IEC60909 Fault Analysis

12/20/2019 6:52 PM

Hi

With fault analysis using iec60909 Ik” is used to determine the thermal withstand of switchboards, cables etc.

But Ik” does not consider the dc offset present for asymmetrical faults. So if Ik” is calculated as say 20kA, but the fault is asymmetrical with peak of 60kA, does this not imply that the rms whilst the dc offset is present will be higher than 20kA?

Shouldn’t the switchboard thermal rating take this into account? I’ve read a few places that the switchboard rating should just be based on Ik”.

So a manufacturer will spec the switchboard rating at Ik” for xx seconds (typically 1 or 3s). Is the increased RMS value whilst the dc offset is present considered negligible?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: IEC60909 Fault Analysis

12/21/2019 11:59 AM

You are right. In 4.5.2.4 it is stated:

For unbalanced short-circuit currents, the flux decay in the generator is not taken into account, and equations (66) to (68) apply.

That means the factor μ for near-to-generator and q for near to induction motor it may be calculated only for symmetrical three phase short-circuits. For all other unbalanced short circuits [as per 2.3.2 Application of symmetrical components]

it is not applicable.

__________________
Julius
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#2
In reply to #1

Re: IEC60909 Fault Analysis

12/21/2019 11:43 PM

So the effect of offset current is considered negligible?

Or perhaps the method to calculate the thermal effect has enough built in unknowns that the introduction of another calculated variable will not cause the result to be exceed the range of the probable calculation result, if excluding the offset data.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: IEC60909 Fault Analysis

12/23/2019 1:57 AM

What this standard says here is to neglect the DECAY of the generator flux. That means to take it entirely untouched [q=1,μ=1].μ and q are always less than unit.

__________________
Julius
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4
In reply to #3

Re: IEC60909 Fault Analysis

12/23/2019 11:45 AM

That's not what OP is stating, so their original assumption is wrong? You apparently are stating that the asymmetrical portion of the fault current is used in calculating the energy applied to the switchboard?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: IEC60909 Fault Analysis

12/26/2019 2:30 AM

If we take Ik"=20 kA and R/X=0 then the Ipmax=2*sqrt(2)*Ik" =56.57 kA[Ip cannot be more]

Actually, if we take Ip at 1 cycle after the three-phase fault start[1/50=0.02 sec] for 0.02 sec

q=0.84+0.26*e^(-0.26*IkG"/IrG)

Let's say IkG"=20 kA for IrG=1kA q=0.84+0.26*EXP(-0.26*20)=0.8415 Ip=0.8415*2*sqrt(2)*20=47.6 kA

but Ib=0.8415*20=16.83 kA rms

Now, if we neglect the generator flux decay q=1 and Ip=56.57 kA and Ib=20 kA

__________________
Julius
Register to Reply
Member

Join Date: Sep 2019
Posts: 5
#6

Re: IEC60909 Fault Analysis

01/12/2020 5:01 AM

Other than symmetrical breaking current rating, switchboard also has rating for making current. Making current takes care of asymmetrical current which is 2.6 to 2.8 times. So while selecting the switchboards take care of both symmetrical breaking and asymmetrical making current. For example while selecting the switchboards breaker, take care for breaker symmetrical breaking as well as making current.

Register to Reply