Circuit Breakers

10/28/2007 6:59 AM

An SF6 circuit breaker having short cirurcit current rating of 40KA for 3 Seconds Is better than that of having Shor Curcuit rating of 50KA for 1 second---which of these should be preferred for installation in a 220KV System?

__________________
inhussain
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Circuit Breakers

10/28/2007 2:28 PM

Well it is really going to depend on your upstream protection elements. Will the SF6 circuit breaker be subjected to a 3 second fault or will it trip out before then. Are you using a 1 second or a 3 second fault rating when designing (or retrofitting to an existing power system)?

__________________
jack of all trades
Register to Reply
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#2
In reply to #1

Re: Circuit Breakers

10/29/2007 1:56 AM

If you really have 50KA short circuit current, a circuit breaker having short circuit current rating of 40KA for 3 Seconds, maybe can not interrupt the 50KA Short Curcuit current. I think magnetude and duration of short circuit current are two different parameters and selected circuit breaker should meet both of them individually.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Commentator

Join Date: Oct 2007
Location: Lahore Pakistan
Posts: 60
#3
In reply to #2

Re: Circuit Breakers

10/29/2007 9:04 AM

One of the supplier claims that 50 KA is more robust having 1 Sec withstand time than 40 KA having 3 second withstand. Obviously 50 KA arc will produce high temperature than 40 KA, but in the former case the withstand time is only 1 second, thus fault will be interrupted earlier without additional temp. rise, whereas in the later case the contacts will be subject to lesser thermal stress but for a longer duration. In the scenario, which one is the better choice?

__________________
inhussain
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#4
In reply to #3

Re: Circuit Breakers

10/29/2007 9:16 AM

50Ka for 1 sec and 40Ka for 3 sec are ratings these do not define the interruption time.!

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Commentator

Join Date: Oct 2007
Location: Lahore Pakistan
Posts: 60
#5
In reply to #4

Re: Circuit Breakers

10/29/2007 11:03 AM

In which of the two cases the thermal stress on the contacts would be higher?

__________________
inhussain
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#6
In reply to #3

Re: Circuit Breakers

10/29/2007 12:11 PM

One of the supplier claims that 50 KA is more robust having 1 sec withstand time

He is right.

Buy his.

Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#7

Re: Circuit Breakers

10/29/2007 3:29 PM

Thermal stress can be defined by I2t;

50KA @ 1 sec. produces 2500 Kamp2.sec

40KA @ 3 sec. produces 4800 Kamp2.sec

Therefore, physically, the contacts of 40KA @ 3sec would be more robust.

However, electrically, it is not a point at all, but:

  • how fast is your protection?
  • how much is your time grading (time coordination) in the protection system?
  • how many amps is prospected to flow in such a CB in the worst case of fault according to a right short circuit calculation?

If the max. short circuit level is less than 40 KA, then 40KA @ 3sec is preferable as it gives you a wider time margin to play time coordination.

If NOT, you are forced to select 50KA @ 1sec.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abbas (1); garth (1); inayat hussain (2); jack of all trades (1); MUKULMAHANT (1); Samak (1)

Previous in Forum: Club Car Golf Cart   Next in Forum: UPS BACK UP
You might be interested in: Circuit Breakers, Load Centers, Circuit Tracers

Advertisement