Dear sirs,

How is the differential protection managed for a gas-insulated substation?

Best Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Differential Protection for GIS

08/07/2019 3:49 PM

The same way it is for any other substation. You define your differential zones of protection, and ask the manufacturer to provide instrument transformers in the GIS to feed into the differential relays' inputs. They you define which circuit breakers to trip for the different zones, and program and wire the relays appropriately.