Generator CT

11/13/2019 9:49 AM

In a power plant, a small blue cable is connected between the generator (11KV,50MW) phase terminal and the CT moulding/casing of window type CT mounted on the generator phase terminal. The cable is the blue one shown in the picture. Can someone explain what the purpose of this cable is?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#1

Re: Generator CT

11/13/2019 12:01 PM

The purpose is to electrically connect them together.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Generator CT

11/13/2019 12:11 PM

Yes. The person who created the "as built" drawing for the installation can do that.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9917
Good Answers: 1141
#3

Re: Generator CT

11/13/2019 12:30 PM

Are you sure that it's around a phase and not the neutral?

Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#10
In reply to #3

Re: Generator CT

11/14/2019 7:32 AM

Yes , see my question where it is written as "CT mounted on phase terminals". the 3 No. CTs mounted on 3 No. Phase terminals have same small cables connected between CT casing and phase terminal bars.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Generator CT

11/13/2019 12:43 PM

Looks like a neutral wire connection to me...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9917
Good Answers: 1141
#6
In reply to #4

Re: Generator CT

11/13/2019 2:52 PM

I don't know if this is applicable, but in Europe, Blue is Neutral...

https://electricalfundablog.com/wiring-color-codes-usa-uk-europe-canada/

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #6

Re: Generator CT

11/14/2019 11:55 AM

Ah! Those are the latest harmonised colours. Prior to 2004 the colours in the UK were red/yellow/blue for the three phase colours, and black was the neutral.

The forum has no information about the age of this installation, nor its location.

It's still looking as though a copy of the "as built" drawing will answer all of the Original Poster's questions. Such a document should always be the first port of call on queries like this.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#11
In reply to #4

Re: Generator CT

11/14/2019 7:34 AM

Why would CT neutral be connected to 11KV bar?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #11

Re: Generator CT

11/14/2019 10:55 AM

The question is impossible to answer without sight of the "as built" drawing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#13
In reply to #12

Re: Generator CT

11/14/2019 11:19 AM

From the angle of the single image, I'm not sure that right angle bus bar is connected to anything else but the blue wire. I realize that the image taken may be the best image possible in a cramped space but this is exactly why a drawing should be examined.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#5

Re: Generator CT

11/13/2019 1:17 PM

Whatever this wire does, I don't like how it is installed. That's a very sharp bend around the bus bar. If it was connected to the other side of the bus bar the strains would be much less on the wire.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Generator CT

11/13/2019 8:23 PM

Look at the schematic.

Ask the electrician.

You could have the electrician use a meter to identify its function.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#8

Re: Generator CT

11/14/2019 12:21 AM

The only entity that can answer this question accurately is the manufacturer of the current transformer. I’d guess that this wire assures the iron core of the CT is at the same potential as the primary conductor. They may have had problems with the secondary insulation they attributed to static charges in the insulated case?

This is unusual construction in my +20yr experience with 15kV class window type current transformers.

Register to Reply
3
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Generator CT

11/14/2019 6:44 AM

Window type CT encounters two layers of insulation - one is air between the 11kV phase conductor and the epoxy outer of the CT, the second is the epoxy insulation to the earthed secondary of the CT.

In some designs, the two layers cause potential grading issues due to unequal capacitances of two layers. Hence, some of the CT vendors provide a metallic shield in the outer part of the epoxy and connect it to the phase conductor. With this, the epoxy only has to be rated to withstand 11kV potential with no capacitive grading issues.

I have seen a case where the CT burst as the shield was not connected to thephase conductor and sustained discharges that ensued, led to CT damage over a period of time.

__________________
Raghunath
Register to Reply Good Answer (Score 3)
Register to Reply 14 comments