Secondary Injection Tester Going into Overload

07/14/2019 7:30 PM

Hello

I am currently trying to test a protection relay per the attached schematic. Basically, the relay has two sets of CT's connected together in parallel with the relay, which are mounted on different feeder cables. The idea is that when feeder A is reading xx Amps and feeder B is reading yy Amps, the relay will see xx - yy Amps.

The feeder B CT's are connected via 2.5mm2 4C+E cable. The feeder A CT links have been opened and this is where I have connected my test set.

When I inject per the schematic shown, my test set goes into overload. The DC resistance between A/A- B/B- and C/C- is ~13 ohms and I am only injecting 100mA. This should not overload the test set? When I short out A-/B-/C-/N- the test set works fine.

Why are these CT's overloading the test set?

Schematic link: [link https://files.engineering.com/getfile.aspx?folder=8331921f-0270-4684-af3d-98bb3e470438&file=schematic.JPG]Link[/link]

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Secondary injection tester going into overload

07/14/2019 7:53 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Secondary Injection Tester Going into Overload

07/15/2019 6:05 AM

One possibility is that there is a source of power on the circuit being tested that is confusing the instrument, however it cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Secondary Injection Tester Going into Overload

07/15/2019 8:35 AM
  1. It may be an elementary point - you have opened feeder A links - but have you short-circuited feeder A CT ?? If not, there would be arcing which could apply spikes to your test set & cause overload symptoms.
  2. How do you know your test set is overloaded?
  3. Have you measured currents to /from test set/ relay/remaining CT with a meter?

Unfortunately, I cannot download the diagram, although other diagram from site do work OK.

If as you write, the CT's secondaries are wired in parallel, then the relay has only one current input per phase. The current A minus current B function is inherent in the CT connection according to the polarity of connections[reversing the leads of one CT would give sum of currents, not difference] .

To test the relay, you isolate its current input from the CTs and inject to the relay CT input: with < and > required operating current difference between CT secondary currents.

But the actual result of two currents....

I = A sinwt - Bsinw[t + T]

depends on the phase/time difference - assuming same frequency [you can draw a vector diagram to get the result I]. If you inject with a test set, it may come from an LV supply of different phase to the cables your CTs enclose or even have its own generator of different frequency to CT currents.

Note that, theoretically, the relay and its connecting cables to the point where CTs are paralleled has negligible impedance/resistance compared to the CTs & their cables or at least makes the CT loads less than rated burdens.

Register to Reply