Alternative to Step-Down Transformer for Induction Motor

07/31/2019 6:33 AM

I have US made tiler with induction motor 110V-120V 0.6kw .
Can I use any alternative to heavy step down transformer to run of 240V grid in Australia?
Like capacitor in series or thyristor dimmer ?
Possibly can not use diode for induction motors.

Register to Reply
Pathfinder Tags: step down transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#1

Re: Alternative to Step-Down Transformer for Induction Motor

07/31/2019 8:09 AM

If its a standard frame motor it might be easier and cheaper to replace the motor.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2
In reply to #1

Re: Alternative to Step-Down Transformer for Induction Motor

07/31/2019 9:25 AM

...or if not, you can have the motor rewound...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Alternative to Step-Down Transformer for Induction Motor

07/31/2019 9:38 AM

A VFD probably exists that will do the complete voltage and frequency conversion for this motor.

Why did you move this motor halfway around the world to make this problem?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: Jul 2019
Posts: 2
#8
In reply to #3

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 3:31 AM

I found electric garden tiler only available in US so far. That was 6 years ago. Even today there is none in whole Australia, and I am not sure if anywhere else do such thing at 220-240V.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Alternative to Step-Down Transformer for Induction Motor

07/31/2019 9:44 AM
__________________
Julius
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Alternative to Step-Down Transformer for Induction Motor

07/31/2019 10:12 AM

In a word, no. 120V means it is a single phase motor, probably with a Capacitor Start type based on the application. That type of motor is incompatible with any electronic solution, you would just set up a race to see which component fails the fastest.

Just replace the motor with something local.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Oct 2012
Posts: 85
Good Answers: 1
#19
In reply to #5

Re: Alternative to Step-Down Transformer for Induction Motor

08/07/2019 7:42 AM

You are probably correct that it is a single phase motor but I have seen 3 phase, 120 volt motors. We had one on a hydrogen meter for a hydrogen cooled generator. Also most modern automatic washing machines use a 3 phase 120 volt motor to avoid using gear boxes. With a VFD the same motor runs at low speed (direct drive) for agitation (reversing) and at high speed for spinning.

Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#6

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 12:14 AM

For around $110 AUD you can buy a 750W 240V 1440RPM single phase motor so why mess around with capacitors etc.

If you were to try a thyristor then it has to be symetrical in its triggering else any asymetric part of the waveform will appear as a DC to the motor and either cook it or saturate the windings and with the small motor DC resistance it doesn't take many volts to give quite a bit of current.

Check inside the motor terminal box it may just be able to be reconnected as 110/220V but then it will run slower for USA have 60Hz not 50Hz as here in Aus.

__________________
Hare today, goon tomorrow!
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#7

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 2:49 AM

As has been noted elsewhere, a replacement motor would be the better choice, but purely as a thought exercise - and I'm only guessing as I have never tried it, but would a heavy duty resistance (thinking the element of a 120V heater) connected in series achieve the desired result? Possibly 2 x 240v elements in parallel and then in series with the motor if you can't find a 120v one

Certainly would not be power efficient, but that wasn't one of the parameters in your question.

I did use a slightly similar thing (the old wire wound ceramic elements) many years ago when I made some DC injection systems for 3 phase dough brakes in a bakery to prevent the staff being dragged into the rollers.

Register to Reply
Commentator

Join Date: Oct 2012
Posts: 85
Good Answers: 1
#14
In reply to #7

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 12:43 PM

Not a good idea. Assuming it is an induction motor since at start up it draws about 7 times running current it would have very low voltage available at start (probably would not start) relatively but high voltage when it reached speed. Say running current is 8 amp at 120 volt so you use a 1,000 watt 120 volt heater in series. At start it would have about 30 volts and heater would have about 200 volt. Motor probably would not start and heater would probably burn out. Sat 5,000 watt (or 5 each 1,000 watt in parallel). At start motor would have about adequate voltage but when it reached speed it would have about 190 volts and probably fail soon. The voltage divider idea works with constant resistances but motor has much more" resistance" (or reactance or effective resistance)at speed than at start.

Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#9

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 5:46 AM

A Variac if available may help you achieve your wishes.. It is a variable autotransformer used in the olden days as dimmers, motor controller..

__________________
vsar
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 11:25 AM
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 11:43 AM

I see a section of electric tillers on eBay Australia. This one is $250 AU and designed for your power grid.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #11

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 11:58 AM

SPECIFICATIONS

Rated power :1250WVoltage/Hz :240V~50Hz
Working width :320mm/13"Working depth :220mm/8.7"
Weight :11kgDimension :385x373x585mm
Tine length :350mmWheel dia :150mm
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #12

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 12:08 PM

Where have I seen this before?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#15
In reply to #13

Re: Alternative to Step-Down Transformer for Induction Motor

08/01/2019 8:21 PM

Hey! Look over there!!! Is that a lost cat???

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#16

Re: Alternative to Step-Down Transformer for Induction Motor

08/02/2019 6:04 AM

Does your 240 volt supply carry a neutral,which is a center tap on the supply transformer from the utility?

Do you have any 120 volt appliances in your home?

If so,use one hot leg of the supply and the neutral to obtain the 120 volts.

Test your voltage from hot to neutral to determine what you have.

Be certain to install the appropriate short circuit (fuse or circuit breaker) as appropriate for the conductor,and protection device for the motor as well.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17

Re: Alternative to Step-Down Transformer for Induction Motor

08/04/2019 9:16 PM

Search Google for a 1 KVA transformer.That will be sufficient for your purpose.

I have seen some,but they will not ship to Oceana,but there are sure to be some in your area.The ones I have seen are about $50.00 US.,good used ones even cheaper.

They should weigh around 23 pounds.

Get one that is NEMA 3R (outdoor) rated and mount it outside with a receptacle added for your tiller.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18

Re: Alternative to Step-Down Transformer for Induction Motor

08/07/2019 6:29 AM

Just replace the motor. "Simples ξ".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply