Transformer neutral

10/10/2007 8:47 AM

Dear friends ,

Can you explain me what are the causes ,when a transformer neutral directly grounded is not proper ie disconnected or loose connection or not properly welded with earthing grid.

please guide me regarding this.

karthik

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Transformer neutral

10/10/2007 10:08 AM

It depends what part of the circuit it plays.

If it is the return path for either + or - signals, It may make some of the circuits not function.

If it is simply a safety ground, all the circuits will continue to work, however, the equipment may build up a large unsafe potential that could electrocute and or kill anyone that touches it. The build up depends on time and modes of operation.

__________________
Perfection is a subjective and abstract concept.
Register to Reply Score 1 for Off Topic
3
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#2

Re: Transformer neutral

10/10/2007 7:55 PM

I suppose that the neutral of the transformer is connected to the neutral of bus-bar feeding loads.

In general, the neutral of a three phase transformer is connected to the earth to force the neutral point at very low potential (ground voltage ≈ 0) even in case of unbalanced loads.

If the ground connection is lost, the neutral point of the transformer will be floating, i.e. its voltage is zero only if the loads in the three phases are balanced. If the loads are unbalanced then the voltage of the neutral point will rise, consequently, the phase voltages of the transformer will deviate from their original values.

Also, in case of single line to ground fault, the faulty phase will be zero voltage, and the other two phases will rise to line values causing damage to single phase loads connected to these two phases (voltage of these two phases rise to 173% of the original value).

So, this connection between transformer nuetral point and earth is very important in most cases.

Regards... Samak

Register to Reply Good Answer (Score 3)
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#3

Re: Transformer neutral

10/10/2007 11:38 PM

There is another problem that could happen,

If the Neutral line is not available on the power outlet, use an outlet that has that connection, if you run from another outlet a separate Neutral line, this could play havoc with your saftey circuits (EL/RCD breakers) as the currents will be unbalanced.

I once had to drive for 2 hours to get to a job site that complained that the new product our company sold them was tripping their breakers, and they had 2 cables running from different sides of the factory, 1 was the phases, the 2nd was the neutral.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
Power-User

Join Date: Jul 2007
Location: Somewhere in the hills of Pennsylvania, I think.
Posts: 246
Good Answers: 4
#4

Re: Transformer neutral

10/11/2007 12:55 AM

I'm not trying to "short circuit" your question, however, in this case, a little knowledge could be a very dangerous thing. Consult an experienced electrician who can make an on-site evaluation of your particular situation. If you are asking because you are working on a hypothetical situation, more circuit details are necessary for a good answer (i.e. transformer details, supply voltage(s), loads and their connection to the transformer, etc.

__________________
I'm somewhere between the age of thirty-something and Alzheimer's. I just can't remember where!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: Transformer neutral

10/12/2007 11:36 AM

Techno was fully correct, you could kill somebody. That somebody might be you, so be careful, do not do anything to cause that situation!!

Have a great day!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#6
In reply to #5

Re: Transformer neutral

10/12/2007 8:18 PM

I'm afraid you confuse with protective earthing and system earthing.

The point we are talking about lies under system earthing as it concerns the connection between neutral of the supply and the earth.

Protective earthing which belongs to safety, concerns the connection between the metallic enclosure (non-current-carrying metallic parts) and the earth. Such a connection is essential for human protection against faulty connection between a live conductor and the transformer body.

Do you agree?

Samak

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #6

Re: Transformer neutral

10/13/2007 7:20 AM

I am not confused, you cannot read or are yourself confused maybe, it could be that time of the month....or you want to play the semantics game!!!!

This blog was all about Neutral earthing, therefore to play safe, one must assume (as has EVERYONE else, except your good self!) and to answer as I did with Techno I believe, with regards to earthing and Neutral, which is/are/should be correctly connected together at the nearest substation.

The reason being that is this is not done and phases are not equally loaded on the transformer, the earth and the neutral would or could end up with a large potential difference that could become dangerous to users. It does not do some sensitive equipment much good either.....ELCBs would also I believe be difficult to set up correctly and would (I believe) be constantly being actuated....I have not had an experience where the neutral & earth were not bonded correctly, so I can only say what I myself have been told by people who at least profess to know better.........

I worked for over 30 years as a specialist in the computer business, I know full well the difference between the two.....I have even helped a few electricians to get it right and I have even helped in repairing equipment when they have got it wrong!!! Over the years, several times in several different European countries.....

Why confuse the issue, up to the point in time of your post, it was quite clear for all concerned.....

....and in spite of what you appear to think with your semantics, the neutral/earth bonding at the local substation IS AN IMPORTANT PART OF EARTH SAFETY.......without it, there would be even more deaths through electricity than they are now!!!

I am all for correct semantics when it helps, in this particular case it does not.....

Read through what Techno wrote again (all I said was that I agreed with Techno!), what is your problem with that? Basically it is simple and correct and covers two different conditions, the first having nothing to do with neutral though, but should I jump down his throat like you do because of that????:-

It depends what part of the circuit it plays.

If it is the return path for either + or - signals, It may make some of the circuits not function.

If it is simply a safety ground, all the circuits will continue to work, however, the equipment may build up a large unsafe potential that could electrocute and or kill anyone that touches it. The build up depends on time and modes of operation.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#8
In reply to #7

Re: Transformer neutral

10/13/2007 10:10 AM

OOPS...ANDY that was abit rough.........

__________________
poy
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #8

Re: Transformer neutral

10/13/2007 10:48 AM

If misunderstood by another reader, not that we would probably ever find out, but someone might get killed.....

Its too dangerous to play with semantics in such areas.....he jumped on me without a "bye your leave" etc., I answered back! Normal business!! Safety first on all fronts!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#10
In reply to #9

Re: Transformer neutral

10/13/2007 11:00 AM

Yo right andy safety first n apparatus later

__________________
poy
Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#12
In reply to #9

Re: Transformer neutral

10/16/2007 12:33 AM

What *is* "bye your leave" anyway? never understood that line

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #12

Re: Transformer neutral

10/16/2007 2:38 AM

Its a largely old fashioned manners way of asking permission to do something. I found an example on the web that maybe explains it better (hopefully!):-

"To the contrary it's head down and forward to wherever your destination may be
without such as a bye your leave to the fellow next to you."

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#11
In reply to #7

Re: Transformer neutral

10/13/2007 6:10 PM

Be relax Forum's friend, and take it easier.

I didn't intend to disturb or upset you. I thought it's a technical discussion just for exchange of knowledge and experiences. However, I'm so sorry for that.

Now,if my apology is accepted, let me clarify what I mean.

In design phase and/or practice, neutral of the system and earth are usually (not always) connected and are world-widely known as system earthing or system grounding. If this connection is lost (even intentionally disconnected), how/when/why...etc. - in your words - "could electrocute and or kill anyone that touches it.", also,what do you mean by the final word in your sentence "it"?

Your answer may S.O.S (Save Our Souls).

What I said is clear:

  1. The above disconnection, will never hurt/injure anybody touches "it", such "it" is any touchable surface of the equipments,(may be a transformer body, a case of computer, etc.).
  2. A human can be electrocuted or injured if a ground fault (phase-to-earth fault) occurs while touching a touchable metallic case/enclosure of the faulty equipment of which its case/enclosure is NOT connected to the earth.
  3. A human will be safe in the above case (#2) if the metallic case/enclosure is correctly connected to the earth. Such a connection is, also world-widely, known as protective earthing (PE).

That's what I believe. And that's what I'll appreciatively leave as soon as I'll be corrected.

Finally,if my apology is not accepted, just correct the above.

Samak

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (4); FKIA (1); olivinak (2); Samak (3); Snaketails (2); techno (1)

Previous in Forum: UPS Selection for 90kW Motor   Next in Forum: Searl Effect Generator

Advertisement