Anonymous Poster #1

Autotransformer Vector Group

08/31/2019 3:06 PM

Dear sirs,

We have a bank of autotransformer connected in three pase and has primary, secondary and tertiary. The connection is star/star/delta. But the vector group says YNa0d11.

How to interpret this? Similarly for a bank of autotransformer of 50/50/10 MVA, if we intend to keep for a full loading of tertiary winding, should the secondary rating be decreased or should the primary rating be increased? Similarly, the percentage reactance would be same for tertiary also?

Best regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#1

Re: Autotransformer vector group

08/31/2019 4:09 PM
__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Autotransformer vector group

08/31/2019 8:46 PM

Dear sirs,

It appears to me that YNa0d11 means star connected HV winding with neutral brought out, autotransformer with 0 degree displacement. LV winding delta connected leading HV by 30 degrees.

Please refer to my original question. The mentioned vector group does not give any information on secondary and tertiary winding. Is this to be understood that primary and secondary winding both are star connected?

Regards,

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4
In reply to #2

Re: Autotransformer vector group

09/01/2019 1:06 PM

You cannot have an auto transformer with a phase shift to LV [except due to reactance], because the LV terminal is just a tap on a "single" grounded winding. It would be the tertiary winding which was delta connected and the theoretical vector of a point of the Δ to ground would have the 30 degree shift.

In other words, the vector group gives information about the connection of the tertiary winding. It is likely that the voltage in the tertiary winding is "LV", hence d11 not D11.

Primary and secondary must be star, with zero vector group phase shift, because there is no other way to use auto transformers on 3 phase.

The percentage reactance is unlikely to be same for tertiary winding as from line to LV winding.

I would think the rating would be 50MVA for the winding A from HV terminal to tap & 50VA for LV winding B from tap terminal to ground i.e. 50VA delivered to external LV load. Since the voltage on winding A is less than HV incoming voltage its current rating will be higher than if it were at the HV voltage, for a specified MVA.

I may be wrong, but I cannot see another way of getting the correct terminal current limits from MVA rating.

This is obviously necessary because winding A must carry current for the tertiary winding as well as the current exiting LV part of the winding at LV voltage. With the tertiary winding voltage, you would know the current rating of tertiary winding. The HT terminal current x HV voltage would be greater than LV terminal current x LV voltage, with difference due to tertiary.

Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5
In reply to #4

Re: Autotransformer vector group

09/01/2019 1:10 PM

Apologies for error in post#4, I wrote 50VA for LV winding, when it should be 50MVA

Reply
Anonymous Poster #1
#6
In reply to #5

Re: Autotransformer vector group

09/02/2019 6:23 AM

Is primary mva = secondary mva + tertiary mva ?

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #6

Re: Autotransformer vector group

09/02/2019 9:04 AM

I think the MVA of the winding A from HT terminal to LV hot terminal must be given to get a correct current limit for the HV terminal - it is feeding both LV & tertiary windings.

The MVA of the external LV load must be supplied as well as the LV winding B contributing to tertiary winding C & losses as part of primary circuit.

There are only 2 voltages possible for HV MVA, HV line to LV tap or HV line to Ground. Using the second will only allow 50 MVA input, with 50 MVA LV output that leaves no power for 10 MVA tertiary or losses.

The relevant information for use is HV voltage, HT terminal current, LT terminal voltage & current and tertiary winding voltage & current which you can meter for operation and relay for protection.

You have not given HV - ground voltage or LV - ground voltage. Nor am I clear if this is 3 single phase transfo or one 3 phase transfo. All I know is that HV auto transfos have low ratios around 4 :1.

If you look at the actual voltages & work out currents as above you may find that HV input = LV output + tertiary MVA + [number for losses/magnetising current] which is believable.

I would consult the manufacturer on how to interpret the data to get the currents & impedances required. Also how they actually test for impedances - you could test from HV with only LV shorted, only tertiary shorted or both shorted. The usual 3 phase transfo with 3 limbs is not symmetrical - not all phases will give same impedance.

Do you have the factory test report? - it should give voltages & currents measured.

Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8
In reply to #7

Re: Autotransformer vector group

09/02/2019 4:42 PM

While I can’t figure how the EE who came up with how to design a tertiary winding even imagined it, I did run across an interesting article on how to set up your protective relaying, may be of help designing protection.

https://www.eiseverywhere.com/file_uploads/a99e2aa556135afc2ea43c68303bd462_zha_pap.pdf

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#9
In reply to #8

Re: Autotransformer vector group

09/02/2019 5:30 PM

Tertiary delta winding on star auto transformer, that is

Reply
Anonymous Poster #1
#10
In reply to #7

Re: Autotransformer vector group

09/02/2019 11:49 PM

This is 3 single phase atotransformer forming a three phase bank. The voltage rating is 220/132/33 kV.

Regards,

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#11
In reply to #10

Re: Autotransformer vector group

09/03/2019 12:19 AM

Yes, still looks like a recipe for disaster for an auto transformer, especially analyzing zero sequence current circulation. Someone had to say, "Sure why not", and figured out how you could interconnect the middle of one auto transformer winding to the middle of another, and make a cheap transformer.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#13
In reply to #7

Re: Autotransformer vector group

09/03/2019 7:51 AM

Not a good answer by me [except to consult test results]. Wrong! Wrong! Wrong! that is a 3 phase wrong!

As analysed in paper referenced by R Williams, the tertiary can be closed delta so it does not draw power in normal operation when phase-ground voltages are equal. The 10MVA/33kV indicates the current rating & ratio for the tertiary winding, while 50MVA/50MVA indicates normally all HV power goes to LV.

67model

Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #7

Re: Autotransformer vector group

09/03/2019 9:06 AM

To answer the Original Post question, correctly, primary input 50MVA/LV 50MVA/Tertiary 10 MVA suggests that if auxiliary power is taken from tertiary [at maximum 10 MVA] then LV MVA must be reduced to 40 MVA.

The primary power could not be increased if the primary windings are designed for the losses/current at 50MVA, 60 MVA would increase primary winding losses by about 50%.

This is a simplification, because reduced losses in LV may allow some increase of losses in HV.

The OP is in a position to know for what actual continuous simultaneous current loadings, LV & tertiary, the transfo was ordered & tested. The factory test ought to be based on the the ordered continuous loadings. Similarly, OP should be able to find if tertiary is connected to a 33kV load or not.

If the transfo were designed for a tertiary winding functional only for harmonic and fault currents, then 50/50/10 MVA makes sense. For a continuous tertiary auxiliary load of 10MVA, then 60/50/10 MVA seems correct for continuous 50MVA from LV.

If, on load test at 50MVA input, 50MVA LV load, zero tertiary load; the HT winding [the one connected to the HV terminal], or LV temperature rise by resistance was already at maximum permitted, then there is no margin for tertiary load.

Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#12
In reply to #4

Re: Autotransformer vector group

09/03/2019 1:14 AM

You have just reminded me why I studied Mechanical Engineering.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: Autotransformer vector group

09/01/2019 5:33 AM

This can be a very complicated subject,as there are many possible configurations of secondary.

The tertiary windings are normally connected in Delta.

It is too deep to go into here,and to repeat the info that is freely available.

If you truly understand transformers and how they work,things will become easier to comprehend.

I suggest further study in the area.

Much info is available on Google.

As someone once said,"I can teach it,but I cannot learn it for you."

I wish you good luck in your pursuit of knowledge.

Here is a link that explains tertiary windings:

https://www.electrical4u.com/tertiary-winding-of-transformer-three-winding-transformer/

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Reply to Forum Thread 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (5); Anonymous Poster (3); HiTekRedNek (2); rwilliams (3); The Prof (1)

Previous in Forum: Rating of Pump   Next in Forum: High Voltages Seen on CT's

Advertisement