HRC Fuse Blow

11/15/2019 6:03 PM

I have came across many incidences when a 3 phase motor insulation fails in one winding (winding to body) with the other two windings are ok (winding to winding as well as winding to body). But always noticed that two fuses blow together. Why so?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: HRC fuse blow

11/15/2019 7:10 PM

Draw a schematic of a three-phase winding with a fuse in each of the lines. Then show a short circuit from one winding to the body (earth). You will see the answer.

Reply Good Answer (Score 3)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: HRC fuse blow

11/16/2019 12:11 AM

Could it be Delta connected motor!!

__________________
Raghunath
Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#3

Re: HRC Fuse Blow

11/17/2019 2:31 AM

Two of the windings in delta connection will both feed the fault that is why the fuses blow because the resistance between the ends of the faulty winding is decreased by the earth fault making the winding two parallel paths via the earthed neutral connection.

I believe that if one winding shorts to earth then both the other windings will show a low resistance to earth. For the other two windings not to show a low earth resistance then the winding with the fault has blown clear or the method of testing is inadequate for the supply voltage unless the terminal box has been opened and all the winding leads separated from each other.

Anyway it doesn't matter for when the new motor is installed all the fuses should be changed not just the failed ones because the other fuse may/will have been stressed.

__________________
Hare today, goon tomorrow!
Reply
Active Contributor

Join Date: Jun 2019
Posts: 12
#4

Re: HRC Fuse Blow

03/10/2020 11:14 PM

The two phases feed the fault that is why the two fuses blown off when there is insulation failures in any of the winding.

Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); raghun (1); Stef (1); vimal76 (1)

Previous in Forum: Coelmo Generator 500KVA AVR Fuse Blows Up Showing Low Voltage   Next in Forum: Cover Block Preparation

Advertisement