Hi All,
We have a project in which we have 90kW condenser water pumps for the cooling towers and at the time of changeover to delta, the breaker control panel (200A) and the main panel sub breaker (250 A) are simultaneously tripping.
With the setting of time delay , short circuit and overload at maximum still the same tripping is observed. Testing has also been done with the connectivity of pump in minimum load without success. At no load without the connection the changeover is successful.
Please advice.
ABB T3N250 MA200 is being used. While Wienman pumps are at design rpm 1450 189 l/s flow .
The installation is brand new.