Design Of Earthing Mesh

10/30/2007 11:51 AM

How to design a grounding mesh of a substation? What parameters are required for a proper design and selection of the size of the grounding conductor?

__________________
inhussain
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Design Of Earthing Mesh

10/30/2007 12:34 PM

The parmeters for designing a grounding mesh are in order of priorty: power handling capapbility of the sud-station wrt the fault currents generated for single and three phase faults .

the faults current levels will determine the conductor sizes.

substatons close to power plants will have higher fault current levels than distrubutuin substation with many mile of transmission line with associated impedances.

te soil conductivity and protection fronm touch and step voltages.

Register to Reply
Guru

Join Date: Jun 2007
Posts: 719
Good Answers: 25
#2

Re: Design Of Earthing Mesh

10/31/2007 6:20 AM

Hi,

I have never used a mesh (only spikes) so my reply may
not be accurate; however I was taught the earth:

Connection to be at least equal to, and preferably greater than,
the capacity of the circuit it protects. (to carry the current.)

Be at least 4 feet, and preferably 6 feet, down below ground
level. (to avoid the ground drying out, making the earth HR.)
Some water absorbent material can be used around the earth.

Be resistance measured to be certain it is not high res. (HR)

Pretty obvious, but hope this helps.

jt.

A Free web page in 30 seconds - http://www.mfnb.at

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Design Of Earthing Mesh

10/31/2007 7:38 AM

The design procedure is and calculations are long.Parameters are as rightly pointed in a reply the fault current at substation bus,and fault current values. If this is not available normally use Incoming breaker's fault current value. The other important thing is limiting the touch ,step potential to sfae limits.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Commentator

Join Date: Oct 2007
Location: Lahore Pakistan
Posts: 60
#4
In reply to #3

Re: Design Of Earthing Mesh

10/31/2007 11:16 AM

Long ago I worked on this assignment. Firstly at various locations of the substation site, the earth resistivity was measured. Then step voltage was decided. Short circuit level was worked out. Assuming the earth resistance to be 2 ohms, the length and size of earthing conductor was calculated. Thereafter, the size of the mesh was determined. But i have forgot the methodology: I would request guidance in the matter.

__________________
inhussain
Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Design Of Earthing Mesh

01/17/2008 5:55 AM

Firstly the earth resistivity of substation area is to be measured. Based on the capacity of the substation and fault level of feeder, the step voltage and touch potential are to be calculated. Finally the earth conductor size, earth electrode size and the spacing between the earth conductors for the entire substation will be calculated

Register to Reply Off Topic (Score 5)
Member

Join Date: Mar 2009
Posts: 8
#6
In reply to #4

Re: Design Of Earthing Mesh

03/08/2009 1:06 PM

send

Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); inayat hussain (1); jt (1); MEHRAJ HASSAN (1); nesubra (1)