Power Factor Improvement

10/17/2007 9:56 AM

For power factor improvement on 11KV feeders the capacitors are normally used. Where should the capacitors be located, at the emanating point, at the terminal point or somewhere between the feeder? What criteria should be adopted for choosing their location?

__________________
inhussain
Register to Reply
Pathfinder Tags: Power Factor Improvement
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Power Factor Improvement

10/17/2007 10:01 AM

They need to be close to the load, so as to reduce the current in the feeder cable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2007
Location: Lahore Pakistan
Posts: 60
#2
In reply to #1

Re: Power Factor Improvement

10/17/2007 10:43 AM

In case of a rural feeder having a diversfied load, scatered across the feeder of approximately 100 KM in length,it would be difficult to locate the load centre. Can we rationalize it by any mathematical formoula?

__________________
inhussain
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Power Factor Improvement

10/17/2007 11:03 AM

Network calculations are, by their very nature, iterative and exceptionaly tedious. It might be better to place the effort where results can be won early.

It is easiest to look at each individual load point and assess the economics of installing power factor correction [PFC] at that point. PFC can significantly reduce the current in branches of a feeder, thereby reducing hot-spots both in it and locations further upstream. It also reduces the risk of needing to replace sections of the feeder with larger-cross-section cables.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4

Re: Power Factor Improvement

10/17/2007 11:04 AM

Locating capacitors on a distribution circuit is as much an art as a science. If your system design is similar to what I saw recently in Thailand, the feeder has a relatively small number of large (500KVA or greater) distribution transformers. I would install capacitors adjacent to the larger distribution units. In my US system, I can estimate the capacitor KVAR at about 25-30% of the transformer KVA, but your load characteristics may be different.

If you want to be more precise, you can do some short-term monitoring of the feeder. Install a meter on the line in several different places to record voltage, current and power factor for about a week. Use the data gathered to find the optimum capacitor placement in order to minimize the distance reactive power will flow.

Once the capacitors are installed, check the power factor on the feeder at the substation. Because the load profile isn't flat (the load varies with time of day), you can't get a constant unity at the feeder. Just find a good average where the feeder is sometimes lagging a bit, sometimes leading a bit, but stays centered around 1.0.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Power Factor Improvement

10/17/2007 1:48 PM

Normally the 11kv supply receivers install it on their 11kv bus.In your case it should be close to the point where u are steeping it downie near the transformer where it is converted to LT voltage could be 440,380 depending upon ur country's practice.