Power Generation - Wye and Delta

10/17/2007 10:23 PM

In most 12 wire generator connections I have seen, there are series star, parallel star, series delta and then parallel delta. Why is there the need for the Delta type connections when the Wye connections can provide the two different required voltages - 208/480 ?

__________________
When it comes to engineering, what we call ourselves is not supposed to matter. The only thing that matters is the knowledge we attain and the respect we give each other.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#1

Re: Power Generation - Wye and Delta

10/17/2007 11:33 PM

AFAIK..

on 3-PH, you'll have a certain voltage across each individual winding, say 208V (AC)

in Delta Configuration, you'll have 208V on each phase

in Wye Configuration, you'll have the 208 from phase -> Neutral, but 480 from phase to phase..

I guess you know that part, but I think its the current's available on the phases that makes most of the differance.

Going the other way, we had some 3-PH motors here at work, they were wired up as Wye, but were powered from 1-PH -> 3-PH power converters, the output from the motors wasn't enough and kept stalling, it was later found that the motors needed to be configured for the other connection.

So, 240VAC in, and then converted to 3-PH (don't think I need the calcs for the resulting lower voltage)

Instead of having the voltage applied across each winding, it was divided across each winding as such

Ph1 - Ph2 = W1+W2

Ph2 - Ph3 = W2+W3

Ph3 - Ph1 = W3+W1

In Delta it would have been ..

Ph1 - Ph2 = W1

Ph2 - Ph3 = W2

Ph3 - Ph1 = W3

May have drifted OT, but I feel its still relevant ;o)

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2
In reply to #1

Re: Power Generation - Wye and Delta

10/18/2007 9:51 AM

Your numbers are off, but the basic premise is correct. The relationship of phase-neuitral voltage to phase-phase voltage on a wye connection is √3, or about 1.732. If phase-neutral is 208V, phase-phase will be 360V. For 480V phase-phase out, the phase-neutral will be 277V.

I suppose it's possible to make a 12-wire genset produce 208 and 480 in Wye, but you'd have to do some serious adjustment on the voltage regulator. Producing 208V requires 120V from each of the 12 winding coils (connected parallel star). For 480V, you'd need 138.5V out of the same coils (connected series star), a 15% increase. Most regulators are only good for +/- 10%, and the winding insulation may not be good for the higher voltage.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#3

Re: Power Generation - Wye and Delta

10/19/2007 9:06 PM

For 12 wire generator, we have 6 coils.

If the series star produce 480 volt and 1000A (say), then each coil produce half of (480/√3),

(480/√3)≈280

Then Vcoil=0.5x280=140v.

Now;

Series star: V=480volt , I=1000amp

Parallel star: V=240volt , I=2000amp

Series delta: V=480/√3=280volt , I=1000x√3=1732amp

Parallel delta: V=240/√3≈140volt , I=2000x√3=3464amp

these are the available combinations, and you can see the differences.

Note that the power is constant in all of the above.

Samak

Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

pwr2thepeople (1); Samak (1); Snaketails (1)

Previous in Forum: Power Generation - Neutral And Ground   Next in Forum: Spot welding machine

Advertisement