Fault Current vs Short Circuit Current

10/10/2007 5:59 AM

what is the difference B/W prospective fault current and short circuit current? or both are one and same.

__________________
manirul
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: short circuit current

10/10/2007 8:36 AM

Fault current - it is the current exceeding the equipment current rating e.g. motor rated 14A & then more than this will be the fault current.

Short Ckt current - it is the maximum current which can flow whem the equipment is short circuited & it can withstand..above this the current will damage the equipment.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#3
In reply to #1

Re: short circuit current

10/11/2007 12:21 AM

do you mean starting current is a fault current because at starting all device having a cold resistance hence starting current is always more than rated current. short ckt is one type of fault. pls clarify.

__________________
manirul
Register to Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#2

Re: short circuit current

10/10/2007 10:39 AM

fault current is the current into a fault be it phase to phase, phase to neutral or phase to ground / earth. In order to calculate it I = V/R you need to know the resistance of the external supply as well as that of your installation. Your supplier should provide information on how much current they would deliver in the event of a fault. You should ensure that the breaking capacity of your protective devices is large enough to handle this. A big fault with a high fault current will clear a fault quickly if your installation is good. To answer your question they are the same, but prospective is the likely amount that would flow in the real world. (not I = 230 / 0)

Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#4

Re: Fault Current vs Short Circuit Current

10/11/2007 2:51 AM

A fault current is a current which takes the wrong path: instead of using the normal cunductors you installed it starts using ground and humans to find its way back to the generator.

A short circuit current is a current which uses the normal conductors but found a shorter way to get back, resulting in much higher currents than those which have been assumed when designing the the system.

Both are a problem: the first can kill you the second can damage your wiring resulting in fire and loss of property.

The problem is indeed the size of these currents: fault currents have typically the size of mA, short circuit currents can be smaller than the startup current of a system.

The solution is to use proper protective devices as the fuse and RCD. Both need to be properly selected to match the installation behind.

If you don't have the knowledge then don't do it, go back to school and get the knowledge behind AC and installation techniques. Electricity is way to dangerous to mess with. If you really need to define a system ask a decent engineering firm to do it for you.

Trial and error is no solution in this domain of engineering.

__________________
"Here we are now, entertain us"
Register to Reply
Anonymous Poster
#6
In reply to #4

Re: Fault Current vs Short Circuit Current

10/11/2007 3:19 PM

spot on nice to see a very precise answer, some of the others are a bit off the mark

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #4

Re: Fault Current vs Short Circuit Current

10/12/2007 11:30 AM

Gwen, you have the best and most accurate answer up to now, all before you did not have a fully thought out and correct answer!

Well put!

I will read the ones below you after posting this!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Aug 2007
Location: Boston area
Posts: 38
#5

Re: Fault Current vs Short Circuit Current

10/11/2007 7:52 AM

Prospective fault current and short circuit current are the same thing.

Register to Reply
Anonymous Poster
#7
In reply to #5

Re: Fault Current vs Short Circuit Current

10/11/2007 3:54 PM

COmment to remember about fault current, it is not the engineer's fault!!!

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #5

Re: Fault Current vs Short Circuit Current

10/12/2007 11:31 AM

...no wonder you have a name like Blitz, but that was an incorrect answer.

Read Gwen's answer, a little higher up....that is fully correct.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#10

Re: Fault Current vs Short Circuit Current

10/12/2007 4:14 PM

"The above link will give you some help to understand the concept."

Understand what exactly? That I should buy this software! It has not explained anything other than that they are a commercial setup trying to sell us something. I do not think this forum is for plugging products UNLESS the generator of the discussion specifically asked for it.

Sorry but that is my 2 cents worth of freely given opinion.

result

Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#11

Re: Fault Current vs Short Circuit Current

10/13/2007 9:59 AM

A fault current can be due to either current being more or less than the normal rated current. Short cct can be a desirable path of low resistance. But they are not the same.

__________________
poy
Register to Reply