Anonymous Poster #1

Induction Motor Synchronisation

10/08/2019 10:07 AM

I have a overhead conveyor belt for unloading materials from production floor to warehouse. The belt runs by two exactly identical motors. 2.2kW, 3 phase AC, 415V, 50Hz, 1415 RPM, current-4.8 A, frame size-110L. The motors are run by two separate VFD-Siemens make micromaster-440, 2.2kW. Both motors are run at 50Hz settings. Load current of both motor are around 4.4A. One of my motors got damaged. I don't have a similar motor available. I am thinking of replacing only the damage motor with the following motor.

3kW, 3 phase AC, 415V, 50Hz, 1415 RPM, current-6.2 A, frame-110L.

Now if I use this motor, will their speed the in synchronisation under load?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: Induction Motor Synchronisation

10/08/2019 10:54 AM

Synchronous motors run at exactly the power frequency, whereas induction motors run slower than the frequency, and as their load increases they run slightly slower with increased torque. I suspect the larger replacement motor will slow down less than the original motor under the same load.

If the two motors are mechanically connected, this probably won't be a problem, the larger motor will just assume more of the load and generate more torque (more motor current).

Reply Good Answer (Score 3)
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Induction Motor Synchronisation

10/08/2019 12:34 PM

Are the conveyors belt driven or direct drive?

..."If the motors are not mechanically coupled, we need to decide what is more important for the application: load sharing or speed matching. If speed matching is the goal, run each VFD in a closed loop vector mode. If load sharing is the goal, use a comparator to bias the speed of one VFD to equalize the loads."...

more solutions here...

https://www.controldesign.com/articles/2002/235/

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3

Re: Induction Motor Synchronisation

10/09/2019 1:42 AM

You indicate each drive is run by their own VFD.

If so, can the VFD supply the higher current? The magnetizing current for the larger motor will be a little higher. Check the NP data.

Now, I am not familiar with the Siemens VFD, but the competing products can estimate the motor RPM to very close tolerances. Assuming the VFD is set to actually run RPM and not in scalar mode (HZ) there should be no problem. However the drive will need to be "tuned" for the new motor.

If you are actually running in HZ (V/HZ, scalar, etc) mode, then just tweak the frequency until the motor runs at the speed you want.

Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4
In reply to #3

Re: Induction Motor Synchronisation

10/09/2019 2:02 AM

The Micromaster drive has a hardware current trip that is not accessible in the software. You shouldn’t have a problem if your breakaway torque is not too high. While fine for variable torque loads, you can need extra torque at start for constant torque loads (like your conveyor) that the drives will not provide, if sized close to the motor kW rating. Adding a little more magnetizing current could possibly send a marginal application over the edge, but worth a try.

I ended up having to replace each drive on some 1.5kW motors running progressive cavity pumps, the pump shafts never turned, drives tripped immediately on Run Command. The equipment package supplier or consultant was not used to those drives, where you as the application engineer need to account for load characteristics beyond drive nominal kW rating.

Reply
Participant

Join Date: May 2011
Posts: 1
#5

Re: Induction Motor Synchronisation

10/09/2019 2:34 AM

Consult manufacturer of VFD if it is OK to run a 3 kW motor using a 2.2 kW rated VFD.

The answer may be negative.

It is simpler to get a 2.2 kW motor than to replace a 2.2 kW VFD with a 3 kW rated VFD.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Induction Motor Synchronisation

10/09/2019 3:29 AM

The nature of the <...damage...> is of interest.

It may prove attractive to order two replacement motors, and keep one as the strategic spare.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#7

Re: Induction Motor Synchronisation

10/09/2019 4:11 AM

The Micromaster 440 comes in several versions each rated for different loads. The crucial point for you is that the next up from a 2Kw is the 3Kw. So if you have been running a 2.2Kw motor on you existing VFD it must be the 3Kw version and it will be compatible with the larger motor. If you run the upstream VFD using the 4-20mA input (AIN1 terminals) from an independent signal derived from the speed of the downstream conveyor speed (not the VFD) then the two conveyors will always match speeds. Don't connect the up and down stream VFDs over than the order that I have indicated or in the event of a downstream failure you will get a pile up of product at the junction.

Reply Score 1 for Good Answer
Anonymous Poster #1
#8

Re: Induction Motor Synchronisation

10/10/2019 8:05 AM

Thanks all for sharing your experiences.

I replaced the VFD with a spare one (4kW rated, other specifications, make are same) that I had. I am running the conveyor. Motors are coupled with the gearbox by belts. So far it is working fine but sometimes under heavy load, I am observing some mechanical jamming on the larger motor side (3kW). It seems that chain conveyor is getting jammed for a moment but conveyor never stopped from running. But its very minor till now. I am coordinating with the mechanical team to assess whether it's a fault on their part or not.

Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #8

Re: Induction Motor Synchronisation

10/11/2019 2:04 PM

You might have some bad roller bearings in the conveyor belt itself that is causing the stress on the motor...this could be the reason for the motor fail...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Reply to Forum Thread 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); chuck cowlagi (1); GW (1); jhhassociates (1); PWSlack (1); Rixter (1); rwilliams (1); SolarEagle (2)

Previous in Forum: Phase Rotation   Next in Forum: Single Core Cables - Above 95 sqmm

Advertisement