Rotation of Generator in Opposite Direction

09/12/2019 3:37 AM

What will happen if we rotate a generator in opposite direction ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: Rotation of generator in opposite direction

09/12/2019 3:46 AM

Nothing wrong electrically. But, the cooling is affected as the shaft mounted fans have curvature designed for certain direction of rotation. This will cause overheating of windings and associated damage.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#3
In reply to #1

Re: Rotation of generator in opposite direction

09/12/2019 11:21 PM

The exciter brushes for the DC to the rotor are often rotationally offset on the slip rings to have a leading and trailing edge which may also have unwanted consequences to the other cooling effects.

Any ancillary items on larger machines, like lube pumps, may be direction sensitive so lubrication also becomes a problem.

__________________
Hare today, goon tomorrow!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Rotation of generator in opposite direction

09/12/2019 6:26 AM

Apart from mechanical effects on auxiliary items like shaft driven pumps or fans mentioned by raghun, the phase rotation will be reversed.

If you then connect to a standard system without swapping generator wires, then motors will rotate backwards, which is likely to cause trouble.

If you parallel with other generators or Grid, it is possible to get 180 degrees out of phase [ a properly connected check or auto-sync unit will not allow]. While generators are designed to survive a short circuit, such a connection causes twice the current and generator will be wrecked.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Rotation of Generator in Opposite Direction

09/13/2019 3:13 PM

One of the possibilities is being invited to work elsewhere on the grounds of a mismatch between the required, and the demonstrated, competence.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#5
In reply to #4

Re: Rotation of Generator in Opposite Direction

09/16/2019 11:37 AM

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply