Surge Diverters in 33KV Switch Yard

01/11/2020 11:09 AM

I want to know how the surge diverters should be connected in a 33KV switch yard and also what should be the specifications of the surge diverters. We are having 33KV power line coming into our switch yard and getting connected to 33KV/3.3KV transformers,one is 10 MVA and 2nd is 7MVA. Whether I have to connect to all the 3 phases or is it sufficient if I connect to only 2 phases.You may kindly show me the connecting drawing also.

Thanks.

Register to Reply
Pathfinder Tags: SURGE DIVERTERS
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Surge Diverters in 33KV Switch Yard

01/11/2020 5:49 PM

The correct people to ask are the suppliers of the surge equipment!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#2

Re: Surge Diverters in 33KV Switch Yard

01/12/2020 2:16 AM

The questions you ask tell me that you are not the person to undertake this. Get a company with qualified and registered high voltage engineers that can issue certificates of compliance to city and country laws on electrical installation and safety regulations. These Voltages are not the place to try and educate yourself. Get the correct people to do it and then ask the questions you need answers for. Learn from that. You get people in the industry that do this work every day that knows what works best for the longest time that they can put their signature on without come backs, use them.

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Register to Reply
Member

Join Date: Sep 2019
Posts: 5
#3

Re: Surge Diverters in 33KV Switch Yard

01/12/2020 2:18 AM

From your question, i understand that there is a 33 kv switchyard and there are two 33/3.3 kv Transformers connected with overhead lines. If this is true, you need to connect Surge arrester at 3.3 kv overhead line for each phase between phase to earth. Also you may require to connect Surge Arrester at 33 kv side terminal box of Transformer depending upon whether it is connected with long /short cable. For surge arrester selection see ABB web page.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#4

Re: Surge Diverters in 33KV Switch Yard

01/12/2020 3:42 AM

The lightning surge could travel through power line and damage the transformers. Hence, it is the practice to connect surge arresters / divertors at the 33kV terminals of the transformer which are supplied by overhead power line).

The surge arrester shall always be connected in all three phases (phase-to-earth). After all, the surge could travel through any phase.

It is important for good protection that the surge arrester is as close to the transformer as possible.

The rating of the surge arrester depends on the system earthing.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5
In reply to #4

Re: Surge Diverters in 33KV Switch Yard

01/12/2020 8:15 AM

This is not a job for a weekend quarterback or engineer in training.

You should be able to do this job without consulting an unknown group on the 'Net.

Consult the manufacturer and request an on site engineer if required.

I think most contributors here will gladly advise on other things,but with the potential of disastrous results no one wants to be a party to the outcome.

No offense intended,but this is a case of what you don't know CAN hurt you and others.

I have seen a switch yard melt down.. puddles of molten steel from I Beams and blast damage far away from the site.

Literally millions of dollars of direct and collateral damage.

Be safe,not sorry.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Active Contributor

Join Date: Jun 2019
Posts: 12
#6

Re: Surge Diverters in 33KV Switch Yard

01/22/2020 11:05 PM

The lightening arrestor can be mounted at the incoming point of the switch-yard. It will protect both the transformers from lightening surges. It is general practice to install lightening arrestor at the point where line terminates in the switchyard.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (1); Oomborrie (1); PWSlack (1); raghun (1); Rakesh Mishra (1); vimal76 (1)