VFD With Step Down Transformer for Speakers and AVR

09/26/2019 4:05 AM

I have Marantz NR1607 AVR which input is 120v 60Hz (230w), DT Pro Cinema 600 (5.1 channel speakers) and input is 120v 60Hz (230w).

Currently I live in Malaysia and the Main power is 240V 50Hz.

I have bought step down transformer which supports for (1750w) which i can connect both of above devices.

But the problem is since frequency is 50Hz, devices is not working even step down to 120v.

Can i use VFD to solve my issue or any other option like fixed conversion from 50Hz to 60Hz

If VFD is the option, how do i setup. Mains => VFD => Step down Transformer => Speakers & AV Receiver

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: VFD with Step down transformer for Speakers and AVR

09/26/2019 4:18 AM

Talk to these people (not an endorsement - other power changer suppliers are available).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: VFD with Step down transformer for Speakers and AVR

09/26/2019 8:03 AM

I would have thought that the input to the unit would be pretty much immediately rectified and filtered to DC, and therefore the input frequency would have little effect on the device. Most amplifiers will work just as well on 50Hz as they will on 60Hz of the same voltage.

Occasionally the filtered DC output voltage can be a tad lower at 50HZ due to the higher XC effect of the filter caps, but I would not expect it to be of great concern.

Are you certain that there is not something else that may be causing your problems?

Edit:- A check of a local Marantz website shows that the unit may be connected to either 50 or 60Hz. Although this is a 240V unit, I would not expect a 120v one to differ greatly in that regard

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2019
Posts: 10
#3
In reply to #2

Re: VFD with Step down transformer for Speakers and AVR

09/26/2019 9:32 AM

I bought Marantz AVR and speakers from US Amazon.com. Each Marantz is different, some other Marantz devices might support 50 to 60Hz. But the one which i have will support only 120v 60hz frequency.

I thought the same before buying that step down transformer like It will convert from 240 to 120v and 50Hz to 60Hz, but it is only converting 240 to 120v, Hz output is same as input Hz. Later i read this point.

The device is switching on and with in 4 seconds, it's switching off with blinking indication. As i read online help for this unit, if input power is incorrect, it will off and blink.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 11:52 AM

So, what's wrong with swapping it for a replacement that has the correct power input configuration, and saving the trouble and outlet on a power converter unit?

This is hardly an Engineering consideration; merely a commercial one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#8
In reply to #4

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 9:50 PM

I tried for replacement, but its not be possible, because I bought form USA and I stay in Malaysia.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #8

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 4:16 AM

Nevertheless, re-ordering the correct one, from wherever, and selling-on the wrong one, into wherever, remains among the options for a solution.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 1:39 PM

No, you cannot use a VFD for this purpose. VFDs are designed to work for AC induction motors. It USES the inductance of the motor to complete the process of recreating a pseudo-AC 3 phase voltage. You don’t have a motor and the power supplies in the audio equipment is not designed to handle the harmonic rich PWM output of the VFD, even IF the VFD does not trip out when it sees no load on one of the phases.

If you must proceed with using this audio equipment in a part of the world it is not designed for, used a voltage converter designed for this purpose. It’s likely however that if this version is not rated for dual sources of input, that means it is older and uses linear power supplies instead of switch mode power supplies. That might mean that any electronic frequency changing system is going to result in noise coming through the audio as background humming.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#9
In reply to #5

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 9:55 PM

The Transformer which I have is...

https://www.amazon.com/Dynastar-Converter-Transformer-Lifetime-5-Year-Warranty/dp/B01576TI6I/ref=sr_1_2?keywords=1750w+transformer&qid=1569549155&sr=8-2

Is there any other way to convert only frequency 50Hz to 60Hz. This transformer will take 50/60Hz input and same output.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#14
In reply to #9

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 12:30 AM

Unfortunately not. The transformer does not alter the frequency like an electronic VFD or electronic inverter.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 2:05 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#10
In reply to #6

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 10:01 PM

This will support for one device. because I need to buy 3 times the rated watts of device. I have AVR 230Wt and Speakers 230wt, So I need to buy 2 units which is very expensive than the devices. Instead I can buy new same devices which support 240v Input.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 2:48 PM

It would likely be cheaper to just buy the correctly rated amplifier unit(s).

It can be done with a step up power inverter but it is expensive and a little messy. I wouldn't recommend trying to use a motor VFD to perform the conversion.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#11
In reply to #7

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 10:19 PM

Yes, You are so true.

but since I have already bought these devices which I spent $11,000. Initially I spoke with one of the device support engineer, they have suggested step down transformer to use in my country. I thought that Step down transformer are made for this purpose. After I have tried, its failed. I didn't knew when I bought all these, now because of frequency both the devices are kept aside.

Now I understood that conversion of frequency from 50Hz to 60Hz is very complex and sensitive for electronic devices, especially audio equipment's.

If anyone find the solution which is cheaper, I will be very happy, otherwise my $11,000 will be trash.

Register to Reply
Active Contributor

Join Date: Sep 2018
Posts: 17
Good Answers: 1
#12
In reply to #11

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 10:33 PM

Hi Praveen,

There are transformers on the market with frequency converters look on google and you can find them. they are a little expensive but a lot less than 11000 USD

I know nothing about this company -- it was the first legitimate looking one that popped up on Google .

Check them and search your self. Ali Baba showed up a lot of them but they all looked fake to me.

Good Luck

Expat07

Frequency Converter 50Hz 60Hz, and 400Hz | ATO.com
https://www.ato.com › frequency-converter

Built in step-up/step-down transformer convert US power supply 120V 60Hz to UK 230V/240V 50Hz, step down 1-phase 220V 50Hz to 110V 60Hz. Three phase ...

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#25
In reply to #12

Re: VFD With Step Down Transformer for Speakers and AVR

09/30/2019 1:22 AM

11,000 Malaysian Ringgit = $2627.13 USD

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#15
In reply to #11

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 12:36 AM

That is very unfortunate if that is the case. Many of the amplifiers down here support dual 50/60Hz operation.

Any chance on a return and refund?

You may have to sell it online and take the loss and buy the correctly rated one as opposed to purchasing an expensive inverter to get the one you have to operate.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#26
In reply to #15

Re: VFD With Step Down Transformer for Speakers and AVR

09/30/2019 2:13 AM

I bought these last year and even to return i need to go USA, can't return from Malaysia.

It was my mistake that i thought step down transformer will take care of everything.

No one in Malaysia will buy this online, because of input power. I can sell this one only in USA.

Thanks for your concern.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #11

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 4:36 AM

<...spoke with one of the device support engineer...>

Bear in mind that this individual has a vested interest in its not returning for a refund!

<...$11,000...>

That would be a trivial amount in Zimbabwe.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Engineering Physics - New Member

Join Date: Oct 2006
Location: MSP, MN
Posts: 728
Good Answers: 8
#13

Re: VFD With Step Down Transformer for Speakers and AVR

09/26/2019 10:36 PM

A motor-generator set with 240v 50hz motor and 120v60hz generator.

Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#16
In reply to #13

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 3:47 AM

You mean VFD?

If VFD, it won't be the best solution as suggested by some one in this discussion.

If not VFD, Please clearly explain the solution.

Thank You

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #16

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 4:41 AM

<...VFD...>

No. A motor-generator, as indicated.

John: 11, 35.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#17
In reply to #13

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 4:03 AM

One way to achieve this is to use the motor generator set as described but not direct coupled as the 50hz 2 pole synchronous motor will run at 3000RPM while the generator will need to run at 3600RPM. I have used a similar setup on an oil rig where the conversion was from 600v 60 HZ to 415V 50HZ and was achieved by having a 10 inch pulley on the motor driving a 12 pulley on the generator but then I was extracting 25KW not a smaller amount but it would work with the pulley ratios reversed to get a step up in speed.

Surely you could return the goods for a refund or has the time limit expired?

__________________
Hare today, goon tomorrow!
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#20
In reply to #17

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 4:37 AM

Return is not possible because someone brought from USA to Malaysia, no one will take these huge items back for return.

What is Motor Generator? is this VFD?

If not VFD, Is it good for to use for Audio equipment's?

Register to Reply
Guru
Engineering Fields - Engineering Physics - New Member

Join Date: Oct 2006
Location: MSP, MN
Posts: 728
Good Answers: 8
#24
In reply to #20

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 9:35 AM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#29
In reply to #20

Re: VFD With Step Down Transformer for Speakers and AVR

09/30/2019 4:17 AM

See #20⇑.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#30
In reply to #17

Re: VFD With Step Down Transformer for Speakers and AVR

10/02/2019 2:04 PM

This setup will not be very efficient nor will it be silent, and unless he can find the parts for very cheap, then it will be cost prohibitive as well...all-in-all not worth the effort or expense.....

The only way I see that this system could be made to work is if he could procure an accurate wiring diagram for the amplifier and convert the components needed to accept the power source available....and this would probably only be worth it if the labor was free, or really cheap....but an accurate wiring diagram with components listed, is probably not easy to acquire...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 4:43 AM

There seem to be all sorts of reasons for not doing things and it is best not to constrain the problem beyond the point where one of the options is viable.

Evaluation of the options and selection of the best solution is very much on the basis of personal preference, something with which the forum cannot really help.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2014
Posts: 33
Good Answers: 2
#23

Re: VFD With Step Down Transformer for Speakers and AVR

09/27/2019 9:27 AM
Register to Reply
Active Contributor

Join Date: Sep 2019
Posts: 10
#27
In reply to #23

Re: VFD With Step Down Transformer for Speakers and AVR

09/30/2019 2:16 AM

Those products are very expensive. For that price I can buy new items that support 240V.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#28
In reply to #27

Re: VFD With Step Down Transformer for Speakers and AVR

09/30/2019 4:16 AM

The forum cannot help with option evaluation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 30 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Epat07 (1); jack of all trades (3); johnhotmer (1); JRaef (1); PWSlack (8); SolarEagle (3); spades (1); SSCpal (2); Stef (1); tpraveen79 (9)