Hydronic system calculations

10/20/2007 12:07 PM

Hi,

I am trying to size a pump for a 3/4 copper pipe system. The system includes 6 ells, 2 butterball valves, and the isolation valves on both sides of the pump. Flow is around 5 gpm.

The water-to-water heat exchanger is an old one I have lying around, but there is no information about it's friction loss available. It appears to be 3/4 inch cu pipe inside 1 1/2 inch cu pipe.

I ran the numbers using the "Copper Tube Handbook" to find the friction loss per fitting, and ended up with about 21.23 psi loss.

Then I ran it through the Global Spec. Calculator and found much, much lower friction loss. It came out as:

Pressure Loss: 0.525 psi Head Loss: 1.212 ft.

So, any ideas which one is correct?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#1

Re: Hydronic system calculations

10/21/2007 5:05 AM

My guess is that it might be related to pump curves, efficiency, positive vs variable displacement, viscosity, valve bore, Reynolds number used, radius of els, length of run, to name a few. Both numbers are right, and both are wrong. For differing flow rates and pressures.

Don't forget your wier plate.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Anonymous Poster
#2

Re: Hydronic system calculations

10/21/2007 7:08 AM

how many miles of straight pipe?

Register to Reply
Active Contributor

Join Date: Aug 2007
Posts: 17
#3

Re: Hydronic system calculations

10/21/2007 7:21 AM

I think the right number is somewhere between those two. Unless you are using really heavy walled pipe, you should have minimal pressure drop going through the pipe and fittings. I see the heat exchanger as the big unknown. Can you borrow a 5 gpm pump and measure the pressure drop through it?

Register to Reply
Anonymous Poster
#4

Re: Hydronic system calculations

10/22/2007 12:08 PM

butterball valves, like the turkey?

Register to Reply
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#5

Re: Hydronic system calculations

10/22/2007 7:55 PM

You don't have a whole lot of selection when you're down that small. My sense is you'd just like to be directed in the sensible path to the cheapest effective circulator that will do the job.

If you want to purchase NEW equipment, a Taco 007 or Grundfos UP-15 is the right pump for the right price.

You can also do just as well with a circulator found at a garage sale.

BUT ! If you're pumping fresh water, ( drinking water ), you'll need the same HP pump, (approx 1/16 hp) but with a STAINLESS or BRONZE BODY, otherwise it'll grow shut with rust.

If you're still bent on doing some math, look up the pressure drop curves of similar looking plate exchangers as yours and choose a pump that will give you the GPM you desire while overcoming the plate exchanger's pressure drop. ( I'm assuming that the exchanger's CV is well in excess of local piping, if not count the CV of other major pressure drops.) PS. stay away from butterball valves, they'll gook up the impeller.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Member

Join Date: Sep 2007
Posts: 6
#6
In reply to #5

Re: Hydronic system calculations

10/22/2007 8:29 PM

Yea, the copper system requires a bronze pump or there will be damage. Taco 007 or a small Grundfos are likely the size I need, but I am trying to balance the pump with the right psi loss so I have a built-in flow regulator: the back pressure.

I have looked at a lot of bronze pumps and even have a request in with one supplier for info, but they do not appear to be too eager to provide the answer to my friction loss question.

Too bad... without that information, I cannot purchase their pump, whichever it is.

By the way, Sniccus, if not butterball valves, what does your experience suggest?

Register to Reply
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#7
In reply to #6

Re: Hydronic system calculations

10/22/2007 8:57 PM

That was as "tongue in cheek" reply. Valves are either BALLVALVE or GATE VALVE or BUTTERFLY VALVE or STOP and WASTE.

Don't get off on a rabbit trail here. You're building a widget to move heat from one place to another. There are fundamental formulas for doing this.

The amount of heat (in BTU's) you needed determines the size of the heat exchanger. It also begins to tell you how strong of a pump you need.

Determine your BTU requirement

Choose a heat exchanger with more than enough BTU's required

Add up your friction losses (in ft. of head) of the heat exchanger, fan-coil and interconnecting piping, (mainly elbows).

Choose a pump that meets or exceeds the GPM needed while meeting or exceeding your perceived friction loss.

Now, you can get same btu delivery with a SMALLER exchanger and a BIGGER pump, or with a BIGGER exchanger and a SMALLER pump. ( Remember if you use an exchanger just big enough, you'll need to force the water through at a high velocity requiring a much stronger and EXPENSIVE pump. I like really oversizing heat exchangers and using smaller pumps for a variety of reasons.

Also, size your pump so it is operating in it's "sweet spot" which is approx. 80%. Don't ever use a pump where it is operating at the TOP of its curve or the BOTTOM of its curve , you'll burn it out.

ALWAYS....put your expansion tank as close to the suction side of the pump as you can.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#8
In reply to #7

Re: Hydronic system calculations

10/22/2007 9:36 PM

You forgote globe valves.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Member

Join Date: Sep 2007
Posts: 6
#9
In reply to #8

Re: Hydronic system calculations

10/23/2007 5:01 PM

To resolve the unspoken question, I should mention that the "Butterball Valves" are butterfly valves manufactured by Milwaukee Valve Company.

Register to Reply
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#10
In reply to #8

Re: Hydronic system calculations

10/23/2007 9:34 PM

I had "globe" valves in mind but it slipped away as I was typing, there's no doubt more.

I got onto a real roll there..hehe.... I teach this stuff at Community College night classes.

Most of what I learned was the hard way. I like teaching electrical theory and troubleshooting because the math equations are typically verifiable with measurements, but not always so with other sciences like fluid flows and heat transfers. ( Usually because the formulas contain other unknown variables.) I like to think that common sense should be used as a "checks-and-balances" procedure for big calculations.

When I bid projects, I always check against old school rules of thumb just to make sure I've not "drifted out to sea" with good reason.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#11
In reply to #10

Re: Hydronic system calculations

10/23/2007 10:09 PM

My first exposure was a 400,000 sq ft high school, with a 3 pipe system (hot,chilled, and return), and summer/winter day/night pneumatic operations with 4 150,000 hp hot water water tube boilers. 3" and over needed globes for throttling, ball valves under. No victraulics when it was built 1964, Threaded 10" pipe. I was supposed to freeze up the school so they could sell the property. Nobody told me in the 4 years I ran it, but it was one of the 2 jobs that I compromised when I was fired and said I'd leave in 6 months. Got by with it both times. I think they figured out that if I didn't freeze up in 2 -27 F winters, wind chills approaching -80, then I was a total failure at what I was hired for. On of the times I tried to leave the construction end.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#12
In reply to #11

Re: Hydronic system calculations

10/23/2007 10:29 PM

You're doing bigger projects than I am, except I'm getting some awfully big warehouses now, that's all they're building here in Pa. is warehouses. And they're easy to heat, big make-up air units, big ventilation, standard RTU's for office spaces.

Schools and other public-funded projects sometimes can get the $$ for better than "bottom line" mechanical systems but rarely are they a complete "common sense" top- shelf installation.

I love to see new "leading edge" installations that get written up in magazines. For everyone of those, there are 10 more that 'could've been if '

My favorites are ground-source installations. They've come a long way....

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#13
In reply to #12

Re: Hydronic system calculations

10/23/2007 11:00 PM

Bolingbrook IL is roughly 8 million sq ft of houses and 60 million sq ft of tilt-up warehouses, 10 to 20 acres, 40 million still empty space, but they keep building them. 20 people work in a half million square feet, moving made in China stock, shipping it to home ebay sellers who pay no local or federal tax on their money, and have no cares about quality, warantees, lead, melamine, sold on paper from brocker to brocker, and why would no-one want dollars oversees?

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#14
In reply to #13

Re: Hydronic system calculations

10/24/2007 10:02 PM

And so goes our country....what ever happened to "build America, buy American" ???

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#15
In reply to #14

Re: Hydronic system calculations

10/24/2007 10:49 PM

Management convinced the workforce that they were better than the unions. No one left to make the companies give insurance, pensions, or even jobs.

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings