04/11/2020 11:14 AM

Hey friends i have a yaskawa drive A1000 has alarm OC over current and when i try to rest i am not able to.. another time when i reboot the machine alarm is gone but as soon as i put run command SC igbt shorted alarm appears and i am not able to reser it again.. please help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#1

Re: Yaskawa a1000 250 kw drive

04/11/2020 1:23 PM
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Yaskawa a1000 250 kw drive

04/11/2020 6:56 PM

Or... it could have a bad transistor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#13
In reply to #2

Re: Yaskawa a1000 250 kw drive

04/14/2020 3:43 AM

...or bad cables or a bad motor...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Feb 2020
Posts: 487
Good Answers: 7
#3

Re: Yaskawa a1000 250 kw drive

04/11/2020 11:01 PM

One can look at the semi conductor output junctions quickly with an octopus.

__________________
Light is only half of what you think it is.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6219
Good Answers: 248
#4
In reply to #3

Re: Yaskawa a1000 250 kw drive

04/11/2020 11:29 PM

Canyou be a bit more specific about your testing device? I've been testing transistors for over 60 years, and haven't heard of the octopus (as a testing device).

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Associate

Join Date: Jan 2018
Posts: 26
#15
In reply to #3

Re: Yaskawa a1000 250 kw drive

04/14/2020 6:07 AM

i have got no idea about octopus, but have oscilloscope.. and trying my best to reach to the root cause for it

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1394
Good Answers: 107
#5

Re: Yaskawa a1000 250 kw drive

04/12/2020 12:33 AM

You think maybe the IGBT is not shorted? You might try it with the motor disconnected, but the circuit that senses a shorted output may use the motor winding current to sense the short circuit.

Register to Reply
Power-User

Join Date: Feb 2020
Posts: 487
Good Answers: 7
#6

Re: Yaskawa a1000 250 kw drive

04/12/2020 12:42 AM

Search for oscilloscope octopus. One can inspect the junction visually. And caps and inductors. Great for trouble shooting in-circuit un-powered boards without prints.

__________________
Light is only half of what you think it is.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6219
Good Answers: 248
#7
In reply to #6

Re: Yaskawa a1000 250 kw drive

04/12/2020 1:05 AM

Thanks! I've done that, just never heard it called an octopus!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#8
In reply to #7

Re: Yaskawa a1000 250 kw drive

04/12/2020 2:02 AM

It has been called an Octopus for years because it has eight arms consisting of 2 power leads, 2 circuit probes and 4 scope leads

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#10
In reply to #8

Re: Yaskawa a1000 250 kw drive

04/12/2020 7:38 AM

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6219
Good Answers: 248
#12
In reply to #10

Re: Yaskawa a1000 250 kw drive

04/12/2020 11:36 AM

Thanks. As I said, I've used that method, and still have the Tektronix 2236 I used, but that was at least 20 years ago. I happen to have a questionable linear power supply on my bench right now, and have all the components on hand, so I'll set one up and try it.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#9

Re: Yaskawa a1000 250 kw drive

04/12/2020 2:53 AM

What are the downstream cable parameter measurements, please?

What are the motor parameter measurements, please?

if in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11

Re: Yaskawa a1000 250 kw Drive

04/12/2020 10:54 AM

Quaiser,

Any time a service tech goes to a site with a component not working, many questions will be asked. The answers are important.

--Is this a new installation or an existing one; if existing how old?

--Has anything been changed; what is the repair or maintenance history?

--Do you smell anything; is there any discoloration of parts?

--Are the cables OK; were they installed according to manufacturer's specifications; what type of cables were used?

--Are cable lengths as specified by the drive manufacturer?

--What are the drive parameters?

--Is the motor a VFD rated motor; are there any load reactors?

--What type of load and load characteristics?

--Have you tested the motor's resistance between phases and megohm resistance to ground (with the drive disconnected!)? If so, what are these readings?

--What does the drive manual say in its troubleshooting section?

We can help, but you have to be our eyes, ears, nose, etc. Let us see, hear, read, explore, and then hopefully we can help you to understand and come up with a probable solution.

--JMM

Register to Reply Good Answer (Score 2)
Associate

Join Date: Jan 2018
Posts: 26
#14
In reply to #11

Re: Yaskawa a1000 250 kw Drive

04/14/2020 6:04 AM

well thanks for your comments and suggestion.. the drive boards have been dismantled and is under checking process.. IGBT was found shorted, checking the c.t. if there is any problem with the measurement, control boards. i think the shorted igbt may have damaged the boards also, as far the control board is ok. rest could be informed later. and hope every body is fine during this epidemic situation. take care... i will be back for your assistance thank you

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#16
In reply to #14

Re: Yaskawa a1000 250 kw Drive

04/14/2020 7:16 AM

Equally as important as repairing or replacing <... the shorted igbt...> is isolating and removing the cause, otherwise there is a risk of recurrence. This is why the test records on the motor and its cables are still worthy of pursuit, so as to eliminate these as possibilities.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2018
Posts: 26
#19
In reply to #16

Re: Yaskawa a1000 250 kw Drive

04/22/2020 4:12 AM

i donot have spares like the capacitor and ic.. i would like to know if i put a slightly less power electronics component like capacitor, ic. will that work and what are the probability it will again get damaged.. i had replaced all the igbt but i have doubt over these slightly less capacity of the other components (like i have 40 and machine requires 42.) those are capacitors, rectifiers etc. please suggest me

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#17
In reply to #14

Re: Yaskawa a1000 250 kw Drive

04/14/2020 9:01 PM

Quaiser,

Praise is due to you--for responding to us in a timely manner, doing what you can on your own, and being a cooperative member of our community.

You have fixed the symptom. As was said to you, now is the time to determine the cause (it may have been a bad IGBT, but many outside factors could cause such a failure), and then fix that cause. That is the essence of good service work.

--JMM

Register to Reply
Associate

Join Date: Jan 2018
Posts: 26
#20
In reply to #17

Re: Yaskawa a1000 250 kw Drive

04/22/2020 4:55 AM

i donot have spares like the capacitor and ic.. i would like to know if i put a slightly less power electronics component like capacitor, ic. will that work and what are the probability it will again get damaged.. i had replaced all the igbt but i have doubt over these slightly less capacity of the other components (like i have 40 and machine requires 42.) those are capacitors, rectifiers etc. please suggest me

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#21
In reply to #20

Re: Yaskawa a1000 250 kw Drive

04/22/2020 5:15 AM

Usually better to go over a little than under a little...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6219
Good Answers: 248
#22
In reply to #20

Re: Yaskawa a1000 250 kw Drive

04/22/2020 11:15 AM

I agree with SE's #21, except that I'd replace "usually" with "nearly always".

Manufacturers are always looking for ways to save money, and a significant part of that search involves finding the cheapest parts that will keep the device working through the warranty period in the majority of cases.

If the device failure was caused by some sudden external factor, such as a motor somehow becoming shorted, then the problem wasn't part quality, but if all external factors remain within reasonable limits, then higher quality parts will last longer.

Especially in the case of capacitors, always try to find ones with a higher voltage rating AND a higher temperature rating than the originals.

Down time and repairs are expensive. if a higher quality component costs twice as much as one having the original specs, it's probably worth it!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Anonymous Poster #1
#18

Re: Yaskawa a 1000 250 kw Drive

04/16/2020 10:41 AM
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dkwarner (4); Haymaker (2); jmueller (2); JRaef (1); PWSlack (3); Quaiser (4); Rixter (2); rwilliams (1); SolarEagle (1); spades (1)

Previous in Forum: Coventional Fire Fighting System with Online Monitoring VS Nitrogen Injection System for Transformer Fire Safety   Next in Forum: Replace 16x4 LCD with MLT018A20-7

Advertisement