Generator Test

06/26/2019 2:45 PM

dear all

how we can do insulation resistance test for generator rotor safely.where we put

the terminal of megger, and are the shaft grounding brushes should be open.

please can any body explain.

thanks

Register to Reply
Pathfinder Tags: generator test
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Generator Test

06/26/2019 9:17 PM

The best answer is going to be the answer you get from the generator manufacturer.

If the manufacturer is no longer in business, the usual procedure in insulation resistance tests is to attach one terminal of the megger to the rotor winding(s) connections and the other terminal of the megger to the shaft and/or frame/laminations.

Are you using an AC megger or DC megger? Your results will vary accordingly.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Oct 2012
Posts: 85
Good Answers: 1
#2
In reply to #1

Re: Generator Test

07/05/2019 12:29 PM

This brings to mind a question I had about meggering a few years back. I had been told (on a previous job) that the most important thing about meggering was to compare current results with previous ones but then was put on a job where we were to check several motors monthly but different people did it and were given no access to previous readings. Do you think this was a reasonable test? Also I had been told to megger with positive to ground but others used negative ground. I found that I got different values + than -.

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#3
In reply to #2

Re: Generator Test

07/09/2019 1:07 PM

One reason you may get different values for (+) to ground and (-) to ground may be due to some contaminants behaving like a semiconductor relative to the windings. Variances I have seen using insulation resistance (IR) testers have been upwards of 10% difference in readings.

For that matter, just taking the same measurement on a piece of equipment several times in the exact same manner can result in fairly significant differences, especially if the equipment has been in service for a good long time. Just the nature of the beast.

A long history showing trends is much more useful than a single snapshot.

Register to Reply