Trane Compressor Failures

10/30/2007 9:24 PM

We have 3 Trane HVAC systems (one 3 ton, two 5 tons) in a house built in May 2002 that is used 6 months out of the year but maintained year 'round. Since then we have had to replace the compressors 4 times! We have full maintenance contracts on all the units and change the filters monthly and the compressors are under warranty. But this is expensive--and depressing. The original contractor that did the installation replaced two compressors in the first two years, then we fired him. Our current contractor pulled the third compressor when it failed and found that the hot gas discharge line at the roto lock fitting was twisted and crimped--he said this is why this compressor failed. Last month the 4th compressor failed (also installed by the original contractor). Besides that one with the crimped line we can't figure this out. At this point we are going to the mat with the original contractor. But I am wondering if these are Trane issues. Ideas?

Register to Reply
Pathfinder Tags: hvac compressor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#1

Re: Trane Compressor Failures

10/31/2007 2:06 PM

I had 2 trane systems that also developed a leak at their "roto-lok" fitting right on the compressor. My roto-loks cracked. I don't know how common it is but Trane will never admit to it.

Safe thing to do is check your new ones if they have the rotoloks.

After 2 burnouts, the contamination really gets into the pores of the copper. Need BIG driers and replaceable core suction filters etc. A good HVAC mechanic will know what to do.

Don't just "zero in" on the compressor, there could be other circumstances killing compressors (except for the loose roto-loks, they were a definite death sentence) such as; in-adequate air flow or excessive load or under-voltage or short cycling.

Are the condenser fans running properly, an intermittent fan is a heart-breaker. If you're running low-ambient controls for the fan, get a GOOD one like the Hoffman, that modulate the fan, not turn it off and on.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2014
Posts: 1
#9
In reply to #1

Re: Trane Compressor Failures

03/03/2014 2:29 PM

common issue with the rotolocks should be a scheduled pm thing on the hotgas line. When you get the burn out in the trane you will find a hardened black like coal builds up in the condenser coil and is near impossible to get out. Best bet is to stay away from trane. The eagles have draft inducers that cost crazy money and they are flawed to the point u may change one ayear.

Register to Reply
Power-User

Join Date: Sep 2007
Location: Cleveland, Ohio
Posts: 100
Good Answers: 2
#2

Re: Trane Compressor Failures

10/31/2007 11:55 PM

I have found that many HVAC (new construction) contractors skip many of the necessary steps to ensure a clean, moisture-free, air-free, piping system. Many of them never put a vaccuum on the lines.

This icould be a problem for the refrigerant circuit. It will cause acid formation, over-heating, etc.

Triple evacuation, oil acid testing, pressure-testing with nitrogen, over-sized filters are needed to ensure the proper operating conditions. Is the piping the correct size?

Are their hidden line crimps?

There are so many possibilities for mistakes. It is difficult to know whom to trust to have the appropriate skills to solve your problem.

Is the evaporator blower clogged with plaster dust?

Are the units over-charged?

__________________
THEOILGUY55
Register to Reply
Anonymous Poster
#3

Re: Trane Compressor Failures

11/01/2007 6:05 AM

I've had a similar problem with an a/c used for an air dryer. After others have worked on it. I believe the problem, and more than likely with yours as well, is that once you have a motor burn out, the system needs to be flushed. Once it burns out, the oil that is carried throughout the system is contaminated. To properly flush it out, the expansion valve needs to be removed and a jumper installed, disconnect it from the compressor, run some flushing agent through the system with a small pump and the return line to the compressor needs to go in a container. You'ld be surprised at the amount of burnt looking oil will come out. There should be a low pressure switch to cut the compressor off if there is a leak that prevents damage to the compressor. Maybe someone has jumpered them. I have numerous Trane units (100+) at work and there are some compressor failures now and then but the units are nearly 20 years old. Nothing on the order of magnitude you are experiencing though.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#4
In reply to #3

Re: Trane Compressor Failures

11/01/2007 6:46 PM

Good advice

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#6
In reply to #3

Re: Trane Compressor Failures

11/02/2007 6:24 AM

There should be a low pressure switch to cut the compressor off if there is a leak that prevents damage to the compressor.

Am not an AC man but I've been using the Honeywell Gas Low Pressure Switch on my Burner Gas train as a safety limit and during winter times it gets handy because of pressure drop due excess use of gas for room heating. Try Honeywell Tradeline Catalog detailing Controls & Instruments on both heating & cooling.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Participant

Join Date: Oct 2007
Posts: 2
#5

Re: Trane Compressor Failures

11/01/2007 9:24 PM

Thanks a million for all of your thoughtful comments--very helpful to me trying to understand what is going on. Sniccus, I particularly appreciate your raising the issue of other factors killing the compressors rather than just the compressors having problems. I will check to make sure that the systems are flushed, Guest, and THEOILGUY55 raises many installation questions as well. My "new" contractor seems to be responsive to my concerns so I will raise these points with him. I am also going to call Trane and see if they can shed any light at all on the situation. This just ain't right.

Register to Reply
Anonymous Poster
#7

Re: Trane Compressor Failures

11/05/2007 12:49 AM

The Trane compressors should have a four year warranty and Trane should be very interested in your problem.

Also consider if the company or person working on your system are Trane authorized represenatives.

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#8
In reply to #7

Re: Trane Compressor Failures

11/25/2007 10:16 PM

My experience (Off late) is Not just trane alone every major equipment manufacturer it may be AC,Elevators,Diesel generators, who have moved their manufacturing base to China or unable to insure quality of their products.may be china is yet to learn understanding English.I have interacted with couple of Chinese engineers they are well qualified and certified as required by American & EC standards but hardly have any field exposure and don't understand the field conditions and very difficult to argue technically with them probably American & manufacturers world wide have traded cost for quality of the product.

crm

__________________
Run silent run deep
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); crm (1); ducon (1); Livie (1); roosterjj (1); Sniccus (2); THEOILGUY55 (1)

Previous in Forum: Introduction Post   Next in Forum: CAD Software

Advertisement