Air Cooled Exchanger Failure

10/25/2007 9:32 AM

I have an air-cooled exchanger that doesn't perform well in the summer months and hasn't performed well for years. The fins on the tubes are L-Footed style fins which API says shouldn't be used for temperatures above 270 °F. I have measured amps going to the fans (they are fully loaded), the blade pitch on the fans is at maximum, corrosion does not seem to be a big factor, the process conditions and atmospheric conditions are basically at design. Typical operating temp on the inlet is 255 °F and outlet temp is 150 °F by design but > 180 °F in operation.

The only thing that I can find that might be a problem is that during shut down and start up of the facility, an upstream exchanger has no cooling flow going to it so the inlet temperature of the process going to the air-cooled exchanger can rise to 440 °F for up to 10 hours at a time. My data historian is only 1.7 years old so I only have that much data (exchanger has been in service for 10 years) but this has happened 6 times during the last 1.7 years.

Obviously this is above the fin's design temperature so I am hypothesizing that these high temperature excursions are causing the fins to separate from the tube wall, causing a permanent loss of heat transfer area. Does anyone have experience with these fin types that could tell me whether or not this failure mode is probable?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Pathfinder Tags: heat transfer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#1

Re: Air Cooled Exchanger Failure

10/26/2007 2:27 AM

Dirty fins are a common cause of low efficiency in fin fan coolers. Assuming that the blade pitch is as per design and they are turning at the right speed (no belt slippage or wrong sized pulleys), then I would get someone to do a very good cleaning job. This can be done with only water or with one of the proprietary "foams", depending on the makeup of the dirt. Care must be taken that an over enthusiastic contractor does not flatten your fins with a pressure-jetter. I have seen gains of >30% in efficiency after washing and where I am at present we get around 3% loss of efficiency in a year. This increases rapidly as fouling gets worse. Tried to insert a picture but with little success, (too higher grade task for me) but it does not need much dirt to loose the kind of efficiency you are, and it is the fins that you can't see that seem to have the greatest fouling effect. Other areas to look at are the blade tip clearances and the condition of the inlet bells.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply
Active Contributor

Join Date: Aug 2007
Posts: 17
#2
In reply to #1

Re: Air Cooled Exchanger Failure

10/26/2007 10:04 AM

Do you know the materials of construction? How many fins per inch?

I have seen cases where 500+ F oil was pumped into the tubes of a cold, plate fin exchanger and those fins got really loose. Try to move your fins on the tube. If you get any movement, that would be the problem, especially at high fin densities. If you can't detect any movement, it still might be the problem since the fins tend to interlock.

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#4
In reply to #2

Re: Air Cooled Exchanger Failure

10/26/2007 10:13 AM

10 Fins per inch with a SS 304 tube and AL 1100 fins. The facility cleaned the exchanger earlier this summer but I wasn't able to be there to witness it so I don't know how thorough they were. There has been little positive effect from the cleaning though.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Power-User

Join Date: Feb 2007
Posts: 273
Good Answers: 3
#3

Re: Air Cooled Exchanger Failure

10/26/2007 10:12 AM

"an upstream exchanger has no cooling flow going to it so the inlet temperature of the process going to the air-cooled exchanger can rise to 440 °F for up to 10 hours at a time"

I am not a real genius but I would think that this would be the first thing that I would fix.

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5

Re: Air Cooled Exchanger Failure

10/26/2007 10:22 AM

Two things come to mind. One is the viscosity of your fluid might be high enough and the velocity of the fluid low enough that you get laminar flow. This can be especially irritating of the fluid has a high rate of change of viscosity with temperature, these can lead to 'channelling' of the hot fluid in the core area with viscous cooled fluid against the walls.

Cure, lower viscosity fluid, higher intensity pumping.

Another problem can be the accumulation of cooling induced precipitation products inside the pipe. 'boiler scale' type of thing.

cure, clean the pipe inarrds somehow.

__________________
Per Ardua Ad Astra
Register to Reply
Active Contributor

Join Date: Aug 2007
Posts: 17
#6
In reply to #5

Re: Air Cooled Exchanger Failure

10/26/2007 11:02 AM

Yeah, I'm pretty sure that you got loose fins. What happens is that the tube expands and pushes the fins along with it. I'm not sure at what temperature aluminum anneals, but at your elevated temperature, I'm thinking that they have a permenant set. Then, when you try to operate at the design conditions, your tubes are not quite expanding into the fins anymore. So it does not have the performance that it did when it was new.

It's time for a new coil. If you can't fix the upstream issue, then make sure the new heat exchanger is designed to take the high temperatures.

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#7

Re: Air Cooled Exchanger Failure

10/27/2007 12:06 AM

Talked with the boss and he likes the idea, we are going to move forward on that assumption. Thanks to everyone for your feedback and opinions.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Participant

Join Date: Jun 2007
Posts: 4
#8

Re: Air Cooled Exchanger Failure

01/03/2008 11:23 AM

I agree that the fins are most probably causing the problem. 'L' footed Aluminum on stainless steel tubes is not a good match to retain the bond. I also want to add that if you have not done so, an can, inspect the inside of the tubes, flouling inside the dubes can cause a reduction in heat transfer as well.