Substation Control Building Grounding

06/15/2019 4:14 AM

Dear sirs,

Should the earthing mat be laid out first before control building of electrical substation is made?

Best regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Substation Control Building Grounding

06/15/2019 11:28 AM

What's an 'earthing mat' ?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Substation Control Building Grounding

06/15/2019 11:53 AM

In my opinion, the substation grounding grid and the substation control building grounding system are 2 different installation which eventually should be connected together.

The grounding grid follows IEEE 80[2013] for instance and the control building NEC [NFPA 70/2017].

If you know -from the substation early design -what will be the limits of the control building and other facilities you may design finally the grounding grid. If don't know, you have to redesign partial -or to fix the cut parts. However, you have to provide grounding grid connecting points on the building-on foundation or floor according to standards.

As a practical recommendations I think this NECA standard could help:

National Electrical Contractors Association NECA 331/2009

Standard for Building and Service Entrance Grounding and Building

__________________
Julius
Reply Good Answer (Score 2)
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3

Re: Substation Control Building Grounding

06/15/2019 11:58 AM

Follow your local codes. We have no idea what location this substation will be placed so we cannot recommend any standard to follow.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4
In reply to #3

Re: Substation Control Building Grounding

06/15/2019 1:31 PM

I agree with you, redfred. It seems to me-according to o.p.term "earthing "- it has to be according to BS. However, it seems to me, for now, these standards are not so far from U.S. national standards in order to build an "earthing mat" according to BS EN 50522 or a"grounding grid" according to IEEE 80 and building[Uffer] grounding according to BS 7430 or NECA 331.

__________________
Julius
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#5
In reply to #4

Re: Substation Control Building Grounding

06/15/2019 2:30 PM

There is also the possibility that the AP is misusing one of the buzzwords in an attempt to look knowledgeable enough to ask such a question.

On that note, most modern substations do not have a control building because the substation is remotely controlled from a central site.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#6
In reply to #5

Re: Substation Control Building Grounding

06/16/2019 3:21 AM

Truly you must live in a blessed country for every substation I have ever built, repaired or maintained had a control building which housed the metering, protection relays, remote control and other necessary equipment.

The opening and closing remote controls were interfaced with the local controls. The substation acted autonomously to protect its own equipment which is needed when the lines of communication are down.

As for the earth mat, now that is a term I am familiar with, for that is what we call them here. As for the requirements for the mat, then the end user may have their own specifications to suit their needs and there are appropriate standards which must be followed as a base line and may be exceeded with approval.

A construction substation for a power station required that the earth mat be 50mm x 6mm flat steel bar on 1m grid and welded at each crossover. It was specified that no copper be buried in the ground and all connection points to towers be able to be accessed through risers. The earth mat had to extend beyond the fence for a distance as specified to prevent step potential and be bonded to fence. All the earth mat trenches were to be filled with a suitable conductive clay.

There are standards that relate to the combined earth mat resistance.

For the building if it were on concrete slab then the earth mat will likely be connected to the floor and trench reinforcing and have a separate earth connection point to an earth bar inside the building and be clearly labeled as must all other earth connection points.

For earthing in mines then other provisions apply.

You need to ascertain what the end users earthing requirements are and ensure they comply with the relevant standards for your area.

__________________
Hare today, goon tomorrow!
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#7

Re: Substation Control Building Grounding

06/16/2019 3:47 AM

Eggs are laid, people are laid, earthing mats/grids are installed. Please, go to a site that is being built and look. Then ask questions on that which puzzles you. That means leaving the seat you are on and venturing out into the world where stuff happens. It will be most educational and mind blowing.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: Substation Control Building Grounding

06/16/2019 3:19 PM

If it is part of the concrete foundation it would make sense to do this first.

What do your local standards say?

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Substation Control Building Grounding

06/17/2019 2:59 AM

Is there a Mentor at the facility that can answer these questions and review the design documentation or is this entirely a home-brew project being carried out by amateurs?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 9 comments