codes this is 1.4.

1.0 x 1.4 = 1.4kN/m2.

Now all you have to do is calculate the force in the bolts. Main difficulty is generally not the bolts, it is the substrate to which you are attaching them.

__________________
omw7
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 17
#24
In reply to #21

Re: Wind Load Calculation Formula for a Communications Cabinet?

10/16/2007 5:32 PM

Thank you all for posting. I think the beast has now been sufficiently slayed.

Best Regards,

John

Register to Reply