110 to 240 transformer.

10/12/2007 1:25 PM

hello, just a quick jolt.....subject..240 volt to 110v stepdown transformer....

is it useable as a step up transformer if i input 110v at the output, will i get 240 volts at the input ? are there any electronics incorporated in them to prevent this??? anyone tried it?

regards.....aaaaahhhh tttuuuurrrrnnnn iittt oooofffffff. hee hee

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - HAM Radio - New Member Hobbies - Model Rocketry - New Member

Join Date: Jan 2007
Posts: 787
Good Answers: 52
#1

Re: 110 to 240 transformer.

10/12/2007 1:32 PM

I've done it in a pinch, and it worked for me, although I would be careful. I know in my application I didn't need much amperage.

Just to clarify I am talking about an actual transformer which looks something like this, and not something called a transformer that plugs into the wall but could contain other circuitry.

Reply
Anonymous Poster
#2
In reply to #1

Re: 110 to 240 transformer.

10/12/2007 1:40 PM

thanks Frank...but im talking about those yellow site ones commonly found in the uk...

regards

les

Reply
Anonymous Poster
#15
In reply to #2

Re: 110 to 240 transformer.

10/15/2007 5:19 AM

Why do you want do do this? 240VAC is more readily avaliable just about everywhere!

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3

Re: 110 to 240 transformer.

10/12/2007 3:11 PM

Yes. Transformers are the same one way as the other. The only thing to watch out for is the power (VA) rating of the transformer.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Anonymous Poster
#4
In reply to #3

Re: 110 to 240 transformer.

10/12/2007 4:29 PM

"Yes. Transformers are the same one way as the other. The only thing to watch out for is the power (VA) rating of the transformer."

thanks for the reply Bill,

can i assume then in a 3kw transformer (240 down to 110) it is the output quoted and stepping up i can input 3kw at 110 volts..(3000/110 =27.27 amps) and i will get 3kw (minus conversion losses) at 230volts and 12/13 amps...? sounds somewhere near right to me( but im the one asking the experts)...would be on a 13amp fuse ............to fill in the blanks ......., i was recently offered an american sine wave power inverter, and was thinking of how i could safely convert its output to UK voltage without too much expense and thought about putting its output through a much larger than reqd transformer to get it to 230/240 volts , if i use a larger capacity transformer then it wont be overloaded but the inverter output can still spike to its momentary rating, usually double the continuous rating....

asked the sparky at work but he gave me a funny look and said he'd never tried it.....

?????????

regards and thanks so far .....

aaaarrrggghhh tttuurrnnnn iiiittt ooooffffff hee hee

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#16
In reply to #4

Re: 110 to 240 transformer.

10/15/2007 8:01 AM

Your assumptions are correct. It's best to not operate the transformer at maximum, as this is typically determined by the temperature rise of the windings, which is a function of the wire size, magnetic efficiency of the core, etc. The limiting factor in transformers is the temperature at which insulation breaks down and causes faults between windings. A 3kVA transformer should not be wound secondary on top of primary, such as is the case in some small transformers, but would ordinarily be wound such that the primary and secondary winding are wound starting in close proximity to the core, resulting in similar efficiencies whether used as step-up or step-down transformer.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Active Contributor

Join Date: Oct 2007
Location: Oregon
Posts: 10
#5

Re: 110 to 240 transformer.

10/12/2007 4:38 PM

The ratio of this xfmr 2:1, and will work in reverse as well, as 1:2, but important facts are that whether it is a single phase or three phase xfmr, the line and load sides of the xfmr must be the same phasing.

__________________
Master
Reply
Anonymous Poster
#6
In reply to #5

Re: 110 to 240 transformer.

10/12/2007 4:45 PM

yep , single phase .....

cheers for that ...

aaaarrrggg ttuuurrrrnnnnn iiiitttt oooooffffffffff hee hee

Reply
Anonymous Poster
#7
In reply to #6

Re: 110 to 240 transformer.

10/12/2007 5:48 PM

thanks for the advice fellas, im gonna give it a go,

regards

les

aaaarrrgggg ttuuuurnnnn iitt offffff hee hee

Reply
Power-User

Join Date: Jul 2007
Location: Melbourne Florida
Posts: 122
Good Answers: 2
#9
In reply to #7

Re: 110 to 240 transformer.

10/13/2007 3:28 AM

holy smoke you have gotten quite a response here, ok here is the low down on on the hooplah .

The 2:1 ratio is correct is correct as far as kva but you must keep in mind that the kva be in the lower portion of the equation. for example if a load at 110 VAC is supplied with with 220vac the load is that of of 1/2 of 230 VAC so if load is for example 5 amps at 110 VAC it is equal to 10.0 VAc at 230 VAC. so for a transformer in a boost application it would be load KVA times two times to give the most power requied for the load. however eighty percent is usually adequate.

Dave

__________________
repeat problems can not be solved by the same way of thinking ( A. Einstein)
Reply
Active Contributor

Join Date: Oct 2007
Location: Oregon
Posts: 10
#8
In reply to #6

Re: 110 to 240 transformer.

10/12/2007 5:57 PM

Remember power in = power out.

__________________
Master
Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#10

Re: 110 to 240 transformer.

10/13/2007 3:43 AM

dont forget to take away the fault current that goes through your finger, arm, body and leg back to earth.....

oh sorry wrong thread.

Reply Off Topic (Score 5)
Guru

Join Date: Aug 2007
Posts: 548
#11

Re: 110 to 240 transformer.

10/13/2007 2:45 PM

"aaaaahhhh tttuuuurrrrnnnn iittt oooofffffff. hee hee"

Is that sound you are getting when you are working with transformer , i aan`t know that

Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#12

Re: 110 to 240 transformer.

10/14/2007 3:01 PM

Yes. Use of transformers is almost symmetric, but due to the losses it's not totally true. The 240 V output will be a bit lower.

__________________
Aged man is not old man...
Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#13

Re: 110 to 240 transformer.

10/14/2007 10:41 PM

Whoa horsey! Before we all go up in smoke....

I'm going back 20 years but I remember theoretically they are bi-directional, but practical transformers are optimised to work at maximum efficiency from primary to secondary; the primary coils are optimised to produce magnetic flux, and the seconary to intercept it (except toroidals which are rare due to the expense of winding them).

Thus when you reverse this process it will work, but at lower efficiency.

All OK until you used the magic words "3 kW" and "yellow boxes". Lets say the extra losses are 10% (I'm going to guess this is at least half the real losses). Now our little "box" has to get rid of up to an extra 300watts, on top of what it was originally designed for. Try touching a 300watt halogen lamp. That heat may do some sort of damage to the internal wiring.

By the by, the transformer output will be a socket (female) and the the input a plug (male). To use in reverse infers you will need a live plug from your 110 mains for the socket, and the units male terminals will be live @ 230. Earth continuity may also be an issue, as will volt drop. It might be very noisy too. What fun.

I'd use a 6kW unit to help get rid of the heat (which is a heavy beast) and preferably in someone elses property!

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#14
In reply to #13

Re: 110 to 240 transformer.

10/15/2007 1:46 AM

you remember the " aaaaahhhh tttuuuurrrrnnnn iittt oooofffffff " !

It could all be too late already hehe

Reply Off Topic (Score 5)