Bushing Current in Transformer

09/27/2019 8:42 PM

Dear sirs,

Bushing rated currents for transformers are calculated for three phase only?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Bushing current in transformer.

09/27/2019 9:09 PM

They are generally used for existing transformer protection...

..."A transformer bushing CT (BCT) is a window-type current transformer mounted around the bushing’s flange. They may be inside the main tank (under the cover) or mounted externally. A bushing type CT consists only of a toroidal-shaped core with a secondary winding. The bushing’s centre conductor forms the single turn primary of the BCT. More than one ratio is provided by tapping the secondary winding at multiple increments along the winding. The secondary winding terminals of the BCT (and the BCT’s nameplate) are accessible in the transformer’s control cabinet.

BCTs are typically used for protective relaying purposes. Whether used for protection or metering, the saturation of a CT is undesirable. When operating in saturation, the secondary output current is no longer a miniaturized replica of the primary current but rather a distorted version with a lower than expected amplitude. This may result in the possible misoperation of the protection system.

If used for protective purposes, a current transformer is designed to saturate at extremely high current levels so that the transformer bushing CT can successfully perform its important intended function of accurately capturing (high) fault current information. However, if the CT has excessive residual magnetism, it will saturate sooner than expected. Remanence flux is dissipated very little in service and requires demagnetization of the core to remove.

Testing is important to verify a BCT’s accuracy and performance characteristics, to validate that a very low level of remanence flux exists in the BCT, and to demagnetize its core if not."...

https://megger.com/applications/transformers/bushing-cts

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Bushing current in transformer.

09/27/2019 11:54 PM

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3
In reply to #2

Re: Bushing current in transformer.

09/29/2019 2:06 PM

What are the voltages HV/LV & rating of your transformer??

One could then have an idea about bushing rating.

A 3 phase transfo would have bushing current rated by its 3 phase rating - but a single phase transfo used as one of a set of three for 3 phase would have a single phase rating in kVA 0.333 of a 3 phase transfo of same rating. However, the bushing current rating would be the same for both.

So is this a three or single phase transfo??

Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#4

Re: Bushing Current in Transformer

09/29/2019 2:09 PM

No, each current transformer measures single phase current. You combine the currents according to the equipment the transformers are mounted on, to derive 3 phase kW or kVA.

Reply