Power Generation - Neutral And Ground

10/17/2007 10:14 PM

Alot of people (including myself) have a problem understanding the need for two separate lines for Neutral and Ground when they both share the same connection on the output terminal in the Generator.

__________________
When it comes to engineering, what we call ourselves is not supposed to matter. The only thing that matters is the knowledge we attain and the respect we give each other.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#1

Re: Power Generation - Neutral And Ground

10/17/2007 11:23 PM

If there is/was an application to "DC-Bias" the Neutral of the Generator, you could detach the Neutral and terminate this at another point.

Then you'll have a Generator with the Frame Earthed, and the AC output with a DC Bias from zero.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#2

Re: Power Generation - Neutral And Ground

10/18/2007 12:38 AM

not only it conected at generator output terminal but at distribution board also you will find neutral and ground are connected, this often confuse me....but whay so, no idea.

__________________
manirul
Register to Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Power Generation - Neutral And Ground

10/18/2007 4:06 AM

The ground or earth conductor is there to provide personnel protection in the event of a fault.

The neutral conductor is there to provide a regular return path to the generating point for the current supplied down the live conductor in the case of a single-phase system.

The neutral conductor provides a balancing current flow for a multi-phase system where there are different currents across the phases.

http://en.wikipedia.org/wiki/Earthing_system

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#4
In reply to #3

Re: Power Generation - Neutral And Ground

10/18/2007 10:37 PM

Perfect. Just perfect !

__________________
If it eats, it's going to be trouble!
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5
In reply to #4

Re: Power Generation - Neutral And Ground

10/18/2007 11:37 PM

The ground is there to ensure that if an operator touches the hot wire and ground, he will become aware of this.

Seriously, I see zero need for a ground. I see a need for a return connector. In Canada we have 'double insulated' tools that can be run on an isolation transformer with no ground path at all.

Yet I see relict code requirements for grounds and every year people are killed by touching a hot wire to ground, or when their radio falls into the tub.

More recently ground fault interruptor circuits were develooped to cut power if there is any flow detected outside of the wiring runs, iie in the ground..

__________________
Per Ardua Ad Astra
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#6

Re: Power Generation - Neutral And Ground

10/19/2007 12:05 AM

Read NEC Article 250. Section 6 says that the generator frame can serve as the grounding connection for cord-and-plug connected equipment. In this instance, no earth ground is required.

However, Section 61 requires that grounding and neutral functions be separated on the load side of a distribution panel, and must be handled by separate conductors. There must be an ungrounded ("hot") conductor, color coded with any color except white or green), a grounded, or neutral conductor, color coded with white insulation, and a grounding conductor, which may be bare, or colored green if insulated.

If this generator supplies electricity for an RV, read Article 551. There are some special requirements for recreational vehicles.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#7
In reply to #6

Re: Power Generation - Neutral And Ground

10/19/2007 2:16 AM

Then you can descend down to wiring colours.

3-PH + N + G = Red, White, Blue, Black, Green/Yellow trace

3-PH + G = (as above no Black)

Single Phase = Brown (A) Blue (N) Green/Yellow trace (Ground)

DC = Red (+) Black (-)

Then another country is different, like Black and Blue swapped ;o(

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply Off Topic (Score 6)
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#8

Re: Power Generation - Neutral And Ground

10/19/2007 5:00 AM

The ground line protect the human in case of the electric shock or fault.

And neutral is one of line of supply lines.

You can conect them in generator or transfomer but cannot conect them on control panel or the machine.

__________________
Nature is unlimited, human's knowledge is limited
Register to Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#9

Re: Power Generation - Neutral And Ground

10/19/2007 9:31 AM

Many machine manufacturers do NOT KNOW what to do with regards to earth and neutral either. We worked with machines from the states which, when connected up in europe would fail the safety tests as the neutral was in fact connected to the earth. Often we would have an inteference fault on the low dc voltage lines and in particular the electronic sensors. We would find that even in the low voltage dc lines the generated common or neutral or minus would be connected to earth at the end of the line, i.e. behind the last relay in a full bank of them. This was done for many years and not picked up on as it was not a problem untill plc's and electronic semiconductor items were being used. Still don't know the ins and outs of why it was done, all we knew was that prior to installation we always had to check all the earth and neutral connections and seperate them. Funny!

Register to Reply
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#10

Re: Power Generation - Neutral And Ground

10/19/2007 12:36 PM

Your question seems elementary at first, but you really do have a valid point. The power companies want the separate neutral and grounds for personal protection against electrocution as PWSlack replied. In the US, Neutrals and grounds are "bonded" ONLY at ONE point, the main service panel. After that, they are separated and for good reason, if there are parallel paths for the electrons, they'll take it! And we don't want no current flow on the ground circuit unless its saving your life.

We draw different pictures of a generator, is it portable? If so, as it rests, it probably is NOT making a good electrical connection to the earth, therefor, if you touched either the hot or common wire and were standing on the ground but NOT touching the generator frame, there's no reason for electrons to flow through you. But in America, its all about lawyers now, so needed or not, the manufacturer's follow the National Electrical Code

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Active Contributor

Join Date: Apr 2007
Location: Washington State
Posts: 19
Good Answers: 2
#11

Re: Power Generation - Neutral And Ground

10/19/2007 12:51 PM

Without the safety ground circuit the circuit protection device would have no means of sensing a situation in which the hot lead shorts to a conductive enclosure. A person that inadvertently completed the circuit from that enclosure to earth ground with their body would be very aware that something was amiss--if they survived the incident. This safety ground to neutral/ground buss connection heats the breaker/fuse and causes it to open; thereby protecting life and breaking the circuit before enough heat can be generated at the short to induce a fire.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12

Re: Power Generation - Neutral And Ground

10/20/2007 8:12 PM

I have forgotten what the breakers are called nowadays, they used to be called earth Leakage Circuit Breakers or trips....but they would have a big job saving someones life if not for the way earth and neutral are related.....in fact, they could not work at all....

They sense the line current and the neutral current and if any current is accidently diverted over the earth path, more that 30 ma I believe, it trips the supply.....

I have a long time ago, accidently touched live and put our training lab into darkness.....believe me it still hurt!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User
Popular Science - Cosmology - New Member

Join Date: Aug 2007
Location: Virginia
Posts: 122
#13
In reply to #12

Re: Power Generation - Neutral And Ground

10/20/2007 8:26 PM

I once touched one leg of a 440 3 phase system while wiring a motor. Had even pulled fuses ........ in the wrong panel. luckily i was poorly grounded and got no more then a proper tickle and a Lil numbness. Fuses in the panel were 200 amp per leg ..... i think i might have cooked awhile before it popped.

__________________
The major difference between a thing that might go wrong and a thing that cannot possibly go wrong is that when a thing that cannot possibly go wrong goes wrong it usually turns out to be impossible to get at or repair...Douglas Adams
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#14
In reply to #12

Re: Power Generation - Neutral And Ground

10/20/2007 8:36 PM

Here is the USA/Canada they call them "ground fault interrupters", we call earth - ground, so it is the same thing. All kitchens, laundry rooms and washrooms must have them retrofitted by the code, but many do not. All new houses must have them.

As soon as they see a current in the ground versus the neutral, they shut off.

Of course, if you touch the hot wire and neutral it does not care you = toast.

__________________
Per Ardua Ad Astra
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15
In reply to #14

Re: Power Generation - Neutral And Ground

10/21/2007 3:13 AM

One always hopes that at least 30 ma is going to find a way via ground, that way the circuit beaker pops!

NATO Ships are 440v 3 phase no neutral.....I once touched a phase, it sort of stopped my "processor" for many seconds, nasty! Luckily my heart was not affected....I always said, it was like sitting on the palm of a giant when he decides to clap his hands......real hard!

I prefer making my toast some other more banal way....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#16
In reply to #15

Re: Power Generation - Neutral And Ground

10/21/2007 4:33 AM

When I was real young, No not that long ago , I worked with my father in my school holidays.

He worked as a print technician rebuilding and repairing graphic machines, loads of fun. Anyway, He had to rig up a supply for a larger than normal machine one day and I happened to be there. He stood on a stool reaching into the distribution board and.....SHHHWSSHHHBANGGGGGG, I NOW KNOW THAT PEOPLE CAN FLY, BUT NOT LAND VERY WELL.

He had to go to the doctor to be checked out but according to the doc his rigger boots and the fact he stood on a wooden stool, saved his life.

He had only touched 600V

Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#17
In reply to #14

Re: Power Generation - Neutral And Ground

10/22/2007 9:00 PM

I'm not sure if it actually monitors the current in the ground, more like they monitor the current that isn't returned thru either of the 2 lines.

I used the same principle in VLF loop antenna's for the mining industry.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply Off Topic (Score 5)
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (2); aurizon (2); bubbapebi (1); case491 (2); Dragonfly (1); manirul (1); nam70 (1); PetroPower (1); PWSlack (1); Snaketails (3); Sniccus (1); wgh71 (1)