GIS Bays

09/11/2019 11:18 PM

Dear all:

GIS bays are 9 for 132 kV GIS in our typical case. But while going through the single line diagram, I found that there are so many pressure gauges to read the gas pressure in various compartments.

Does many pressure gauges implies many motors that gets started once a low gas level alarm is sounded? Is this automatic or we have to start the motor after low gas level alarm is sounded? In that case gas needs to be filled from single gas storage source.

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: GIS bays

09/12/2019 1:13 AM

I believe you are talking of a gas insulated substation (GIS)

To answer one question, many pressure gauges does not mean many motors get started at once.

How many motors are started depends on how many there is in the first place and what the starting logic says.

Besides the single line diagram there should be more documentation about the station. The more information you provide here and the clearer the question the better the help you can get from the people in this forum.

All the best

__________________
Common Sense Dictates
Reply Score 1 for Good Answer
Anonymous Poster #1
#4
In reply to #1

Re: GIS bays

09/16/2019 3:51 PM

I am not able to upload pictures from attachment.

Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: GIS bays

09/12/2019 3:54 AM

GIS is not supposed to require topping up or filling of gas in its life time.

The pressure gauges are provided to monitor the gas pressure and sound an alarm in case the pressure goes down to a level that is unsafe to operate.

The pressure loss to that extent could only happen if there are leaks due to improper installation etc.

Since, the leakage rate is so low and no topping up is envisaged during the life time, no automatic refilling is provided for this gas.

Moreover SF6 gas comes under 'Green house gas' category and is subject to restrictions in use and disposal due to environment concerns.

__________________
Raghunath
Reply Score 1 for Good Answer
Associate

Join Date: Feb 2017
Posts: 42
Good Answers: 1
#3

Re: GIS Bays

09/13/2019 9:26 PM

See this slide giving a few examples of how to trip on low gas pressure:

https://www.slideshare.net/ercachaq/presentation-for-seminar-fixed

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Electron Spinner (1); IdeaSmith (1); raghun (1)

Previous in Forum: Higher Fault MVA   Next in Forum: Rotation of Generator in Opposite Direction

Advertisement